Here's the quick synopsis. House with a detached garage, electric coming into it is a 2 wire cable (hot and neutral, no ground). How can I fix this short of digging up the cable and replacing it?
Here's the quick synopsis. House with a detached garage, electric coming into it is a 2 wire cable (hot and neutral, no ground). How can I fix this short of digging up the cable and replacing it?
Since it's detached I think it needs its own ground anyway. So drive in ground rods, etc. whatever is easiest for the situation and meets local code.
Not sure of your garage setup, but if it were me, I'd dig it up, bury conduit, and pull new conductors. I did this last year when I wanted to upgrade my garage service with a 60A subpanel.
Since you asked for something "short" of that, there's not other good way to pull a proper ground wire from your house panel, so you could ground the detached garage locally by driving an 8ft ground rod into the soil and running a ground to your local garage panel (assuming you have one, if not your should get one because that's the only proper way you'll be able to distribute a ground to the rest of your garage circuits.
If the whole garage is on one circuit, then I suppose you could tie the new ground conductor directly into your newly grounded circuits, but a local panel is so easy and provides you the ability to separate some circuits (lights from outlets, etc), it'd be worth the bit of investment into the garage.
A word on code: Post NEC2008, the local building ground isn't considered code and you need to ground the detached building back to the main house panel, and do NOT have the neutral bonding screw in the local garage sub panel. The risk is chassis ground current faults is pretty minimal if you do it with the local grounding rod, but technically correct is the best kind of correct.
This is completely wrong.
A ground rod or electrode is NOT the same thing as an equipment ground, which provides a low impedance fault current pathway. Fault current will NOT flow on ground rods back to the main panel to facilitate a breaker trip.
Tying the GEC from a rod to the ground terminals on outlets is DANGEROUS advice. DO NOT DO THAT.
And your word on code is wrong as well.
"The local building ground" im assuming you mean ground rod, and that has always been required. However, that NEVER provided the EGC between the sub and main. Prior to 2008, the neutral in a sub in a DETACHED BUILDING was allowed to be bonded and was used as the EGC. After 2008, a separate ground wire is required IN ADDITION to ground rods.
You really need to study up on the difference between grounding conductors and grounding electrodes.
There is an article in the Electrical FAQ thread you could read.
Yes, it goes to service neutral main. Old code allowed 3 wire feeds if there were not other interconnecting pathways. This all worked till someone came along and added a phone line or metal piping, water or gas then it made for alternative pathways for neutral currents as the N and the G needed to be bonded on 3 wire to have a pathway for faults back to the main.where does the current go to trip the breaker, the transformer on the pole?
So a ground conductor must be run from the detached building to the main panel (where the neutral and ground bus are connected) where does the current go to trip the breaker, the transformer on the pole?
Just asking as it was wired without any type of ground going back to the panel. Damn there were live wires just cut and hanging outside of boxes. Also wires were just stuck into boxes with no clamps.
I guess I'll have to run new power to the garage with the correct stuff.
So I need a ground rod and a ground going back to the box in the house?
Yes, it goes to service neutral main. Old code allowed 3 wire feeds if there were not other interconnecting pathways. This all worked till someone came along and added a phone line or metal piping, water or gas then it made for alternative pathways for neutral currents as the N and the G needed to be bonded on 3 wire to have a pathway for faults back to the main.
If this is a 3 wire feed t needs a bond. As a side note here a while back I put a wire in and an old timer came back and hooked the panel up. He left the 4th wire dangle and used 3 while adding the bond screw as I recall. He had commented to someone,,, I am not sure what the 4th wire was for.
4 wire keeps all the operating currents insulated, neutrals are insulated and with everything hooked together keeps anything metal at the same potential. No difference between any 2 pieces in the event of a fault.
As was mentioned the ground rods are for lightening and some step potential between the equipment and the ground you are standing on.
Copied from another forum.
The panels in separate buildings are not really subpanels as far as code is concerned. They are the service equipment for the structure. You can have a subpanel from the service equipment in each building if you want. Between buildings, section 250.32 applies and if there are metal interconnections between buildings such as water piping, or air lines, or any metal interconnection at all, then you must install an equipment ground wire so if you have a 120/240 system, you would have four wires. The neutral would be separated in each building and a grounding bar would be installed, just like a subpanel. Then the code requires a grounding electrode conductor (GEC) to a grounding electrode (usually a ground rod). The GEC will be connected to the equipment ground bar at each building. This is not to clear overcurrent devices, this is for two reasons. One is lightning, the more important one is to put the equipment ground at the same relative potential as the earth. This is for step potential or touch potential voltages so that what you touch in the building is at the same potential as what you are standing on. Now the tricky part. If you do not have any interconnecting metal between buildings, the code allows you to install three conductors between buildings. When you do this you bond the neutral and ground the neutral just like a new service. Some inspectors think that every panel in a separate building must be treated as a subpanel, but this is not true.In past codes (1996 and older) these rule were in section 250-24 and Exception 2 addressed the grounding bus.
Last changed: June 17, 2002
If the 2-wire service is in a conduit, disconnect it and use that for pulling a messenger line through. Then use the messenger line to pull the original 2 wires plus a ground through.
The ground does not need to be in the same jacket.
The ground is not one of the conductors in any circuit; it is a separate ground, and is in the same raceway/conduit.
The ground is made of conductive material but is not one of the conductors in the circuit.

Try not to get too hung up on these names.![]()
Is that where it says that current carrying conductors should be in the same jacket?
I think one thing that confuses many people (including ez-duzit), are the abbreviations "EGC" & "GEC", and the difference between the two. The old saying "Ground is ground the world around" doesn't apply here.
ground and grounding, bonding, & lightning ground,
can get confusing to the layman. You need 3 wires hot, neutral, & ground, ground and neutral are separate all the way back to the main panel where they connect and go the ground rod and service ground. With 3 wires you still need a ground rod at the end of your run.Ground wire goes to it, the neutral and grd. do not connect at this point. You can add a ground wire separate from the feed cable if you want ?
Why are people making this so hard?


For anything coming off the main panel you need a neutral, an EGC, and one or two hot legs - 120 or 240 volts...Why are people making this so hard?
Because of misinformation?
You don't need neutral for a 220-volt circuit, just 2 out of phase 110-volt legs and ground.
...True, you don't need a neutral for a straight 240 volt circuit, but guess what - many of us will pull one anyway - plans change....