I am bring ACWU90 2 gauge 3 conductor into my garage. What is the best way to get it from the outside to the inside? I was thinking running it into an LB connector on both sides, only issue is I would need to run the cables out of the coated BX to do that. Is this the best way or is there a better way?
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Is this a service from a meter base or a branch circuit from a main service panel. I assume it's an under ground run. My gut tells me you got the wrong wire. It should be 4 conductor. Plus what country/state are you in?
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
D

Deranged_1

Well-known member
Joined
Apr 23, 2012
Messages
97
Location
Ottawa, Ontario, Canada
Here it's called a 2/3 they don't specify the ground but there is one. It's the same thing as Armorlite. My question is how to get it in the panel since it needs to basically do a 180 down to the panel.
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Why does it need to do a 180? Are you coming up from below the panel then up and over and back down through the top of the panel? Anyway, if you need to make a tight turn, I'd assume you'd need to cut the armor and put a box at the turn point. I take it the armor will not bend to the radius you need?
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
In your first post you said it is a 3 conductor cable. Also, is this wire CU or AL?

The 3 conductor comment threw me too. I believe the Armorlite style cable only comes with copper conductors. The nomenclature for the Armorlite is the same as NM where the ground is not included in the conductor count identifier.

Edit: For curiosity I looked up the ACWU90 and it appears to be Al conductors.

Deranged, are you in Canada?


*
 
Last edited:
OP
D

Deranged_1

Well-known member
Joined
Apr 23, 2012
Messages
97
Location
Ottawa, Ontario, Canada
Yup I am in Canada, I should update my profile. well I need to come into the wall from the outside to the inside and either feed the panel from below or above. Either way they are tight turns so I was thinking LB connectors would work but I would need to remove the armor and run the cables trough the lb conduit.
 
Last edited:

awdblazer

Well-known member
Joined
Oct 17, 2011
Messages
1,100
Location
winnipeg, manitoba, canada
just sleeve it
i would put a 90 from your trench to a little stub to the lb into your garage
make sure it is big enough, i would use like 2 inch forsure to make it around the lb
 

tfi racing

Well-known member
Joined
Apr 19, 2008
Messages
2,907
Location
Cedar,BC
1 1/4" PVC conduit and LB will be fine,if you don't want to work as hard,go with 2".No need to strip the cable,you are just using the PVC for supplemental mechanical protection(and for appearance) on the exterior of the buildings,ACWU can be run as is just about anywhere,inside,outside underground.:beer:
 