Adding a "panel" - rerouting ground

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,682
Location
Austin, TX
Need a little advice on the existing GEC (Grounding Electrode Conductor) in a main panel. Basic configuration is this:

1780252011509.png
Current look at the main panel, I don't know where the ground is tied.. UFER or ground rod.
1780252063692.png


I'm going to reconfigure this and add a Sol-Ark inverter in front of the load panel (200A utility pass-thru), so the inverter becomes the main panel.
I'll unbond the load panel.

1780252325684.png

Question is:
Is there a way to "share" the existing GEC? Or do I need to drop in a new ground rod. Same structure. It's a garage with residential over it.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,995
Location
Modesto, CA
Is there a way to "share" the existing GEC? Or do I need to drop in a new ground rod. Same structure. It's a garage with residential over it.

why would you share it? the GEC needs to go to the new main service panel.

also all those EGCs on the neutral bars need to be moved to a new ground bar(s). make sure the neutral bars are no longer bonded and you will need to run an EGC between the new main and the old main meaning the feeder needs to be 4-wire instead of 3-wire. what type of wire do you have between the meter and current main service panel
 
To avoid these ads, REGISTER NOW!
OP
D

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,682
Location
Austin, TX
why would you share it? the GEC needs to go to the new main service panel.
I was thinking "because the sub-panel" needs a GEC too.. But then I remembered these are the "same structure", main gets the GEC, sub gets connected to the main 4-wire..

Last sub-panel I did was a separate structure, so that's what confused me.

I assume I can "spice" the existing GEC and get it over to the main (inverter)? Running a new wire to ground actual ground connection would be a pain...
also all those EGCs on the neutral bars need to be moved to a new ground bar(s). make sure the neutral bars are no longer bonded and you will need to run an EGC between the new main and the old main meaning the feeder needs to be 4-wire instead of 3-wire.
Got it.
what type of wire do you have between the meter and current main service panel
I don't know, 200A service.. This is up north, so quality of work is usually better, but I'll see if there is any indication of wire type..
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,890
Location
NJ
I assume I can "spice" the existing GEC and get it over to the main (inverter)? Running a new wire to ground actual ground connection would be a pain...

I don't know, 200A service.. This is up north, so quality of work is usually better, but I'll see if there is any indication of wire type..
The splice in GEC can be made by permanent means. See NEC 250.64C.

Your pic shows 4/0 conductors in the panel....
1780331027743.pngIt looks like (at least) the neutral is copper?1780331161947.png
 
OP
D

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,682
Location
Austin, TX
The splice in GEC can be made by permanent means. See NEC 250.64C.
Your pic shows 4/0 conductors in the panel....It looks like (at least) the neutral is copper?
Thanks. I can't tell if it's copper, it has anti-ox on it. Doesn't really matter, need to run new main wires anyway. 200A service.

1780332790917.png

Current "main" panel is essentially on the back side (interior side) of the meter.

1780332846572.png
 