6ga wire to subpanel 50amp or 60amp breaker

mdale

Well-known member
Joined
Aug 22, 2008
Messages
92
Location
Indiana
I'm replacing my subpanel in the garage and it is fed with 6ga copper and is powered by a 50 amp breaker in the house panel. From what I've been told 6ga is usually on a 60amp circuit, should I replace to 50a for a 60a breaker after I replace the panel?
 
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
what kind of wire is it? thhn in conduit or romex?
 

warrenw

Member
Joined
Aug 27, 2008
Messages
8
Location
Edmonton, AB, Canada
NEC will allow 60Amp, but save your money unless you want a welder in your Garage. Really, it is dependant on your load in the garage not based on the wire size.
If your home has 100Amp service, again don't bother with the 60Amp Breaker.
 
To avoid these ads, REGISTER NOW!
OP
M

mdale

Well-known member
Joined
Aug 22, 2008
Messages
92
Location
Indiana
Not romex, I'm guessing thhn, I have 4 cables - 3 6ga and 1 8ga?? ground in conduit
 

metal1313

Well-known member
Joined
Apr 28, 2009
Messages
3,416
Location
clinton NJ
they left a little wiggle room basicially. you could upsize the breaker but it is not necessary. i will be running the same size circut, but may up size to 75-80 amps. just gotta have the house panel replaced first, not enough slots and some weird wiring in the house.
 