650’ pull

Rmoore7167

New member
Joined
Sep 11, 2022
Messages
2
Hope this is ok to post here. I have a 650’ pull from home to our gate. The original owner put in 650’ of conduit but nothing to pull with☹️. There is some water in the line and cant seem to blow out . There is air coming out of other end when blow so not blocked. Ive trid sucking a bag through line put just gets too water and stops. Any ideas? I see there it some pullers for about $200 on amazon but wonder it i could really push something that long through pipe
 
To avoid these ads, REGISTER NOW!

tool_scrounge

Well-known member
Joined
Jul 20, 2010
Messages
4,242
Location
Southern California
I suspect you need pull boxes as PCustoms noted. Then you have an excuse to get a vintage Crosman jet line 101 CO2 conduit pistol. It does not shoot pellets, it launches the whole CO2 cartridge as a rocket thru the conduit with a thin string attached. Sorry I sold mine. I really did not need it but it was fun to test. But with standing water in the conduit this is probably not going to work so well.

The web site is in German, but the photos are pretty good.

 

Walkers

Well-known member
Joined
May 17, 2021
Messages
3,912
Location
Cave Creek Az
If the problem is really only water, then just let the air run through it for a few hours to dry it out. More likely, there are a few stones in there too, causing the hood up.
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
20,274
Location
Northern Virginia
Can you not install a shop vac on one end and just leave it run till it ***** clean? I think the shop vac suckage will do better than trying to blow. The nozzle will try to self seal/**** in vs you restraining the blow (man this does not sound right..)

650' is a long run. Sparkies will be be along soon and talk about voltage drop.
 

LXCam

ALLIANCE MEMBER
Joined
Apr 23, 2013
Messages
19,383
Location
AZ
Buy a conduit mouse and blow or **** a pull string thru, that’ll get a majority of your water out. But If your bends are pvc, i wouldn’t suggest using the string to pull the wire, you will absolutely eat into n groove those bends and you wire pull will either end up stuck or chafed badly. Get some mule tape n pull that in with the string, then move onto pulling the wire.

But I highly suggest you install at least one pull box if not two.
 

vavet

Well-known member
Joined
Mar 6, 2012
Messages
5,363
Location
Ashland, VA
I suspect you need pull boxes as PCustoms noted. Then you have an excuse to get a vintage Crosman jet line 101 CO2 conduit pistol. It does not shoot pellets, it launches the whole CO2 cartridge as a rocket thru the conduit with a thin string attached. Sorry I sold mine. I really did not need it but it was fun to test. But with standing water in the conduit this is probably not going to work so well.

The web site is in German, but the photos are pretty good.

That’s cool as hell. You could sell those on any aisle of Home Depot with absolutely no hint of what to use it for. Pretty sure the inventor‘s wife was out of town the weekend he invented that. It was the German equivalent of “hey y’all, watch this!”
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,596
Location
Fullerton, CA
Then you have an excuse to get a vintage Crosman jet line 101 CO2 conduit pistol. It does not shoot pellets, it launches the whole CO2 cartridge as a rocket thru the conduit with a thin string attached.
I've used one to go through a new 1-1/4" underground run <150' long and it got wedged in an elbow. We tried unsuccessfully to remove it.
We finally had to sawcut and jackhammer the slab to replace the elbow.
Better to use the compressor/vacuum method
 

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,858
Location
East Bay SFO
A pressure test even now with the water in it would be a good idea. Seal up one end and pressurize the other. The gauge will tell you whether or not there is a big hole somewhere. That would be good to know before you go any further.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
A pressure test even now with the water in it would be a good idea. Seal up one end and pressurize the other. The gauge will tell you whether or not there is a big hole somewhere. That would be good to know before you go any further.
Why? Water is normal in electrical conduit. Most guys don't prime and definitely don't glue it up like plumbing. Expecting it to hold pressure will likely leave you disappointed
 

Half-fast eddie

Well-known member
Joined
Jul 10, 2021
Messages
1,479
Location
Virginia
A hunnert yrs ago i was working for a gc building a high rise building … 49 floors. We pumped concrete for the elevater shaft walls all the way to the top. At the end of the pour th3 used nerf footballs to clean out the concrete pipe. Cut the ends off the footballs, soaked them in a bucket of water for an hour, put them in the pipe at the top and blow them through with compressed air. Repeat as needed until a football came out the bottom still looking like a football.

Point being … get a couple of high density rubber balls, insert them into the conduit, and blow them through to clean out dirt and water. Tie a pull string to the last one.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
before you go to all this trouble with the existing conduit, you should tell us what size it is and what load you want to put on it

the existing conduit may be too small...
 
Last edited:

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,133
Location
Central Iowa
Have you considered solar?

You're going to need some big wire for even a 10a draw.
If he can come up with a 240 volt gate opener, #8 will probably work. That brings up another problem; where to get two lengths of #8 and a #10 that are 650' long. I buy it by the 500' spools, I've never needed more than that though I'm sure there are 2500' spools available as cutting reels at supply houses.

Me thinks this would be better served by digging the pipe up and cutting in Quazite style pull boxes.
 

