I had to read this about three times, yes, electric cable, 8-2 w/grd UF (if the welder doesn't need the neutral internally for any 120v circuits, would be fine on a 30 amp breaker/30 amp receptacle circuit. This is single phase, there is no two phase commonly available in the US (though it does exist in a couple of rare instances).
Are you running this underground? If no, you really do not need the UF cable and a jacketed romex type cable is much cheaper.
Charles
I am not sure I understand this response to this question or issue.(B) Increased in Size. Where ungrounded conductors are
increased in size, equipment grounding conductors, where
installed, shall be increased in size proportionately according
to the circular mil area of the ungrounded conductors.
6 & 8 AWG NM & UF cable has a 10 AWG equipment grounding conductor & because of the above code section disallows the use of either size or type for 30A, because one cannot put a larger EGC in the cable assembly.
The wire in the cable is already an assembly, comes with the correct ground wire, he didn't change anything, he didn't increase the conductors at all, he is just using a lower breaker than the max allows.
If you increase the wire size on the ungrounded conductor you MUST increase the grounding conductor proportionally there is no exception for anything in the code section, and he would be using a larger size conductor then required.
NEC section 250.122(B) 2008 edition.
(B) Increased in Size. Where ungrounded conductors are
increased in size, equipment grounding conductors, where
installed, shall be increased in size proportionately according
to the circular mil area of the ungrounded conductors.
Have you ever had an inspector catch this? It would never happen in Maine with a piece of UF
First, there is no argument that you probably know more about electric than I ever will, so we can get that out of the way right now, but, that does not apply to this cable. By this implication this cable would be suitable if he put a 40A breaker on it vs a 30 is that correct? That section is for individual wires where the installer has increased wire size for V drop, say he went from a 6 to a 4 he would need to use an 8 vs a 10, could still be fed by a 50A breaker.(B) Increased in Size. Where ungrounded conductors are
increased in size, equipment grounding conductors, where
installed, shall be increased in size proportionately according
to the circular mil area of the ungrounded conductors.
he hasn't changed this relationship, he just didn't put as large as breaker on as allowed, no rule says you have to use as large a breaker as you can.shall be increased in size proportionately
# 10 AWG ground is good up to 60 amps. 250.122(B) only applies if you increase the size of conductors to compensate for voltage drop, increased ampacity, etc. This really falls under250.122(F)(1)....Grounding conductor based on OCPD.
Norcal is right on this one, even it defies logic. Perhaps someday this part of the code will be refined.
It sounds like the OP wants to power a detached garage/shed with both 120 volt and 240 volt loads. If so he needs a four wire feed and ground rods at the existing breaker panel in the structure.
A picture of the existing panel would help.
measurement as of earlier
from main panel to sub in building = 97'
from sub in house to building= round 75'
what you don't know is
building was previously wired by step dad (deceased) with 12-2 and 2 20amp breaker in sub panel. wiring was cut some years ago and has to be reran back into the house to have power again. perfect for turning back on the lights and installs outlets to run power tools,grinder,etc and maybe my compressor if i go with a 30amp breaker.
I dont get where he is increasing, it says proportionately, he didnt increase the proportions. ALL he is doing is using a smaller breaker, so let me get this right, all he would have to do then is increase the breaker to 40A and all would be well? If he runs any less than a 60A breaker on a number 6 wire he has to increase the groiund wire?

But, if fed with a 40A breaker the ground wire would have to be increased?#6 UF is only rated for 55 amps, so a 50 amp breaker would be fine.
#6 UF is only rated for 55 amps, so a 50 amp breaker would be fine.
The reason I mentioned the 110 volt circuits is you are only allowed one feed to detached building, so restoring the old damagred feed is not an option once the new wire is installed.
NEC 250.122(B) will not allow one to use a larger NM or UF cable for the use invisioned in the OP.
Here is a copy & paste from the 2008 NEC.
(B) Increased in Size. Where ungrounded conductors are
increased in size, equipment grounding conductors, where
installed, shall be increased in size proportionately according
to the circular mil area of the ungrounded conductors.
6 & 8 AWG NM & UF cable has a 10 AWG equipment grounding conductor & because of the above code section disallows the use of either size or type for 30A, because one cannot put a larger EGC in the cable assembly.
#6 UF is only rated for 55 amps, so a 50 amp breaker would be fine.
The reason I mentioned the 110 volt circuits is you are only allowed one feed to detached building, so restoring the old damagred feed is not an option once the new wire is installed.
So I'm asking everyone, including electricians, who's been failed for that violation?
Not to hijack the OP's thread, but could you point me (us) to a handy web reference that specifies current capacity of various conductors. Working on my own garage plans. Thanks.
You can use an online calculator, here's a link to some various ones:
http://www.electrician2.com/calculators/elcal.html

So, what size would the ground need to be with a 30A circuit?Strange thing is if someone wanting the same thing, using IMC or rigid conduit underground w/ 2 -6 AWG conductors on a 30A circuit & using the conduit as the sole grounding means, there is no issue w/ upsizing at all.
I understand about this upsize requirement Ace but what about when its included in the cable?I always thought this rule was kinda funny. I know a lot of electricians that run 100 amp feeders using #2 Cu, including the members on here, that don't upsize their grounds from #8 to #6 when doing so.
So, what size would the ground need to be with a 30A circuit?
ok im lost on this ruling thing if it already has a 10awg ground with the wiring and even if it's put into conduit why does the rule stand when nothing is going bigger? all i want to do is run the 6-3 uf on a 50amp breaker to the building wire in a disconnect panel and breaker it again.
then maybe use the 8-2 that i already have or maybe the 12-2 that is already in the building ( no sense in wasting it) and use it to power 120v devices air compressor,grinder,lights drill press
yes i know it was said it will work on a 50-60amp breaker
how can the rule keep poping up though if nothing is changed is what im asking