Greetings,

My house appears to have a "main disconnect" next to the electric meter. In this panel, there is a 100A breaker plus a 50A breaker for my A/C unit.
10AADC9B-F347-4A99-A404-63D88DA5FDBE.jpeg
DF412B16-AD5E-4271-BA3B-9B86F446D556.jpeg

The 100A breaker leads to a 100A subpanel that is located in an utility room that is adjacent to the garage. As you can see from these photos, this subpanel is very full.
7F01B751-5CB9-4100-BBC1-30BB0BBAB384.jpeg
153A23A0-A9DE-44F6-B2FD-AFA005649CA2.jpeg

I would like to add a second 100A subpanel (in the garage). Obviously the goal is to add capacity for future needs. It has been suggested that I relocate the 50A A/C breaker to this new panel. Based on these photos, does this appear feasible?
 
Last edited:
To avoid these ads, REGISTER NOW!

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,442
Location
Western North Carolina
Greetings,

My house appears to have a "main disconnect" next to the electric meter. In this panel, there is a 100A breaker plus a 50A breaker for my A/C unit.
29-4Done.jpg
photocell-1.JPG

The 100A breaker leads to a 100A subpanel that is located in an utility room that is adjacent to the garage. As you can see from these photos, this subpanel is very full.
IMG_1476.jpg
IMG_1468.jpg

I would like to add a second 100A subpanel (in the garage). Obviously the goal is to add capacity for future needs. It has been suggested that I relocate the 50A A/C breaker to this new panel. Based on these photos, does this appear feasible?
Interesting looking main panel you have there. 😉
Sorry could not resist and you might want to update your pictures.

Good luck with your project.🍻
 

infinkc

Well-known member
Joined
Jan 19, 2012
Messages
862
Too bad you didn’t put the sub in when they did the solar. Doesn’t look like you have much more choice than moving the AC. Not sure if you can back feed solar from a sub, or if move that
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
What's going on with the breakers that have taped handles?

I don't think you will get a breaker that allows the PV back feed with a 100a connection for a sub.

I'd be considering replacing the existing sub panel with a larger one and then connection the new sub to that
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
Only way I see is a service change to a 200A meter main, the original install was a cheap as possible job leaving absolutely no room for expansion. When I see a panel full of twin breakers, only see bad things. Circuit directory is not code compliant either.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
Do you need capacity or just extra spaces? What size is your service?
The main service looks to be 200A with space for 2- 2 pole breakers, since there is a 100A 2 pole (Q2100) and a 50-30 quad, it's full & so is the 100A subpanel, unless the main can accept a 200A breaker and add a 200A panel next to the main panel, & move everything into it, but do not have a clue if it would work.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,877
Location
NW Iowa
The main service looks to be 200A with space for 2- 2 pole breakers.
Very possible but it sounds like a big assumption. I've never been around a seimens meter/main like that though so maybe you have experience with them.
 

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,903
Location
Southern Oregon
You should check under the hood for labels that could tell you what's acceptable, or at least a panel catalog number.

This breaker might fit, but it only has 2 input stabs. There might be a removable mini-bus in your panel that converts the normal main breaker position into 4 slots. You need to take the front off and see what's really in there.

 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
Fixed it for you.
If that was done that way from the start, that is a sure sign the gene pool needed more chlorine, much as I dislike AFCI's cutting way back on twin breaker use since being required is one good thing.
 