Noltz

Well-known member
Joined
Mar 10, 2020
Messages
377
Location
Ontario, Canada
before you go to all this trouble with the existing conduit, you should tell us what size it is and what load you want to put on it

the existing conduit may be too small...

You're going to need some big wire for even a 10a draw.

Jesus you guys aren't kidding. Calculator.net says a 10A load at 650' needs 3AWG copper, or seven 14awg conductors per phase to get under 3%.

If it's less than 1A battery charger load then you can get away with 14awg. 1.5A (I'm thinking a LED pole light) needs 12awg. Just curious what the rules are when you're sizing a circuit for a specific load <15a? Does it need to be hard-wired to the opener here?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
Jesus you guys aren't kidding. Calculator.net says a 10A load at 650' needs 3AWG copper, or seven 14awg conductors per phase to get under 3%.

If it's less than 1A battery charger load then you can get away with 14awg. 1.5A (I'm thinking a LED pole light) needs 12awg. Just curious what the rules are when you're sizing a circuit for a specific load <15a? Does it need to be hard-wired to the opener here?
cant run parallel conductors for same phase, smaller than 1/0
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Does it need to be hard-wired to the opener here?
I certainly wouldn't put a receptacle in beyond what is needed to feed the opener and if you did one for that, I would label it. If someone were to use it at higher draw, it could damage the device.

I know you can get 10a breakers, not sure about smaller
 

Jlanciani

Well-known member
Joined
Jun 7, 2020
Messages
172
Location
Home
#8 with a 7.5% voltage drop will be fine. It's a gate opener, not a data center.
Jesus you guys aren't kidding. Calculator.net says a 10A load at 650' needs 3AWG copper, or seven 14awg conductors per phase to get under 3%.

If it's less than 1A battery charger load then you can get away with 14awg. 1.5A (I'm thinking a LED pole light) needs 12awg. Just curious what the rules are when you're sizing a circuit for a specific load <15a? Does it need to be hard-wired to the opener here?
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
12,046
Location
Austin, TX
Hope this is ok to post here. I have a 650’ pull from home to our gate. The original owner put in 650’ of conduit but nothing to pull with☹️. There is some water in the line and cant seem to blow out . There is air coming out of other end when blow so not blocked. Ive trid sucking a bag through line put just gets too water and stops. Any ideas? I see there it some pullers for about $200 on amazon but wonder it i could really push something that long through pope

Tried sucking the water out with a shop vac? That's worked better for me.
Once you clear the water, the plastic bag thing will work a lot better.
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
12,046
Location
Austin, TX
Is the opener DC or AC? My openers typically are 12V DC. Don't want them to fail to function if the power is out.
 

kaffine

Well-known member
Joined
Dec 13, 2009
Messages
3,610
Location
Henderson, NV
What are you using to try and blow out the conduit?

I've had to have conduit blown out with a compressor a few times. We used a large tow behind compressor. I would think a compressor with a decent size tank would be able to. You may not get all the water out with a small compressor but should be able to get a mouse through the conduit with a string attached. Then use the pull string to pull in mule tape (a wide flat rope) so you don't cut through at corners assuming pvc pipe.

As far as using a fishtape well duct rodder at that size that far unless it is really large conduit that is mostly straight I would be surprised if you can do it. I've had fairly straight shots of 4 inch conduit 400 feet that I wasn't able to get a duct rodder through. I did have issues as it was partially filled conduit, I ended up having to backpull an existing wire to get a pull string in.
 

Ilikeike

ALLIANCE MEMBER
Joined
Jan 8, 2015
Messages
2,452
Location
Northern Ca.
Battery, inverter (if ac) small solar panel.
maybe a small trickle charger for battery off your 650' run so you could down size wire to a 1amp trickle charger load.
Just a thought, I did this for a remote irrigation controller, minus the trickle charger.

Me, I'd trench and put a couple Christy boxes in and run wire for the gate and maybe a dusk to dawn light.
 

tdkkart

Well-known member
Joined
Jun 17, 2006
Messages
6,887
Location
Eastern Iowa
Leave one of the kids at home, call when you're within a couple miles, have them run down and swing the gate open.

Maybe a trained goat pastured at the gate?

I'm thinking the solar setup would be way easier than dickin' with a 650ft wire run. Likely the conduit isn't big enough for the wire you need.
 

kbuhagiar

Well-known member
Joined
Dec 27, 2005
Messages
1,801
Location
Escondido, CA
Just curious...

Say we are starting with a gate located 650ft (or more) from the residence (and power source), but nothing has been done. No conduit, nothing installed yet.
What would be the recommended solution from the experts? I just recently visited a residence where the outer gate was easily a half-mile from the dwelling, with no adjacent structures/improvements/poco lines close by. As I punched in the gate code I was wondering how in the heck would they get power out here?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Just curious...

Say we are starting with a gate located 650ft (or more) from the residence (and power source), but nothing has been done. No conduit, nothing installed yet.
What would be the recommended solution from the experts? I just recently visited a residence where the outer gate was easily a half-mile from the dwelling, with no adjacent structures/improvements/poco lines close by. As I punched in the gate code I was wondering how in the heck would they get power out here?
Solar
 