I would like to have power in my shed. I am thinking about buying a compressor again, the unit will likely pull 20amps on 110v.

Good idea to upsize the wiring to 10G for a 50ft run? I'll be burying in conduit
 
To avoid these ads, REGISTER NOW!
OP
M

[memphis]

Well-known member
Joined
Sep 30, 2016
Messages
129
I would run at least 30 amp at 240v for future needs. it's not that much more to run a 10/3 or 8 /3 .

I was thinking that for my 240v welder. I'm not an electrician but I assume that would mean I should run another line if I want lights which would be on a separate circuit?
 
OP
M

[memphis]

Well-known member
Joined
Sep 30, 2016
Messages
129
Maybe better to run a heavier wire, say 50 Amps to a small sub panel and have what you need.

Sub panel definitely appears the way to go... I could put a 60amp panel in quite easily instead of fishing two lines through conduit for 50 ft
 
To avoid these ads, REGISTER NOW!

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,486
Location
VT
I was thinking that for my 240v welder. I'm not an electrician but I assume that would mean I should run another line if I want lights which would be on a separate circuit?

No.

You can oly run a single feed to a detached building.

So you would want to run 8/3 out to the shed and install a small (6 space?) Panel. Circuit for lights, circuit for outlets (or 2) and a 240v circuit for a welder.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You may already know, but basically such as UF... #10Cu = 30A, #8Cu = 40A, #6Cu = 50A. Amps change with the use of conduit and THHN/THWN wire.
 

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,318
Location
Alexandria, VA
I'm not a code expert or electrician, so take my suggestion with a grain of salt.

I think you could run 8/3 wet rated wire for now (or maybe even 6/3), and wire it as a 20 amp MWBC with a GFCI on each circuit. This means there would be no subpanel, just a 3 wire circuit for the garage. As an MWBC, it would only provide two 120 volt circuits and there would be no 240 volt circuit.

I believe the MWBC meets code requirements for a single circuit feed to a detached building. The only catch is that with larger wire I'm not sure a GFCI or other initial 20 amp device could accomodate the 8 gauge wire.

Later on you could upgrade it to a subpanel and add ground rods and other items needed to be code compliant for a subpanel that has provides 120 volt and 240 volt circuits.

Bruce
 