....I know you can't use a lower rated receptacle with a higher rated breaker and wiring. I thought there were 30A receptacles available in the same format as 5-15/20r because of my father's house. I know now his must be a 5-15r as there is no slot for a horizontal blade and it isn't a 5-30r....
A 5-30r has an L slot for the neutral and a 5-20r has a T-slot for the horizontal blade on a 5-20p.
What size breaker feeds this outlet at your fathers house?
I was just thinking about it though, why can't you install a 5-15r receptacle on a 30A breaker with 30A capable wire? You wouldn't be able to plug in anything that would draw more than the receptacle could handle, so what is the problem here? Not saying I am going to do it, just curious what the issue is. Putting a 5-30r receptacle on a 15 or 20A circuit is where there would be danger I would think.
As far as what the manual says, it says input current is 20A and to use a circuit with a 20A breaker, but that the cord is 15A and the plug is a 5-15p. It also says you can use up to a 50ft. extension cord as long as it is 12ga or larger. I was thinking of making a 6ft. extension cord with 12ga, not nearly the 50 they say is max. This would be long enough to reach everywhere I need.
Actually, u COULD plug something in that would pull more than 20a. There is utilization equipment which doesnt have internal thermal overloads. If the equipment draws more than 20a then the outlet can be fried.
Also, the other issue with doing that is if theres multiple outlets on the same 30a circuit, accumalatively more than 20a can be pulled through the circuit but less than 30a. This can melt the screw terminals on the outlets because obviously the breaker wont trip.
I have personally seen this happen on a service call. Guy bought an old condo built in the 70s and the heater wasnt working. So he plugged in a bunch of space heaters unbeknown to him, all plugged into the same circuit. After they all heated up he lost power to all of them. So he went to the panel and didnt find any tripped breakers. Tried flipping all the 15a and 20a breakers but that didnt fix it.
So then he called us. I pulled a few outlets and discovered the hot side of the outlet had melted at the terminals. Went to the panel and discovered that the breaker feeding the circuit was a 30a Zinsco. Whoops!
Is there any other loads on this circuit? Perhaps youre overloading the circuit and the breaker is simply doing its job. Often times people equate tripped breakers to something broken or wired wrong when in actuality all theyve done is plugged in too much equipment to the same circuit and pulled too much current.
You would not believe how many service calls Ive been on that ended up being this EXACT scenario! People were bummed that they had to pay a service fee just for an electrician to tell them they need to move equipment to different circuits.
Also, what brand of panel do u have? If its an older panel the breaker may be weak!
As far as the extension cord goes that should work fine.