Looking for some advice on my A/C woes.
I have a 2500sq ft home in PHX area with a pair of heat pumps, a 3T and a 2.5T Goodman. I think the 3T is a 2004 and the 2.5T is a 2011. Air handlers are from 1999
3 Ton unit
---------------------------------------------------------------------------------------
The 3T wasn't cooling when it was 120 outside. I observed the outside fan not running. It didn't turn freely. I had a friend who owns a A/C business come out and install a new fan. This unit seems OK for now.
2.5 Ton unit
------------------------------------------------------------------------------------
While he was out we heard the 2.5T unit's compressor kick on while the outside fan was running. Assumption here is compressor was in thermal shutdown. He measured cap, currents and line pressures said all looked OK. Later, unit wasn't cooling and I found breaker (20A) tripped.
Got a quote to replace unit but I wanted to know why it took a dump... So I opened it back up and looked for comp/fan coil shorts to GND. Didn't find any issues but noticed the cap (40/5uf) wasn't wired per schematic.
I rewired (Fan and comp start coils were reversed) and as expected, unit started, ran and was cooling. It ran for a few hours and got it's 1/2 of the house to set point.
On subsequent cycle it tripped the breaker (at 11pm, no sun on panel or unit). This morning, unit running I measure 1A of fan current and 7A for compressor which is inline with specs (1.10 and 10.8).
I measured startup current after a short off-cycle, the unit draws 58A (LRA=60) but does so for a few seconds before compressor actually starts. This is enough to trip breaker, but not a normal use case as thermostat has a minimum timer. Unit lists max breaker at 20A. Wire is 6ga. to panel, maybe 20ft.
So the compressor is on its way out, with thermal and starting issues. Since I am a cheap-*** SOB, I would like to keep this turd in service for as long as I can. Would a band aid like a 'hard start kit' (aka cap+relay) limp me though this summer? What else can I check?
Eventually the whole system(s) will have to be replaced.
I have a 2500sq ft home in PHX area with a pair of heat pumps, a 3T and a 2.5T Goodman. I think the 3T is a 2004 and the 2.5T is a 2011. Air handlers are from 1999
3 Ton unit
---------------------------------------------------------------------------------------
The 3T wasn't cooling when it was 120 outside. I observed the outside fan not running. It didn't turn freely. I had a friend who owns a A/C business come out and install a new fan. This unit seems OK for now.
2.5 Ton unit
------------------------------------------------------------------------------------
While he was out we heard the 2.5T unit's compressor kick on while the outside fan was running. Assumption here is compressor was in thermal shutdown. He measured cap, currents and line pressures said all looked OK. Later, unit wasn't cooling and I found breaker (20A) tripped.
Got a quote to replace unit but I wanted to know why it took a dump... So I opened it back up and looked for comp/fan coil shorts to GND. Didn't find any issues but noticed the cap (40/5uf) wasn't wired per schematic.
I rewired (Fan and comp start coils were reversed) and as expected, unit started, ran and was cooling. It ran for a few hours and got it's 1/2 of the house to set point.
On subsequent cycle it tripped the breaker (at 11pm, no sun on panel or unit). This morning, unit running I measure 1A of fan current and 7A for compressor which is inline with specs (1.10 and 10.8).
I measured startup current after a short off-cycle, the unit draws 58A (LRA=60) but does so for a few seconds before compressor actually starts. This is enough to trip breaker, but not a normal use case as thermostat has a minimum timer. Unit lists max breaker at 20A. Wire is 6ga. to panel, maybe 20ft.
So the compressor is on its way out, with thermal and starting issues. Since I am a cheap-*** SOB, I would like to keep this turd in service for as long as I can. Would a band aid like a 'hard start kit' (aka cap+relay) limp me though this summer? What else can I check?
Eventually the whole system(s) will have to be replaced.