Adding a subpanel to my garage extension

Moto-Dude

Member
Joined
Jul 29, 2021
Messages
15
Location
Cougar Trap, Texas
I've built out my attached garage an additional 14'. I am adding a 100a subpanel, running 1/0 AL lines from the main to the subpanel.

I have a 220v circuit for a 18,000 btu mini split. According to the manufacturer, it draws about 6.82 Amps. I am planning to run a 30a breaker and 8ga 3 wire (2 hots and a ground). The wire is overkill but I may add a welder later, so this would handle that. My question: the mini-split should not cause any problems, it doesn't draw that much, right? But I've seen comments that say if the minisplit develops a problem and shorts out, the 30a breaker won't trip and protect the mini-split wiring...? It was suggested that a fusible link be added to the line where the minisplit joins the disconnect.

I thought that if a device shorts out, it will draw a ton of amps and that would trigger the 30a breaker...

I've also been told the breaker is there to protect the circuit wiring, not the device.

Definitely open to suggestions, thanks!


Sprite 167.jpg
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
I've built out my attached garage an additional 14'. I am adding a 100a subpanel, running 1/0 AL lines from the main to the subpanel.

I have a 220v circuit for a 18,000 btu mini split. According to the manufacturer, it draws about 6.82 Amps. I am planning to run a 30a breaker and 8ga 3 wire (2 hots and a ground). The wire is overkill but I may add a welder later, so this would handle that.

Wire for AC circuits is sized based on the MCA- minimum circuit ampacity. the breaker is sized based on the MOCP. both figures are found on the nameplate of the unit. I wouldnt run oversized wire. youre just wasting money.

so post a pic of the nameplate or make and model so we can look at the manual

also this circuit should be dedicated. i wouldnt run a welder on this circuit.
My question: the mini-split should not cause any problems, it doesn't draw that much, right? But I've seen comments that say if the minisplit develops a problem and shorts out, the 30a breaker won't trip and protect the mini-split wiring...? It was suggested that a fusible link be added to the line where the minisplit joins the disconnect.

I thought that if a device shorts out, it will draw a ton of amps and that would trigger the 30a breaker...

I've also been told the breaker is there to protect the circuit wiring, not the device.

Definitely open to suggestions, thanks!
this is just a ton of speculation when you havent given us any info on the unit

some AC units do indeed require fuses to protect the unit because the breaker wont respond fast enough.

if the nameplate says max fuse then you need to use a fused disconnect
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,585
Location
BC
Leave the mini-split on its own (small) circuit. It's circuit breaker requirement is to protect the equipment.

Wire a separate welding circuit based on the welder's needs, after you get it. If you have to rough something in, install a conduit; or, if you surface mount the panel you can easily pipe out of it later.
 
OP
M

Moto-Dude

Member
Joined
Jul 29, 2021
Messages
15
Location
Cougar Trap, Texas
Ok, very good, thanks! I had not thought of it needing to be a dedicated circuit only for the AC.

The wire: I already have the 8ga wire left over from a previous project, somehow I am losing sleep over not using it :)

I haven't bought the mini-split yet, I am leaning towards this: DuctlessAire-21-SEER-18-000-BTU
It seems to be a decent unit, although the installation pdf is super-generic

I don't have access to the nameplate, so suppose I need to buy the unit and then I can determine what wire and breaker to use for this circuit?
23454.JPG

There are 750 Q&A for this unit but they vary wildly!
Capture3246.JPG
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,893
Location
NJ
And most likely your dedicated welder recept could be wired with 12-2nmb.

Since you would have a mini split, I doubt you would ever be plugging a heater into the welder recept.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,479
Location
Richmond, VA
You steal that from a manufacturing plant? ;)

If the individual conductors are labeled thhn/then (I know they are same spec, but don't know about labeling) you could strip the outer cover and run in conduit. I doubt it would be code to run it in walls as-is though

What colors are they?
 
OP
M

Moto-Dude

Member
Joined
Jul 29, 2021
Messages
15
Location
Cougar Trap, Texas
No, lol, I bought it from an electric supply place in Freeport, TX about 6 years ago. I had a camper and a 70' run and my friends scolded me because I was using 12-3 wire for 50A service.

All three conductors are black.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,479
Location
Richmond, VA
No, lol, I bought it from an electric supply place in Freeport, TX about 6 years ago. I had a camper and a 70' run and my friends scolded me because I was using 12-3 wire for 50A service.

All three conductors are black.
Interesting they sold you that.... Not a cable that would be used for that application.

