6/3UF underground, which wire is needed to transition above ground

DTL504

Well-known member
Joined
Jan 9, 2011
Messages
62
Location
Sandhills, North Carolina
I have 50FT of gray 6/3 UF from the detached garage subpanel going approx 18" underground into 1 1/2" conduit to the back of my house which is brick with crawl space. The easiest way to the main panel is to bring the cable into the attic and feed it down into the wall into the main panel. My 6/3 UF ends about 6ft above ground. I am adding a 4x4x4 junction box for a splice to transition to the appropiated wire and continue the run up the back wall to the top gable into the attic using a 1/ 1/2" LB then to the main panel crossing the beams and through the bedroom interior wall where the main panel is located. What option/s do I have to continue the run from the the outside wall to the main panel inside the house
 

Attachments

  • gtarage.jpg
    gtarage.jpg
    53.4 KB · Views: 11
To avoid these ads, REGISTER NOW!

BigJohn20

Well-known member
Joined
Sep 4, 2011
Messages
168
On the outside wall you can either do conduit with individual conductors or more UF.

Once inside the house, I'd transition over to 6-3 NM-B WG since it's easier to work with. If you really wanted to and had the wire, you could go to the panel with UF.
 
Last edited:
OP
D

DTL504

Well-known member
Joined
Jan 9, 2011
Messages
62
Location
Sandhills, North Carolina
1. If I continue the splice with more 6/3 UF when going into the attic can it be loose like NM and staple to the rafters or do it have to be in conduit to the main panel?
2. If I used THWN can I run it in conduit to the top of gable thru an LB and loose to the main panel?

Thanks
 

BigJohn20

Well-known member
Joined
Sep 4, 2011
Messages
168
1. If I continue the splice with more 6/3 UF when going into the attic can it be loose like NM and staple to the rafters or do it have to be in conduit to the main panel?
2. If I used THWN can I run it in conduit to the top of gable thru an LB and loose to the main panel?

Thanks

Once UF is in the house, it IS NM cable.

340.10 Uses Permitted. Type UF cable shall be permitted
as follows:
(4) Installed as nonmetallic-sheathed cable. Where so installed,
the installation and conductor requirements
shall comply with Parts II and III of Article 334 and
shall be of the multiconductor type.

THWN must be run in conduit.
 
To avoid these ads, REGISTER NOW!

kngelv

Well-known member
Joined
May 25, 2011
Messages
2,233
Location
Detroit, MI
This does not sound like an easy path. You should really try and find a more direct route. A 4x4x4 box will be a little tight for a splice point. If you can use a 6x6x6.

James
 
OP
D

DTL504

Well-known member
Joined
Jan 9, 2011
Messages
62
Location
Sandhills, North Carolina
This is the easiest route. Coming from the crawl space would be painbful. My current plan of action is the most direct path. I would explore the option of the 6x6x6.
 