Adding 2 220V outlets out to my garage.

Rebelman

Member
Joined
Jan 17, 2017
Messages
9
Hello! I'm new to the garage journal as of today. I'm wanting to put 2 220v outlets out in my garage. I need one for my air compressor and I have 10/2 wire and a 30 amp breaker for this and one for my welder and I have 6/2 wire and a 50 amp breaker for this. 2 separate runs ok or is there something that is probably easier? Thanks for any help.
 
To avoid these ads, REGISTER NOW!

Radix2

Well-known member
Joined
May 28, 2014
Messages
1,853
Location
the thumb!, MI
Detached garage? If so, you need to go out with one feed and then split off from a panel there ( only one feed to a building allowed)

If attached, it may still be easier to go with one feed and put a small panel rather than running direct, up to you.
 
OP
R

Rebelman

Member
Joined
Jan 17, 2017
Messages
9
Garage is attached to the house. I'd probably have to run a 6/3 wire to have a panel out there.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
Do one feed to a subpanel then run your individual circuits from there.

It will be cheaper this way.

Where is your main panel?
 
OP
R

Rebelman

Member
Joined
Jan 17, 2017
Messages
9
Main panel is in the basement, garage is about 16' away.

Sent from my SM-T230NU using Tapatalk
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
So run something like #4-4-4-6 AL SER or #2-2-2-4 AL SER which will give 70a or 90a respectively.

put in a small subpanel making sure to isolate the neutral bar which most likely means buying a ground bar kit.

What is the HP rating on the compressor?
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
At 16 ft it would depend on my need for space, if I had plenty in the main simply run 2 wires. As long as it's not a 250 mig it can be 10 cable for the welder. If it's a 200 mig a 30A will work, if you want to use a buzzer it needs a 50A.
 
OP
R

Rebelman

Member
Joined
Jan 17, 2017
Messages
9
Air compressor is a puma 6 gal 3.2 hp 230v / 1hp and the welder is a lincoln 225 arc welder. The compressor says the breaker size (trip rating) for circuit breaker is 35A, for fusible switch (melting style) the 30A dual element time delay fuses are suggested. The welder calls for a 50A.

Sent from my SM-T230NU using Tapatalk
 
To avoid these ads, REGISTER NOW!
OP
R

Rebelman

Member
Joined
Jan 17, 2017
Messages
9
How far off the floor does a sub panel need to be?

Sent from my SM-T230NU using Tapatalk
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Air compressor is a puma 6 gal 3.2 hp 230v / 1hp and the welder is a lincoln 225 arc welder. The compressor says the breaker size (trip rating) for circuit breaker is 35A, for fusible switch (melting style) the 30A dual element time delay fuses are suggested. The welder calls for a 50A.

Sent from my SM-T230NU using Tapatalk

Both those will run from 10 cable.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Hello! I'm new to the garage journal as of today. I'm wanting to put 2 220v outlets out in my garage. I need one for my air compressor and I have 10/2 wire and a 30 amp breaker for this and one for my welder and I have 6/2 wire and a 50 amp breaker for this. 2 separate runs ok or is there something that is probably easier? Thanks for any help.

2 runs are for you. There isn't easier way.
 
OP
R

Rebelman

Member
Joined
Jan 17, 2017
Messages
9
How bout this. Put a sub panal next to main panal run wires from there out to garage. Work! I don't have enough breaker space to put in 35A and a 50A breaker.

Sent from my SM-T230NU using Tapatalk
 
OP
R

Rebelman

Member
Joined
Jan 17, 2017
Messages
9
I have a few, there are a few that I could put on a tandem breakers to free up a few more.

Sent from my SM-T230NU using Tapatalk
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
I have a few, there are a few that I could put on a tandem breakers to free up a few more.

Sent from my SM-T230NU using Tapatalk

So why not run one large feeder to new subpanel in garage?

This will enable u to add circuits down the road should u expand
 