AC capacitor?

DocPhilMD

Well-known member
Joined
Dec 28, 2015
Messages
157
Location
Mid Michigan
Hello guys. Question about my AC unit. A couple weeks ago, condenser would kick on but not the fan. Fan would spin after manual start. I took off the cover and the capacitor was a rusty piece of junk. Replaced it.

Today I turned unit on and it worked for about 5 seconds and shut off. Breaker flipped. Now, it won't turn on at all.

I tried attached some pics and the capacitor I got. Bad capacitor? Wrong capacitor?

Unit is a Lennox HS29-036-1P

https://www.amazon.com/gp/aw/d/B00EZPMNBA/ref=sxl1?qid=1465661621&sr=1&pi=AC_SX236_SY340_FMwebp_QL65
 
To avoid these ads, REGISTER NOW!
OP
D

DocPhilMD

Well-known member
Joined
Dec 28, 2015
Messages
157
Location
Mid Michigan
How do I test that? Check amp draw at the fan motor?

Any instructional videos on how to check amp draw at the fan? This would be my first time
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
That is the proper size cap for that unit, do you have a meter that can test a capacitor? Having a cap go bad can happen but isn't that common for it to happen that quickly.
 
OP
D

DocPhilMD

Well-known member
Joined
Dec 28, 2015
Messages
157
Location
Mid Michigan
That is the proper size cap for that unit, do you have a meter that can test a capacitor? Having a cap go bad can happen but isn't that common for it to happen that quickly.

I have a basic DMM but now is probably the time to invest in a meter that tests capacitance and amp draw. Anyone you guys recommend?
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
I have a basic DMM but now is probably the time to invest in a meter that tests capacitance and amp draw. Anyone you guys recommend?

You will get a bunch of guys saying Fluke and they are nice but I feel you are paying for the name to some degree, I use a fieldpiece sc440 and it does everything I need.
 
OP
D

DocPhilMD

Well-known member
Joined
Dec 28, 2015
Messages
157
Location
Mid Michigan
OKay. I think I figured it out and this is of course a newbie mistake.

The new capacitor came with a yellow mark on one connector. I let my caveman brain that likes colors take over instead of looking at the number of fittings on each connector. I've never worked with capacitors before so I assume the number of connectors is more important than a spray painted dot. So I moved the wires around and it works! I think I had it hooked up wrong.

Here is a picture of the original connectors, how I had it first then how i have it now. Can someone confirm and explain what those different number of connectors means?

In my terms, I changed it so that the wire that was hooked to the two prong connector went to the new 2 prongs (purple), the three prongs to three (yellow) and the four to four (red)
 

Attachments

  • IMG_20160528_182340958.jpg
    IMG_20160528_182340958.jpg
    133.3 KB · Views: 63
  • IMG_20160611_140206412.jpg
    IMG_20160611_140206412.jpg
    138.9 KB · Views: 60
  • IMG_20160611_141831090.jpg
    IMG_20160611_141831090.jpg
    130 KB · Views: 57

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
OKay. I think I figured it out and this is of course a newbie mistake.

The new capacitor came with a yellow mark on one connector. I let my caveman brain that likes colors take over instead of looking at the number of fittings on each connector. I've never worked with capacitors before so I assume the number of connectors is more important than a spray painted dot. So I moved the wires around and it works! I think I had it hooked up wrong.

Here is a picture of the original connectors, how I had it first then how i have it now. Can someone confirm and explain what those different number of connectors means?

In my terms, I changed it so that the wire that was hooked to the two prong connector went to the new 2 prongs (purple), the three prongs to three (yellow) and the four to four (red)


There are markings on the cap, fan, common and herm(for hermetic compressor).

In your case the purple goes to fan, red to common and yellow to herm, the colors could be different depending on brand but I looked yours up on davenet to be sure.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
A dual run cap has three terminal groups- "C" (Common), "Fan" (Fan) and "Herm" or "Comp" (Compressor.) The wire from the contactor goes to "C". The wire from the fan start winding goes to "Fan" and the wire from the compressor start winding goes to "Herm".
Looking at the wire colors, you have it right now.

Tommy
 
Last edited:

manwithtools

ALLIANCE MEMBER
Joined
Aug 24, 2015
Messages
14,064
Location
Lebanon, TN
WTF? "Herm" instead of "Compressor"

That is priceless, the most evidentiary proof that the HVAC industry wants to insure they get to do the service work. That's it, I need to take the exams to get the certification to do my own HVAC work.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
"Herm" is no "industry secret" or code word. :lol_hitti It's short for "hermetic". Internally driven welded shell compressors are hermetic compressors. I have NO idea why it's that way on the capacitor, but it's been that way since before I started in the trade.

Tommy
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
"Herm" is no "industry secret" or code word. :lol_hitti It's short for "hermetic". Internally driven welded shell compressors are hermetic compressors. I have NO idea why it's that way on the capacitor, but it's been that way since before I started in the trade.

Tommy

Exactly, I figure if they shorten up compressor to com it would get mistaken for common.
 
To avoid these ads, REGISTER NOW!

TheEquineFencer

Well-known member
Joined
Jan 15, 2009
Messages
9,278
Location
Farmville, NC 27828
You will get a bunch of guys saying Fluke and they are nice but I feel you are paying for the name to some degree, I use a fieldpiece sc440 and it does everything I need.

