I got into a stink on that very subject at a home inspectors forum, a poster argued that one was not required to do so, he emailed the NFPA (Publishers of the NEC), here is a copy & paste of the email.
From: Cloutier, Mark [mailto:
[email protected]]
Sent: Tuesday, December 22, 2009 10:19 AM
To:
Cc:
[email protected]; Johnston, Michael; Henderson, Carol
Subject: RE: NEC 250.122 (Log #29202)MC
To:
Date: 12/22/09
This is in reply to your email concerning the National Electrical Code®. The NFPA electrical staff cannot approve a particular design or arrangement, comment on workmanship issues, review or perform calculations for compliance. Issues of compliance are the responsibility of the Authority Having Jurisdiction, but I can provide some general remarks.
Section 250.122(B) requires an equipment grounding conductor (EGC) on the load side of an overcurrent device to be increased in size wherever the associated ungrounded conductors are increased in size. The increase in size of the EGC must be done proportionately according to the circular mil area of the ungrounded conductors. Once the ungrounded conductors are increased in size for whatever reason deemed necessary, 250.122(A) is no longer applicable and the requisite requirements of 250.122(B) are required.
Mark Cloutier
NFPA Senior Electrical Engineer
Important notice! This correspondence is not a Formal Interpretation issued pursuant to NFPA Regulations. Any opinion expressed is the personal opinion of the author, and does not necessarily represent the official position of the NFPA or its Technical Committees. In addition, this correspondence is neither intended, nor should be relied upon, to provide professional consultation or services.
~~~~~~~~~~~~~~~~~~~
I did edit out the orig recipient info, all other text is unchanged.