I'm well aware it's time to call someone, I just want some advice on what's going on so I don't end up paying for things I don't need to.
Problem; Trane A/C less than 2 years old. Compressor runs for an hour or so, Cools OK. After a while I get a loud humming noise and it stops cooling. Compressor fan still running. Compressor motor gets pretty warm, but not too hot to touch. Evaporator not iced over. Suction line cool to touch- not iced, liquid line not warm or cool. (at compressor) Temp split at coil is ok on start up (16-17 degrees) the longer the unit runs the worse the split gets.
What I've done/checked; Changed filters. Changed batteries in thermostat. Cleaned condenser coil. Checked water drains (float switch). Measured contactor both normal and during humming, no change at line voltage or 24v line. Checked compressor motor for resistance and short to ground,, 0.8 common to run, 1.6 common to start. 2.5 run to start. Check capacitor, measures within 1% of label.
After humming starts; Everything measures out the same, resistance is only slightly higher. Still have continuity between common, run, and start so I don't think it is out on thermal overload.
Problem; Trane A/C less than 2 years old. Compressor runs for an hour or so, Cools OK. After a while I get a loud humming noise and it stops cooling. Compressor fan still running. Compressor motor gets pretty warm, but not too hot to touch. Evaporator not iced over. Suction line cool to touch- not iced, liquid line not warm or cool. (at compressor) Temp split at coil is ok on start up (16-17 degrees) the longer the unit runs the worse the split gets.
What I've done/checked; Changed filters. Changed batteries in thermostat. Cleaned condenser coil. Checked water drains (float switch). Measured contactor both normal and during humming, no change at line voltage or 24v line. Checked compressor motor for resistance and short to ground,, 0.8 common to run, 1.6 common to start. 2.5 run to start. Check capacitor, measures within 1% of label.
After humming starts; Everything measures out the same, resistance is only slightly higher. Still have continuity between common, run, and start so I don't think it is out on thermal overload.