if I pull #4Cu to a subpanel, can I put a 90A main breaker in it? QO main breakers don't come in 85A. I can't find the section in the code that deals with this (if there is one).
In many (most?) applications, that 10a get you nothing useful and costs more money.Why not #3 and 100 amp? 100 amp is more common...
You can put whatever size main you want in the sub as the feeder size is irrelevant. That breaker is just a disconnect.
The breaker in the main which feeds the sub is the one that the size matters on
A main is only required if the sub is in a out building and has more than 6 circuits. OP did not specify the location. Im thinking he is talking about the breaker feeding the sub.You can put whatever size main you want in the sub as the feeder size is irrelevant. That breaker is just a disconnect.
The breaker in the main which feeds the sub is the one that the size matters on
He may be, but the wording definitely points to a main in the subpanel.A main is only required if the sub is in a out building and has more than 6 circuits. OP did not specify the location. Im thinking he is talking about the breaker feeding the sub.
I think having a main breaker in the sub is smart.sorry, yes I'm talking about the main breaker in a subpanel in an attached garage. while I think technically I don't need a main breaker, I'm going to use one anyway since the main panel is in the basement on the other side of house... but the same question applies to the double pole breaker feeding it, I think?
it's separate conductors in 3/4" metal conduit. it'll being running the whole house, which is not at all continuous. seems to vary from about 15A to a little over 30 depending on if the well pump is running at the same time as the furnaces, etc.The generator being continuous doesn't matter, it is what is connected to that. Is the #8 individual conductors in conduit or is it NM cable?
I'm not an electrician, so I'll leave a confirmation to one of the guys here.it's separate conductors in 3/4" metal conduit. it'll being running the whole house, which is not at all continuous. seems to vary from about 15A to a little over 30 depending on if the well pump is running at the same time as the furnaces, etc.
as for 240.4(B).... if I'm reading this correctly, I can go with a 90A breaker to feed the subpanel with #4 if there's only hardwired loads and no more than one receptacle for plug-in loads. did I get that right? this subpanel will be used for a 240V garage heater and future EV charger(s), so yeah they will all be hardwired. now what some future owner might add to it is their issue to work out, right?