I got a Comfort Zone 5000w electric heater for my shed. I am somewhat unsure of the wiring required. The manual says use at least 10ga wire, but also says to use a 32-40 amp breaker. I wired it up on a 30 amp breaker and 10/2 Romex for now, and measured the amps using a clamp on ammeter. This heater has a switch to run at 3k/4k/5k watts. At the heater I measure 13.4/17.8/22.1 amps. At the breaker I see 22.5 amps on the 5k watt setting.
My understanding is for a continuous load such as electric heat you derate the wire and breaker at 125% of load, which would mean a 30 amp breaker is good for a 24 amp continuous resistive load. Is 10ga wire okay to use with this heater?
Walls in the shed are unfinished but I'm closing in the ceiling and insulating, and may do the walls eventually. I have a short run of Romex direct to the heater but I have a metal box and faceplate with knockout I want to terminate the Romex in this box and install MC cable from the box to the heater. Before I get material for this I want to be sure 10ga wire is sufficient. Given the load is under 24 amps and I ran it for a few hours today at 5k watts while working in the shed and the 10ga wire does not feel hot or warm. Thoughts?
My understanding is for a continuous load such as electric heat you derate the wire and breaker at 125% of load, which would mean a 30 amp breaker is good for a 24 amp continuous resistive load. Is 10ga wire okay to use with this heater?
Walls in the shed are unfinished but I'm closing in the ceiling and insulating, and may do the walls eventually. I have a short run of Romex direct to the heater but I have a metal box and faceplate with knockout I want to terminate the Romex in this box and install MC cable from the box to the heater. Before I get material for this I want to be sure 10ga wire is sufficient. Given the load is under 24 amps and I ran it for a few hours today at 5k watts while working in the shed and the 10ga wire does not feel hot or warm. Thoughts?