Having just spent the weekend combing this forum I'm very aware of the numerous "sub panel in the garage" questions that have been posted here. Unfortunately none of them seems to address my particular issue so I guess I'll add to the litany of sub panel questions already here.
First some background:
Mine is a small, detached one car garage (14'x20') with a 12'x12' shop stuck on the back. It's currently fed by one 20A-120V circuit that runs lights, a 25 gallon air comp. , a table saw, a mitre saw and garage door opener. I plan on adding a 100A main wired as a sub in the garage fed via three 4AWG CU conductors (plus ground) from a 60A or 80A 240V breaker installed in the house panel (currently 100A service; no A/C; all gas house except for clothes dryer). Future additions in the garage will include a small electric heater (Fahrenheat/Dayton G73 type) and maybe a small MIG welder.
I've wired subs before, so I'm familiar with separating the neutral and ground
busses, installing ground rods for the sub, etc. What I'm struggling with is how to get the feeder from the house to the garage. My tiny excuse of a garage is separated from the house by concrete...everywhere...While it takes different forms (driveway/poured concrete patio/rear bedroom addition on concrete slab) from the north side of the lot to the south side of the our city sized lot is nothing but concrete. So my options for running the feeder seem to come down to these:
#1 Cut the driveway and dig a trench for an underground conduit run directly from the basement mounted main to the sub in the garage (abot 20'-25'). This is the shortest run but probably the most expensive as I'd have to pay a mason to repair the driveway.
#2 Run the feeder across the basement (about 15'), around my furnace/hot water tank and through a brick wall and into a conduit hung on the inside wall of our enclosed patio. After travelling the fifteen foot length of patio the conduit would enter a trench in the yard that would travel the last five or so feet to the garage. I would eventually box-in the exposed conduit in patio since "industrial" isn't how the patio is decorated.
#3 Run the feeder almost all the way across the basement (20 ft) and then to the rear of the house where it would enter 2" Rigid snaked underneath the rear house addition. This addition is a slab but is set on a modest brick foundation so, while there's no crawl space, per se, there is a void space that would accept the 2" Rigid. (Since the NEC only requires 2" Rigid to be supported every 16 feet and the addition is only 15 feet long, I shouldn't have to worry about supporting it from underneath the slab.) The feeder, once it emerges from underneath the slab, would then enter a trench and travel the ten or so feet to the garage.
#4 Run the feeder out of the basement, up the side of the house and then cross the driveway at a height of 12' via messenger supported overhead wire to a mast that would need to be supported by guy wires at the garage end. (Shed roof on garage is only 9.5' above grade).
Now it's your turn. What do I do? In my mind, option one and option four seem the most straight-forward. Option one would cost more as I'd need a pro to fix the driveway but it is the most direct run using the least amount of materials. Option four is almost as direct as option one, but would require more cable and materials to make it work plus, as I've never run wire overhead, I'd need to figure out exactly what such an endeavor involves before I commit. The other options are doable (I think) but really give me heartburn when I think about them.
So there you have it...another sub in the garage question but with a twist. Thanks in advance for the input and advice.
First some background:
Mine is a small, detached one car garage (14'x20') with a 12'x12' shop stuck on the back. It's currently fed by one 20A-120V circuit that runs lights, a 25 gallon air comp. , a table saw, a mitre saw and garage door opener. I plan on adding a 100A main wired as a sub in the garage fed via three 4AWG CU conductors (plus ground) from a 60A or 80A 240V breaker installed in the house panel (currently 100A service; no A/C; all gas house except for clothes dryer). Future additions in the garage will include a small electric heater (Fahrenheat/Dayton G73 type) and maybe a small MIG welder.
I've wired subs before, so I'm familiar with separating the neutral and ground
busses, installing ground rods for the sub, etc. What I'm struggling with is how to get the feeder from the house to the garage. My tiny excuse of a garage is separated from the house by concrete...everywhere...While it takes different forms (driveway/poured concrete patio/rear bedroom addition on concrete slab) from the north side of the lot to the south side of the our city sized lot is nothing but concrete. So my options for running the feeder seem to come down to these:
#1 Cut the driveway and dig a trench for an underground conduit run directly from the basement mounted main to the sub in the garage (abot 20'-25'). This is the shortest run but probably the most expensive as I'd have to pay a mason to repair the driveway.
#2 Run the feeder across the basement (about 15'), around my furnace/hot water tank and through a brick wall and into a conduit hung on the inside wall of our enclosed patio. After travelling the fifteen foot length of patio the conduit would enter a trench in the yard that would travel the last five or so feet to the garage. I would eventually box-in the exposed conduit in patio since "industrial" isn't how the patio is decorated.
#3 Run the feeder almost all the way across the basement (20 ft) and then to the rear of the house where it would enter 2" Rigid snaked underneath the rear house addition. This addition is a slab but is set on a modest brick foundation so, while there's no crawl space, per se, there is a void space that would accept the 2" Rigid. (Since the NEC only requires 2" Rigid to be supported every 16 feet and the addition is only 15 feet long, I shouldn't have to worry about supporting it from underneath the slab.) The feeder, once it emerges from underneath the slab, would then enter a trench and travel the ten or so feet to the garage.
#4 Run the feeder out of the basement, up the side of the house and then cross the driveway at a height of 12' via messenger supported overhead wire to a mast that would need to be supported by guy wires at the garage end. (Shed roof on garage is only 9.5' above grade).
Now it's your turn. What do I do? In my mind, option one and option four seem the most straight-forward. Option one would cost more as I'd need a pro to fix the driveway but it is the most direct run using the least amount of materials. Option four is almost as direct as option one, but would require more cable and materials to make it work plus, as I've never run wire overhead, I'd need to figure out exactly what such an endeavor involves before I commit. The other options are doable (I think) but really give me heartburn when I think about them.
So there you have it...another sub in the garage question but with a twist. Thanks in advance for the input and advice.