I am running a 60 amp circuit to my furnace in my pole building. I have run 3/4 EMT from the service to where the furnace is located. My plan is to run 2 #6 THHN and a bare ground. Is this acceptable or do I need a #6 neutral also ? ? and what guage should the bare ground be ?
I am also running 2 50 amp circuits (again in 3/4 EMT) with 2 #8 wires. Same question..do I need a neutral and what size should the bare ground be ?
Thanks!
I am running a 60 amp circuit to my furnace in my pole building. I have run 3/4 EMT from the service to where the furnace is located. My plan is to run 2 #6 THHN and a bare ground. Is this acceptable or do I need a #6 neutral also ? ? and what guage should the bare ground be ?
I am also running 2 50 amp circuits (again in 3/4 EMT) with 2 #8 wires. Same question..do I need a neutral and what size should the bare ground be ?
Thanks!