I have a power pole for my dock that recently became submerged when the lake level came up about 13' over a couple days. It is the highest I have ever seen the lake - ANYWAY, it totally cooked the GFCI in the box on the pole, but did NOT trip the breaker. I was wondering, how that is possible? I killed the power to that branch and this weekend replaced the GFCI and everything is good again - but what's up with the breaker? Is that typical, possible, or what would the reason be? It is a 20A circuit and this one outlet is the only thing on it and it was definitely 6" - 12" underwater for a couple days.
The breaker didnt trip because the water provided enough resistance to act as a load and the resistance was high enough that there wasnt a dead short.
In order for a breaker to trip, it would either need to see an overcurrent above its rating, or for a short circuit, no resistance and thousands of amps.
The GFCI cooked simply because the electronics got submerged...
Is the breaker a GFCI breaker? Because it probably should be.
It sounds like the GFCI outlet did it's job and tripped itself properly, but the current leakage was minimal through the water, so it didn't trip the breaker. This is a serious hazard, as if anyone had gone into the water, they could have been electrocuted.
A GFCI breaker would not provide any additional protection here.
An the GFCI cooked not tripped.
That's a tandem.
I would definitely put it on a GFCI breaker with those kind of water problems.
wont do any good since there is no other pathway for the current to become imbalanced between hot and neutral...
This. A GFCI breaker, or another GFCI upstream in the circuit in a location that cannot be submerged would be a good safety addition.
wont make a difference unless there is an alternate path to ground in the panel.
The current will travel right through the person in the body of water and back to the neutral...
Within a small radius of that one outlet that has a neutral and ground wire within a few inches of the 120VAC line, possible. see my link to the electroboom blog above. I could list a whole list of why it's not THAT dangerous to have a single submerged outlet in "fresh" water, but will probably get lost in forum flaming and minutia.
Easy solution, replace the feed breaker with a GFCI type, and inspect the wire for corrosion in a few months after replacing the toasted GFCI outlet.
Not true. People are electrocuted in this exact scenario all the time after they jump into the lake.
Someone the Electrical code discussion group on facebook recently posted an article about a girl who was electrocuted in this exact scenario...
If it is not in conduit, I believe GFCI is required. In conduit, not required.
It's called Electric Shock Drowning or ESD, and it is a very real and very dangerous problem.
http://www.boatus.com/seaworthy/magazine/2013/july/electric-shock-drowning-explained.asp
Yes, if the ground wire was still intact at the outlet, the danger is minimal, but
without a functional GFCI at the source, you have no knowledge of whether or not there is a break in the ground.
Conduit doesnt negate the need for a GFCI...
And the ground wire doesnt provide any additional protection.
And GFCIs dont monitor or care about intact ground wires. A GFCI can function perfectly fine WITHOUT a ground wire attached to the ground terminal. This is because a GFCI only monitors the current on hot and neutral...
Not flaming, but some minutia here. Fresh water is worse BECAUSE it is less conductive. Salt water is more conductive than your body, so you will not experience an electric potential while in the water. Fresh water is the opposite, and current will end up flowing through you.
That being said, if this were in a metal box with a metal cover, and it was all grounded, I don't see much potential for an electric field to escape. But I still would feel more comfortable with upstream GFCI protection.
The direct burial wire is fine. So yeah, it is probably UF (or equivalent). I just wanted to make sure it was not stranded THHN in conduit. THWN may be rated for the insulated wire to be in wet locations, but the bare ends still should not get wet......
Unless there is enough fault current flowing between the hot and the metal box, the breaker wont trip. And obviously in the OPs case there wasnt.
THWN is rated for wet locations...