AC clamp Meter. What's it actually reading?
seagull369
This question is in regards to a true-RMS clamp meter set on amps ac,,, On the non-inrush setting, is the value displayed considered to be a true-RMS reading of the current waveform it's analyzing? When on the inrush current reading, is that simply just giving you the largest peak current (I-max) value it's able to capture?
u2slow
BC
Your first question.... A true-rms meter gives you an true-rms reading. That's the whole point.
The second.... you have to find out how the manufacturer defines the feature. I suspect it will be the RMS value of whatever inrush it captures.
RPH
Michigan Thumb
As with anything electrical math is involved. Most use a resistor used as bourdon resistor across transformer windings. This measures a voltage drop across it. The math is required for the types of non-sinusoidal waveforms.
dave*99
Coastal NJ
I think you mean burden resistor.
Bourdon invented the Bourdon tube for measuring gas pressure.
dave*99
Coastal NJ
Thankfully the true RMS meter does the math. Often the waveform that must be measured is a combination of more than one of those neatly drawn waveforms.
The true RMS meter digitizes the signal and calculates the reading.
A simple way to think of RMS is it is the heating value of the waveform.
If you connected a resistor to a DC source and measured its temperature then switched to a complicated AC waveform and the resistor rose to the same temperature…… you would know the RMS value was the same for both.
rlitman
Long Island
Is your meter an AC only clamp meter, or an AC/DC current clamp. They work fundamentally differently.
Also, most meters sample more quickly than they refresh their displays, so your inrush measurement will likely be higher than a max-hold type current reading, if your meter has both modes.