A/C Unit Breaker tripping

jaado

Member
Joined
Aug 2, 2010
Messages
7
Recently I observed that my A/C Unit (downstairs) one keeps tripping once in a while. Especially when I use my clothes dryer or sprinkler system, its the A/C breaker is going off and i have to put it back.
It works fine after I put it back and after a while its breaking. Happening now a days mostly on weekends.

Any suggestions if I can troubleshoot it or need to call the A/C or electrical guy? confused.


My house is brand new 4 yeard old and so are the HVAC units..

thanks.
 
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
sounds like voltage drop from a bad connection somewhere. Get a licensed electrican out there to look at it.
 

bazar01

Well-known member
Joined
Jan 30, 2009
Messages
326
Location
Leesburg, GA
Recently I observed that my A/C Unit (downstairs) one keeps tripping once in a while. Especially when I use my clothes dryer or sprinkler system, its the A/C breaker is going off and i have to put it back.
It works fine after I put it back and after a while its breaking. Happening now a days mostly on weekends.

Any suggestions if I can troubleshoot it or need to call the A/C or electrical guy? confused.


My house is brand new 4 yeard old and so are the HVAC units..

thanks.

Is your A/C unit, and clothes dryer on the same circuit? The sprinkler system only consumes a very small power so that is out.
If you have a clamp type ampmeter, that is the only way to get the actual draw on the circuit and compare that to your circuit breaker rating.
 
OP
J

jaado

Member
Joined
Aug 2, 2010
Messages
7
Ok.. Looks like I have to call up the electrician to come and have a look at it..

Is there is any chance that is has to do with the A/C unit.. as only that is breaking. The upstairs A/C unit is fine though it may not be running all the time..
 

sams ron

Member
Joined
Aug 3, 2010
Messages
5
If the breaker trips right away after unit starts (like within seconds) it's probably the compressor which is a fairly costly fix.

If it runs for five minutes or so before it trips, it is most likely a run capacitor. Expect to pay about 32.00 plus service charge.

some units do have hard starts as mentioned by the previous answerer, that can do it also, but not all units have hard starts.
 
OP
J

jaado

Member
Joined
Aug 2, 2010
Messages
7
thanks to all for your useful replies..

The unit runs for sometime ranging from 1hr to weeks by itself and all of a sudden it keeps tripping every one 1-2 hrs when I am using my clothes dryer.

But last night the breaker went off by itself with no dryer being used.
Later today when I go home I will see if it breaks and will post it. Will call the electrician and ask him to check.. hopefully its a small fix. :)
 

rockchucker

Well-known member
Joined
Mar 27, 2010
Messages
1,764
Location
Seattle WA
100% ^


Also make sure all of the Wires are very tight that go into the Breaker. My buddy decided to do his own panel at one point in time and called me out due to issues with his Pump tripping the Breaker...Needless to say he was lucky he did not have a fire. Most all of the connections were only barely finger tight. They MUST be very tight when dealing with heavy loads. Something to check for free anyways.

Of course turn off the Main while doing this blah...blah...blah...
 
To avoid these ads, REGISTER NOW!
OP
J

jaado

Member
Joined
Aug 2, 2010
Messages
7
so the a/c tech came over and checked all the connections, capacitor etc and said everything was fine and it might be a bad breaker.
The breaker and the dryer ones are facing each other in the breaker box and he said sometimes it might be getting heated and replace that with a 30 amp one.
I went to lowes to get the 30 amp one and the dude over there scared me off saying that amp should not be increased only decreased as it may catch fire...
Well i returned back with a 20 amp one and the tech replaced it for me.. (luckily my home is nearby to lowes and he waited.. he didn't have that model with him)

hopefully this fixes it :)
 

burleymike

Well-known member
Joined
Feb 25, 2009
Messages
935
Location
SE Idaho
What size wire is the dryer on #10 can handle a 30 amp breaker. I am assuming we are talking about an electric dryer.
 

bonneyman

Well-known member
Joined
Apr 22, 2010
Messages
8,779
Location
Desert SW
What brand of breaker is it? I just learned (the hard $$$$$$ way) that FPE (Federal Pacific) style breakers stink and can cause fires. Have to have my main breaker panel replaced - old FPE's are a problem, according to the electrician.
 
OP
J

jaado

Member
Joined
Aug 2, 2010
Messages
7
not sure whats happening but my breaker went off again... looks like this will be a long fix...
 

cowboyjosh

Well-known member
Joined
Mar 11, 2010
Messages
1,066
Im betting on a loose connection or bad breaker if your AC guy checked the AC out and gave it a clean bill. Also on the outside disconnect to make sure all connections are secure there as well.

Another thing you might want to check is the wiring itself, is there any visible damage between the box to the outside disconnect? Is there any damage between the disconnect outside to the outside condenser unit? Have already seen where the insulation is nicked and grounds itself out when there is any vibration.
 
Last edited:
OP
J

jaado

Member
Joined
Aug 2, 2010
Messages
7
All connections were checked and he did leave something on the wires to check the amp for around 30-45 min..

thats what I am thinking, will take a second opinion from a different a/c guy most likely.

Lately my garage is very hot (its like 106 in dallas from last two weeks) and my main breaker unit door is kinda not properly closing. Does this have to do with the amount of heat in the garage by any chance?

thanks.
 

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
I doubt it. I would make sure you have the correct size breaker and wiring for the unit. You may just be right up against the limit on the permissible load before the breaker trips. This unit is working hard and under heavy load in your climate. The breakers are thermal units and they have trip curves that are very interesting. Not what you would think. Google inverse time delay breakers and look at the current vs time for their trip curves.
 