I'm a handy home-owner and plan to do most of this work myself. I want to develop a game plan, run it by a friend of the family who is an electrician, and then have him connect the panels. I could probably do it, but better safe than sorry.
I have a 200 amp main panel in my unfinished basement. I want to put a 90-100amp panel in the already dry-walled garage about 90 feet away (includes out of main panel, 54 feet through floor joists, out of the basement, up a wall over 6 feet, then back down 6 feet or so to the new panel.
1. Do I need to worry about the gauge/length of SER wire if its under 90 feet?
I read that 2-2-2-4 SER is only good for 90 amp at 75 deg C; however, when I looked around I can't find any 90 Amp Load Centers.
2. Is my only option if I want 90 amp load center, to buy a panel without main breaker and buy a separate 90 amp main breaker?
I believe i'd have to up my AL wire to 1-1-1-3 in order to have 100 amp using the 75 deg C chart I saw online. The additional cost for the bigger wire would be about $108. Additional cost for new breaker plus blank panel vs 100 amp panel with main breaker included would be about $30.
3. Should I just **** it up and spend the extra $78 on the bigger wire and have more capacity?
I was planning to drill a hole straight through the wall from basement to finished garage, then use a 2" LB to route the SER to the panel.
4. Due to the configuration of the garage, I would like to use 3 - 90deg bends to get it to the panel. is this a problem with 2-2-2-4 or 1-1-1-3 SER running inside of a 2" conduit?
5. How does one mount the LB to the wall, or do you not need to? Is it wrong to drill a hole through the back of the LB and screw it to a stud?
6. I didn't notice any single screw 2" conduit clamps. It looks like everything was secured with 2 screws, one on each side of the conduit. This makes running it in the exact corner of the room impossible. Are you not supposed to do that? I wanted to run it up the corner, kick it 90 to run along the ceiling/wall corner, then another 90 down the wall to the panel.
7. What height does the sub-panel need to be off the ground, and is there a requirement for how far way from a door frame or window frame it needs to be?
I have a 200 amp main panel in my unfinished basement. I want to put a 90-100amp panel in the already dry-walled garage about 90 feet away (includes out of main panel, 54 feet through floor joists, out of the basement, up a wall over 6 feet, then back down 6 feet or so to the new panel.
1. Do I need to worry about the gauge/length of SER wire if its under 90 feet?
I read that 2-2-2-4 SER is only good for 90 amp at 75 deg C; however, when I looked around I can't find any 90 Amp Load Centers.
2. Is my only option if I want 90 amp load center, to buy a panel without main breaker and buy a separate 90 amp main breaker?
I believe i'd have to up my AL wire to 1-1-1-3 in order to have 100 amp using the 75 deg C chart I saw online. The additional cost for the bigger wire would be about $108. Additional cost for new breaker plus blank panel vs 100 amp panel with main breaker included would be about $30.
3. Should I just **** it up and spend the extra $78 on the bigger wire and have more capacity?
I was planning to drill a hole straight through the wall from basement to finished garage, then use a 2" LB to route the SER to the panel.
4. Due to the configuration of the garage, I would like to use 3 - 90deg bends to get it to the panel. is this a problem with 2-2-2-4 or 1-1-1-3 SER running inside of a 2" conduit?
5. How does one mount the LB to the wall, or do you not need to? Is it wrong to drill a hole through the back of the LB and screw it to a stud?
6. I didn't notice any single screw 2" conduit clamps. It looks like everything was secured with 2 screws, one on each side of the conduit. This makes running it in the exact corner of the room impossible. Are you not supposed to do that? I wanted to run it up the corner, kick it 90 to run along the ceiling/wall corner, then another 90 down the wall to the panel.
7. What height does the sub-panel need to be off the ground, and is there a requirement for how far way from a door frame or window frame it needs to be?