50a Welding Outlet - Vote Which Wire

Which Wire?

  • #8 THHN

    Votes: 6 27.3%
  • #10 THHN

    Votes: 1 4.5%
  • #6 THHN

    Votes: 11 50.0%
  • Old #6 Wire that still looks in good condition - Stripped from 6/3 WG NM (Not NM-B!) Rated at 60c

    Votes: 4 18.2%

  • Total voters
    22

HamAndEggs

Well-known member
Joined
Nov 16, 2020
Messages
932
Location
Houston, TX
Details here:

I'm looking for your vote if I should use some old copper 6/3 Wire. Its NM wire, not NM-B Wire. I will strip the jacket and run in conduit. Its rated at 60c

Install will not be inspected

Per the NEC, the lowest wire gauge I could go with this welder would be #14 because of the duty cycle. But that's obviously the cheapest way
 
To avoid these ads, REGISTER NOW!

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
Is this circuit just going to be for that welder, or do you want to plug a EV charger in there also. That will tell you what size wire. I would not use the old wire.
 

KenC

Well-known member
Joined
Dec 20, 2009
Messages
2,604
Location
oklahoma
Just so you know, inspection or not, stripping cables and using the individual conductors is not code compliant. For a lot of reasons, I'd go with 10ga THWN. Or be sure the THHN is dual rated as W also.
 
To avoid these ads, REGISTER NOW!

gtae07

Well-known member
Joined
Mar 6, 2015
Messages
3,015
Location
Fayetteville, GA
Wire it as a general purpose 50A outlet using #6 NM-b or #8 THHN in conduit.
+1
Build in the extra capability. You never know when you might want to plug something else in there. I wound up using my "welder" outlet to run an old electric range so I could bake parts. And the ine in the attached garage will probably wind up with an EV charger one of these days.
 

TractorJeff

Well-known member
Joined
Dec 8, 2013
Messages
3,309
Location
Elkhorn, WI
6ga. Only because you NEVER KNOW what will get plugged in there later!
Or a BIGGER Welder!
I Know because I started out with a 20% Duty Cycle on high range full output and ended up with a 60% on high range full output but 100% in the ranges you would typically use.
 

Noltz

Well-known member
Joined
Mar 10, 2020
Messages
377
Location
Ontario, Canada
#6 THHN can carry 60A and is spec'd for most EV's biggest chargers. Currently wearing a Nema 14-50 plug, but likely will put it into a sub-panel now.
 