60 amp breaker with 10 gauge wire???

thammel

Well-known member
Joined
Oct 3, 2005
Messages
2,259
Location
Maryland
My 5hp new compressor instructions say 10 gauge wire with a 60 amp breaker...huh?? I ran 8 gauge NM and put in a 40 amp breaker. I can upsize the breaker to60 amps but this doesn't sound correct to me. I thought 6 gauge was required for 50 amps, 8 gauge for 40 amps and probably 4 gauge for 60 amps. Now I can see how the start surge might hit 60 amps, but I'm concerned about having only 8 gauge wire in place.

Comments please!
 
To avoid these ads, REGISTER NOW!

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
This is for a motor circuit. Its different. You can oversize the breaker up to 250 percent of the FLA per the table in the NEC. This is for inrush current for starting that motor, so it does not nuisance trip the breaker. It only happens for a milli second. Any short circuit will still trip that breaker. The motor also has internal thermal overloads that will shut it down if it draws to much current for a longer period of time.

If its a true 5hp motor, you will need a # 8 NM-b (romex) or a # 10 THWN/THHN conductor
 
Last edited:

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,861
Location
NW Iowa
5hp only pulls ~25A. Needs a big breaker to handle startup current. 40A breaker will probably be fine but is the minimum I would install for a 5hp motor. Code allows up to 70A breaker and #10thhn or #8 romex for 5hp motor.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,631
Location
BC
My 5hp new compressor instructions say 10 gauge wire with a 60 amp breaker...huh?? I ran 8 gauge NM and put in a 40 amp breaker. I can upsize the breaker to60 amps but this doesn't sound correct to me. I thought 6 gauge was required for 50 amps, 8 gauge for 40 amps and probably 4 gauge for 60 amps. Now I can see how the start surge might hit 60 amps, but I'm concerned about having only 8 gauge wire in place.

In a nutshell, motors and welders (inductive loads) break the usual rules of matching breakers to wire sizes.
 
OP
T

thammel

Well-known member
Joined
Oct 3, 2005
Messages
2,259
Location
Maryland
Thanks for all your replies! Yes, I have run 8 nmb for this circuit so that should be fine. I'll install a 6am breaker. It is a true 5hp Baldor motor. Check out CAS compressors. Great products!!
 

MoonRise

Well-known member
Joined
Nov 5, 2010
Messages
4,045
Location
NJ
In a nutshell, motors and welders (inductive loads) break the usual rules of matching breakers to wire sizes.

Not wanting to derail this thread, but I would like to learn more about the rules for welders.

Wiring for welders (or some other intermittent and duty-cycle limited devices) are or can be done based on the "Duty Cycle" of the machine.

Since most/many 'home' sized machines (and even some commercial/industrial machines) have a rather limited duty cycle at the high-end output settings, that non-continuous run-time is reflected in the wiring requirements.

made up but semi-realistic example: A welder needs a 50 amp breaker to handle the transformer start-up surge so it doesn't nuisance insta-trip on start-up but only draws maybe 20-30 amps at 'full' output. But it only has a 20% duty cycle at full output. So you might wire it with a 50 amp 240 V double-pole breaker and use #10 wire to the NEMA 6-50R to plug the machine into. (pretty much a buzz-box aka 'tombstone' stick welder)

Code used to require such wiring to be labeled something like "For Welder Use Only" so someone didn't go and plug in something like a 100% duty-cycle 50 amp draw device (heater, perhaps) and thus 'overload' the wiring from the breaker to the receptacle.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
They dont cause the heater doesnt come with a plug. A buzzer can be 12 single circuit in pipe with 50A. No one thinks thats really great and that is full output which it doesnt normally run so the real draw is about 40 under common use. But, the terminations are poor with that small wire and V drop is rather significant especially at some distance. When a guy goes to 10 most all that goes away.
I think the legal limit on 12 is about 48A.
 
To avoid these ads, REGISTER NOW!

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
20,148
Location
Northern Virginia
Moonrise - thankyou.

Wiring for welders (or some other intermittent and duty-cycle limited devices) are or can be done based on the "Duty Cycle" of the machine.

Since most/many 'home' sized machines (and even some commercial/industrial machines) have a rather limited duty cycle at the high-end output settings, that non-continuous run-time is reflected in the wiring requirements.

made up but semi-realistic example: A welder needs a 50 amp breaker to handle the transformer start-up surge so it doesn't nuisance insta-trip on start-up but only draws maybe 20-30 amps at 'full' output. But it only has a 20% duty cycle at full output. So you might wire it with a 50 amp 240 V double-pole breaker and use #10 wire to the NEMA 6-50R to plug the machine into. (pretty much a buzz-box aka 'tombstone' stick welder)

Code used to require such wiring to be labeled something like "For Welder Use Only" so someone didn't go and plug in something like a 100% duty-cycle 50 amp draw device (heater, perhaps) and thus 'overload' the wiring from the breaker to the receptacle.
 

andyvh1959

Well-known member
Joined
Feb 15, 2020
Messages
2,611
Location
Green Bay WI
I have my welder (Millermatiic MIG) and my compressor (upright 6.5hp) on a 30amp circuit, with the dryer style 30 amp plug connection. Never had any issues on start up or usage for 15 years.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,201
Location
Modesto, CA
I have my welder (Millermatiic MIG) and my compressor (upright 6.5hp) on a 30amp circuit, with the dryer style 30 amp plug connection. Never had any issues on start up or usage for 15 years.

a dryer plug (10-30 or 14-30) is not the right plug for 240v equipment. you need a 6-30r and p
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,631
Location
BC
Not wanting to derail this thread, but I would like to learn more about the rules for welders.

There's a code section for welders. You will need the line amperage and duty cycle of the machine and do some math.

Or, in your welder's manual, it usually has all this worked out for you... X minimum wire size and Y max breaker size.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
I have my welder (Millermatiic MIG) and my compressor (upright 6.5hp) on a 30amp circuit, with the dryer style 30 amp plug connection. Never had any issues on start up or usage for 15 years.
If that compressor is a true 6.5 hp. You should have it hardwired with a disconnect. The proper plug and receptacle for that is very expensive. That dryer plug and receptacle is not rated for 6.5 hp.

Sent from my SM-G960U using The Garage Journal mobile app
 
Last edited:

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Remember,,, the min wire and max breaker depends on the wire for the small units. If you use the min wire the breaker is limited, if it's bigger than the min wire the max breaker is 50, the plug it comes with.
 