ishiboo
Well-known member
Okay, I know the correct answer for the question but I'm looking for some additional input.
My property has 3 meters right now, the house has 2 and it WAS a duplex, and the barn has one. The barn is approximately 115' from the house. We currently have 100A service at the house and it meets our needs.
With the current service entrance being busted, and the fact we'd like to add a propane generator with automatic transfer switch, I'd like to power the house completely from the barn and eliminate 2 meters ($17/month), separate power bills (they will not combine), etc.
1. Since the house already has correct grounding as well as the barn, I'd like to run 4/0 4/0 2/0 without ground between the two, and leave the two separate ground points. I know in a typical sub panel I would run 4-wire, however do you think this is logical and acceptable?
2. The run will be approximately 160'. At a 200 amp service, this gives me a maximum continuous load of 160A. The voltage drop calculator I am using gives me a 1.8% drop at 240v... I do use 240v and not 120 since I have the two legs, correct? 120 which would give me 3.7%... would that be acceptable? I know >3% is right at the line.
3. My current panel in the barn is a QO. A 100A breaker on the current QO will not handle 4/0. How do you recommend I get between the two? I am thinking a disconnect switch and then running a smaller copper rated for 100A between the two.
Thanks in advance... this is an emergency as we have no well water, so I have to execute fast!
My property has 3 meters right now, the house has 2 and it WAS a duplex, and the barn has one. The barn is approximately 115' from the house. We currently have 100A service at the house and it meets our needs.
With the current service entrance being busted, and the fact we'd like to add a propane generator with automatic transfer switch, I'd like to power the house completely from the barn and eliminate 2 meters ($17/month), separate power bills (they will not combine), etc.
1. Since the house already has correct grounding as well as the barn, I'd like to run 4/0 4/0 2/0 without ground between the two, and leave the two separate ground points. I know in a typical sub panel I would run 4-wire, however do you think this is logical and acceptable?
2. The run will be approximately 160'. At a 200 amp service, this gives me a maximum continuous load of 160A. The voltage drop calculator I am using gives me a 1.8% drop at 240v... I do use 240v and not 120 since I have the two legs, correct? 120 which would give me 3.7%... would that be acceptable? I know >3% is right at the line.
3. My current panel in the barn is a QO. A 100A breaker on the current QO will not handle 4/0. How do you recommend I get between the two? I am thinking a disconnect switch and then running a smaller copper rated for 100A between the two.
Thanks in advance... this is an emergency as we have no well water, so I have to execute fast!