I'm looking to add a ceiling fan in my garage to get some air moving. There is an unfinished bonus room/attic above the garage, so I'll just have to pull up some OSB flooring to mount the box, no biggie there.
I just want to check and be sure my plan for the wiring is sound.
Right now I have a 15A breaker feeding a 4 gang switch box in the hallway that leads from my garage into the house.
These switches feed as follows-
1-Hallway light (2x 60W bulbs)
1-Motion/Flood light (LED-23W)
1-Left bank of 4xT8 Fluorescent Fixtures-8 bulbs at 32W each-256W
1-Right bank of 4xT8 Fluorescent Fixtures-8 bulbs at 32W each-256W
Taking into consideration the efficiency loss/startup in a ballast, I'll just round up the total fluorescent fixture wattage to 600W, (haven't actually pulled a ballast down to check how much it really draws yet), I'm at a total of 743W, again, I'll just round up to 800W. So I'm well under the 80% usage 1440W capacity of a 15A circuit.
This is the fan I'm looking at:
http://www.homedepot.com/p/Hampton-...ar-Ceiling-Fan-52869/202670136#specifications
According to the instructions it uses .97A/107W on high, so with the addition of that we are still well below 1000W so I don't think any momentary inrush current at fan start would be an issue either.
So, my plan is to take both left and right banks of fluorescent lights and connect them together so one switch operates them both (anytime I'm out there I have both on anyway). Then since my fan will be situated between the two lights, I will take the wire that used to operate the left bank of lights and use that to switch/power the fan.
This way the only new wire I will have to run is to connect the two banks of lights together since I'll be reusing the old run that operated the left bank of lights to power the fan.
Does anyone see an issue with this?
I just want to check and be sure my plan for the wiring is sound.
Right now I have a 15A breaker feeding a 4 gang switch box in the hallway that leads from my garage into the house.
These switches feed as follows-
1-Hallway light (2x 60W bulbs)
1-Motion/Flood light (LED-23W)
1-Left bank of 4xT8 Fluorescent Fixtures-8 bulbs at 32W each-256W
1-Right bank of 4xT8 Fluorescent Fixtures-8 bulbs at 32W each-256W
Taking into consideration the efficiency loss/startup in a ballast, I'll just round up the total fluorescent fixture wattage to 600W, (haven't actually pulled a ballast down to check how much it really draws yet), I'm at a total of 743W, again, I'll just round up to 800W. So I'm well under the 80% usage 1440W capacity of a 15A circuit.
This is the fan I'm looking at:
http://www.homedepot.com/p/Hampton-...ar-Ceiling-Fan-52869/202670136#specifications
According to the instructions it uses .97A/107W on high, so with the addition of that we are still well below 1000W so I don't think any momentary inrush current at fan start would be an issue either.
So, my plan is to take both left and right banks of fluorescent lights and connect them together so one switch operates them both (anytime I'm out there I have both on anyway). Then since my fan will be situated between the two lights, I will take the wire that used to operate the left bank of lights and use that to switch/power the fan.
This way the only new wire I will have to run is to connect the two banks of lights together since I'll be reusing the old run that operated the left bank of lights to power the fan.
Does anyone see an issue with this?