6AWG circuit derating / correct size OCD

quakerj

Well-known member
Joined
Nov 11, 2021
Messages
171
Location
Meade County, KY
I have a 3/4 EMT conduit run that is going to contain two 6ga wires for a welder outlet, and three 12ga wires for a MWBC quad-receptacle.

I know more than 3 conductors require derating, what is the appropriate breaker size for the 6ga circuit? I probably don't *need* more than 30A here, just trying to future proof in a sense. All wires are THHN, 12ga is solid. Any issues with conduit fill?
 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,997
Location
Central Iowa
If you're using copper THHN/THWN the max breakers are going to be 60 for the #6 and 20 for the #12. This is after derating, which is 80%.
 
OP
Q

quakerj

Well-known member
Joined
Nov 11, 2021
Messages
171
Location
Meade County, KY
Welders have special wiring requirements based on duty cycle, so you are very likely significantly oversizing the wiring. A typical 50a home welder can be hooked up with #12.
Oversizing the wire was sort of intended in this location as at some point in the future it may change from a welder circuit to something else entirely, like a mini-split or who knows what. I just wanted a big beefy circuit in at least one spot for the future unknowns, in the meantime it can be an extra place for a welder receptacle. The wire cost nothing, it was left over from a project I did years ago.

Sounds like up to 60A is okay if I ever need it?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,858
Location
Richmond, VA
How long is the run?

If any decent distance, would a subpanel be more useful? Then you can easily have multiple receptacles off it. Keep the welder and add hvac, or an ev
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,997
Location
Central Iowa
Isn't that 80% for continuous loads? I can't imagine a welder being a continuous load.
The question was what is the largest size breaker that can be used for the #6 with that many wires in the conduit. #6 THHN is rated for 75 amps, the adjustment factor is 80% meaning the largest breaker that can be used for #6 is a 60. I left out that a welder receptacle is a 6-50 so it's limited to a 50 amp breaker so #8 would work and I would probably use #10, but those weren't part of the question. Continuous/non continuous has nothing to do withhow many wires are in a conduit.
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,891
The question was what is the largest size breaker that can be used for the #6 with that many wires in the conduit. #6 THHN is rated for 75 amps, the adjustment factor is 80% meaning the largest breaker that can be used for #6 is a 60. I left out that a welder receptacle is a 6-50 so it's limited to a 50 amp breaker so #8 would work and I would probably use #10, but those weren't part of the question. Continuous/non continuous has nothing to do withhow many wires are in a conduit.

if it was a larger conduit would the same derate apply? or is it a # of conductors in there triggering it?
 
To avoid these ads, REGISTER NOW!

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
If the wires/conduit see ambient temps over 86 degrees F, you'll have to derate them some more (310.15(B)).
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,997
Location
Central Iowa
But at what size is it no longer "conduit"? Dun dun dun
The one and only time it's been an issue for me was about 15 years ago. I got dinged for having six #14 and two #12 in a 2" that was about five feet long and didn't derate.
 
Last edited:

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
I wonder if they take that into consideration in every single exterior conduit run in Texas?
They should be! I'm in CT where the temps hardly ever go above 85*, and even I take it into consideration. I looked up the highest recorded temperatures in my area and base the derating off of that. Temps between 96-104* get derated to 91%, which is what I use. It's those rare, unusually hot times when you need the extra ampacity the most.
 
OP
Q

quakerj

Well-known member
Joined
Nov 11, 2021
Messages
171
Location
Meade County, KY
Thank you fellas for all the answers and I certainly enjoy reading the extra debate.

I'll probably go with a 40A breaker for now because I happen to have one on hand. In this corner of the shop, it's not perfectly suited for HVAC but could be used as such. For an EV it's in the perfect location. I used #6 because I didn't have to buy it, not because it was really needed.

The rest of the shop is run in #12, which will suit all my 240V locations (lift, air compressor, welder outlets) just fine. I might need to add a conduit run in the future for HVAC if I want to put it in the back, but that shouldn't be a huge ordeal.

Just for clarification, many of my #12 branch feed wires leave the panel out of 3/4 EMT that is about 1' long before they enter a junction box. I don't have to derate there, correct? By the time I'm done, the pipe will have about 15 conductors, some of which aren't considered current carrying. I should mention the #6 leaves out a different pipe, so these are all #12's, think I'm allowed up to 16 in that 1' section if I'm not mistaken.
 