I may have misunderstood one of the earlier posts but if a gfci trips on land only makes sense it would trip if something connected to it went in the water, what would be a bigger fault other than something connected by a ground wire? It works if it's fed 2 wire and it works for 2 wire equipment,,, which it the basic point, for use with ungrounded equipment but if it has 3 in and 3 out it is a direct pathway other than neutral. Which is also the point and the currents are so much less than what it takes to fault a breaker which could likely even sit in a mud puddle and remain energized.
A GFCI senses the difference in current flow between two different wires and trips if the difference is too great, 5 mA for the typical residential ones. A standard thermal magnetic breaker such as a 15 A miniature residential one trips at about 6-10 times it’s marked setting or 90-150 A for 15 A instantly via a magnetic coil. This is for dead shorts. Or over time down to about 80% of that so 12-15 A so you can surge much higher as in motor starting but sustained overloads trip it.
The impedance through bonding and grounding is much higher than through the main conductors (hot and neutral) so by nature it’s a lot less. Industrially it won’t hardly trip anything by the time you get to say a 100 HP. The connection between the grounded equipment housings (called bonding in Code) goes back to a single connection (system bonding jumper) at the service entrance. That’s also where the ground rod connects.
Code allows smaller wiring in the bonded circuit and allows steel and aluminum conduit, boxes, etc., to be part of the circuit. Since it only gets used during faults and theoretically even then for short periods this is all legal but a little corrosion totally eliminates it. Worse still is the practice of “peg grounding” which causes stray voltage and noise and interference in ground loops.
Typically when I measure it I get around 0.1-1 ohm with ground wiring like the ground wire in residential NM-B cable. It goes to around 3-10 ohms to the load in conduit if it’s new. With flexible metal conduit after a couple years it’s open. It measures 1.000-10.000 ohms...typical background/concrete and earth resistances with NO intentional grounding). So on a 15 A breaker at 12 A that’s about 120 V / 12 A = 10 ohms. So even in typical corroded up steel or aluminum conduit at a dock trying to get the breaker to trip even without passing through water is iffy at best. A ground rod is supposed to be under 25 ohms by Code. They vary a lot with soil but probably half of them are over 10 ohms.
What really happens is once everything gets melted and heated (welded) together from the arcing, you get a line-to-line (dead short) and then the breaker trips typically in under a second unless it’s a GFCI. Then just a heavy dew or fog will trip it. Nobody pays ground faults much respect in reality based on 25+ years of industrial experience.