A Fluke is like anything else, you get what you pay for. Mainly the warranty, Lifetime and VERY accurate. I have several meters and depending on what I'm working on dictates which meter I use.

An example is when I worked at Cummins. I had a customer's generator they said had low voltage output and he wanted it load tested and the voltage checked. I load banked it and raised the Hz slightly, about 1 Hz. I finished and he came to pick it up and went off on my service advisor because it wasn't right. I got called out to recheck it. I did and then the customer whips out this wall socket plug in meter that was reading 117VAC and said the voltage wan't right. I stick my Fluke 87V into the socket tight above it and it says 120.2VAC. Then he starts in about his meter is brand new and is right. After I quit laughing, I went back to my tool box and came back with my Calibration Certificate for mine and asked to see his and asked him which he thought was more accurate, his $20 Camping World Meter or my $700+ Calibrated and tested Fluke?

I like the meter recommended and If I run across one I'd probably buy it. Lowe's sells a Southpoint brand I've used of another guys at work, it's OK but I like the way the functions on my Fluke work better.

The main functions I look for are the ability to test Caps and Hz, most meters will do everything else.
 

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
That sc260 doesn't appear to do DC microamps, you need DC microamps to check flame sensors on modern furnaces, if that's not a need then don't worry about it.

Sent from my XT1254 using Tapatalk
 
OP
D

DocPhilMD

Well-known member
Joined
Dec 28, 2015
Messages
157
Location
Mid Michigan
and thank you all once again for all the help.

I am not on here very often but you guys are great when I come on. if you have a medical question, feel free to PM me and we can take it offline
 

dclassical

Well-known member
Joined
Sep 25, 2008
Messages
1,130
You will get a lot of opinions about meters... I do like Fluke. I have been around high end electronic equipment for a long time (not at home).

I got a Fluke 189 and this is my reasoning for the choice I made.

- The 115 series (116, ...) are made in China and have a one year warranty, so I did not want that. Though I have a friend who does a lot of TV repairs (and electronics) with a 115 and a scope.

- The 28x are very nice with data logging features but I don't see needing them (at home) very often. Can be nice.

- The 87V is extremely nice and precise. I don't feel the need for that at home.

So I got the 189. Well built, not too pricey (~$300 with accessory kit).

If I want data logging, duty cycle, ... I can use my oscilloscope.
 

crabjoe

Well-known member
Joined
Jul 15, 2012
Messages
197
Location
Ceciltucky, MD
I noticed no one mentioned True RMS. If you're going to get a new meter, make sure it's a True RMS meter.

I personally have the Fieldpiece SC440, but for homeowner use, it's a bit pricey and a bit of an over kill. If I were to do it again, I'd probably buy a Uni-T UT210E. It's a True RMS clamp meter, it does capacitance, and can be had for under $40.

My buddy has some older Fluke that he used, when he was an HVAC tech ... He's no longer in the HVAC business, but he wanted a True RMS meter for around the house, so he picked up a Uni-T. He said the measurements are almost identical to his old Fluke and it was cheap.
 

joel63

Well-known member
Joined
Oct 9, 2012
Messages
1,912
Location
Central FL
I noticed no one mentioned True RMS. If you're going to get a new meter, make sure it's a True RMS meter.

I personally have the Fieldpiece SC440, but for homeowner use, it's a bit pricey and a bit of an over kill. If I were to do it again, I'd probably buy a Uni-T UT210E. It's a True RMS clamp meter, it does capacitance, and can be had for under $40.

My buddy has some older Fluke that he used, when he was an HVAC tech ... He's no longer in the HVAC business, but he wanted a True RMS meter for around the house, so he picked up a Uni-T. He said the measurements are almost identical to his old Fluke and it was cheap.

What is the advantage of a True RMS meter?
 

Brian_WK

Well-known member
Joined
Jun 30, 2015
Messages
1,177
Location
NE South Dakota
The Fieldpiece SC440 is a darn good do it all meter for HVAC and residential use. I have one for work but my home meter is an 13 year old UEI from college. I like both and have not had an issue with either.

Brian
 

homebuilt burner

Well-known member
Joined
Dec 8, 2014
Messages
1,763
Location
central Wisconsin
This is a difficult question because everyone works on different things. I am a diesel mechanic and I work part time for a farm equipment dealer. Up until a month ago my Fluke 73 III was all I ever needed. But then, I got working on silo unloaders and needed to check capacitors and the 73 won't do it. So now I am thinking about a 115 (yes they are Chinese) but the 115 doesn't have an amp clamp so I would have to get an external clamp the same as my 73.

So it depends what you want to do. Personally I have a $20 cheapie at home and if I get in deeper than that I take my fluke home from work or borrow someone else's.
 

TheEquineFencer

Well-known member
Joined
Jan 15, 2009
Messages
9,278
Location
Farmville, NC 27828
I've been kicking myself in the butter for a while now. I found two Fluke 87V meters on CRAIGSLIST, one for $100, the other for $125, both like new w/box ect. I told a good friend of mine about them as he was wanting one. He asked if it was ok if he got one that was closers to him and I said OK. I go to get the other one and it a Fluke83. The one he got was Brand New in the box and was a certified calibrated with the paperwork and had the Deluxe leads. He still owes me a nice meal.
 