We have a commercial customer that did his own sub panel work in a restruant and the building dept revoked his occupancy permit, until he gets an electrical permit / inspection . He wants a list of everything I found wrong and the NEC # explaining it. The guy did nice work , only a few small thing wrong.
1. No plastic bushings
2. No separated ground bar in sub panel
3. #2 2-2-2-4 SER cable on a 100 amp breaker. Sub panel is homeline or eaton, I thinks the lugs are 75 degree.