Our 1992 home didn't have GFCIs in the bedrooms. I put them in the kids' bedrooms soon after we moved in. Finally decided to put one in our master bedroom. Should be easy. Simply find which box has the home run and put it in. New GFCI trips instantly. Klein outlet tester has peak capture and shows 30V.
Correct me if I'm wrong, but in my experience it means a neutral on this circuit is tied together with neutral(s) on the other 120V leg. The house is full of "networked" neutrals. I suppose it would be easier to move the bedroom breaker over one slot so all the bedrooms are on the same leg.
Also found a neutral wire for a closet with continuity to ground which would also trip the GFCI. I'll be having a fun week.