at home
Ordered some 8/2 mc cable for my compressor and welder. The outside diameter measures just a touch over 5/8in. Searched my local lowes for mc connectors. Every thing is either too small or too big. Is there an online option? Maybe an odd size?
8/2 for a welder? whats the make and model on the welder?
whats the HP rating on the compressor? If its 5hp, #10 MC is fine.
C
caleb90
at home
Hobart ironman. Manual calls for 50 amp breaker with 10g wire. Compressor calls for 40amp breaker and 8/2 wire. Bought a roll of 8/2 mc to save money and use on both
compressor manuals are usually pretty horrible when it comes to electrical specifications... again what is the HP rating on the motor label?
dogdog
C
caleb90
at home
The Mc cable connectors are not glove fit. They are held in by a set screw with something like these as an example.
Were you looking at something else ?
No. Wont fit in 3/8, and 1/2 in is to big. Can screw set screw in all the way, and pull the cable out
C
caleb90
at home
Got home, and the motor reads 5hp 21amps. Im assuming they got there numbers from start up draw. Plus an unheated garage, even with synthetic pump oil it starts slow.. maybe i could have gotten away with 10/2. But the 8/2 was 10bucks more for a 50ft roll.
dogdog
Can’t say 100% with no pics. I say in these situations, I would cut a small piece and head down to electrical supply store and ask them.
Don’t think you have a special cable, probably just choose a wrong type, make sure it is for the right cable type.
C
caleb90
at home
I took a piece with me to lowes. The only thing that fit good was the 1/2 conduit fittings. But they dont have much of a lip to hold the anti short bushing in place
dogdog
Go to an electrical supply store specific ones not big box stores, if you have those in your area. Besides that, I get wires cheaper with them when I paid cash also. These are the places electrical contractors order from.
nope. 21a would be the FLA/run amps
wire for motor circuits is sized by NEC FLC table amps
for 5HP you need #10 THWN or #8/2 NM-b...
10/2 MC wouldve worked fine for both the welder and compressor...
but now youve violated code because the ground wire in 8/2 MC is #10. code requires you to upsize the ground wire when you increase the size of the ungrounded conductors beyond the required size.
since #10 was what was needed, and you increased it to #8, it means the ground wire should also be #8.... but 8/2 MC has a #10 ground...
Jmellc
Durham, NC
Only if you are upsizing for voltage drop.
C
caleb90
at home
Im not upsizing for voltage drop. Manual calls for a 40 amp breaker on the compressor. 8/2 is 40 amp wire, why i went with it. Could i have run 10/2? Most likely. Welder calls for a 50amp breaker with 10/2 min wire size. So i figure if im buying 8/2 i might well just get enough for both
rlitman
Long Island
There are other types of MC connectors than just the normal offset set-screw type. Have you looked at a right-angle connector with the cover that has an angled dimple to engage the armor? That might fit your cable better.
Or there are take-all connectors that are rated for NM as well as MC that have a very wide range of opening size compatibility.