You can't use a black conductor for ground, so you'd have to buy a new one for at least that.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,585
Location
BC
You can't use a black conductor for ground, so you'd have to buy a new one for at least that.

I dont know about NEC... but, stripping one conductor of the cable completely bare at both ends may be acceptable.
 
OP
M

Moto-Dude

Member
Joined
Jul 29, 2021
Messages
15
Location
Cougar Trap, Texas
Ok, thanks, that makes sense. I ran the 12-2 wire to the rough in, now: the big question! I need 50' of cable to connect the main circuit panel to the subpanel. I am going with

1/0-1/0-1/0 Aluminum SER Cable w/ 2AWG Ground​



However... there is a 15' section that will be outside the garage and buried in sched 40 electrical PVC conduit.

Applications:
SER is type SE, Style R cable, used as an above ground service entrance cable, a panel feeder and in branch circuits. The cable is rated at 600 volts and 90°C for use in wet and dry locations. SER cables are LEAD FREE and RoHS compliant.

The NEC prohibits SER cable from being installed underground at all; not direct buried and not in buried conduit.

Any suggestions? I don't want to run conduit in the walls and attic. Just outside the garage and when underground.
 
Last edited:
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,479
Location
Richmond, VA
You'll need to transition to another wire type, like xhhw, find another path, or just do conduit end to end.

Why are you running 1/0? Running #2 and a 90a breaker to feed it will be cheaper and easier to run. You can still use a 100a sub
 
OP
M

Moto-Dude

Member
Joined
Jul 29, 2021
Messages
15
Location
Cougar Trap, Texas
You'll need to transition to another wire type, like xhhw, find another path, or just do conduit end to end.

Why are you running 1/0? Running #2 and a 90a breaker to feed it will be cheaper and easier to run. You can still use a 100a sub

2ga wire and a 90a breaker, yeah, that could work, I guess.
The conduit is a problem. The path the subpanel needs a sharp 90 to stay in the wall cavity.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,967
Location
Central Iowa
You can't put an LB below the panel if you're going to cover the walls, burying it. You could come in the back of the panel with an LB outside or put a junction box below the panel to feed up, just make sure that the cover for the box winds up flush with the wall finish. If you've already drill the hole down low for the LB, the options just became limited. About the only other easy thing I can think of is an LB below the panel with an access panel over it.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
You can't put an LB below the panel if you're going to cover the walls, burying it. You could come in the back of the panel with an LB outside or put a junction box below the panel to feed up, just make sure that the cover for the box winds up flush with the wall finish. If you've already drill the hole down low for the LB, the options just became limited. About the only other easy thing I can think of is an LB below the panel with an access panel over it.
With a little bit of planning it would have been simple, just stub up a conduit in the stud bay prior to pouring concrete, all it would of taken, just a little bit of planning..........
 
OP
M

Moto-Dude

Member
Joined
Jul 29, 2021
Messages
15
Location
Cougar Trap, Texas
Can you keep a junction box or an LB accessible to make that corner?



Could do a lb on the interior too.

Why are you going outside for an attached garage?

I think I can. I will plumb it in above the sill plate and the LB should just protrude from the drywall for the all-important "access".


What if you put the LB directly into the back of the panel and paint conduit to match siding?

You can also reduce to 1.5" with the #2's. (Even 1.25")
I thought about that, yeah, just really don't want that massive ugly LB at eye level :sick:

You can't put an LB below the panel if you're going to cover the walls, burying it. You could come in the back of the panel with an LB outside or put a junction box below the panel to feed up, just make sure that the cover for the box winds up flush with the wall finish. If you've already drill the hole down low for the LB, the options just became limited. About the only other easy thing I can think of is an LB below the panel with an access panel over it.
Yes, sounds good. I'm still a little miffed the options are so limited. I'll get over it.

With a little bit of planning it would have been simple, just stub up a conduit in the stud bay prior to pouring concrete, all it would of taken, just a little bit of planning..........
Where were you 14 months ago!? Yeah, the concrete guy even asked about it but I was so far from the electrical phase I said I wasn't sure what I needed and let it go at that. Man, I wish I had known. You have to remember, this is my first electrical project, I had a lot to learn. ;)

Completed wiring in the sub-panel. Man, I can't believe electricians get paid to do this, it's a lot of fun!
IMG_20231120_155240366.jpg

Feel free to point out any issues or mistakes, I'm still learning.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,479
Location
Richmond, VA
Where were you 14 months ago!? Yeah, the concrete guy even asked about it but I was so far from the electrical phase I said I wasn't sure what I needed and let it go at that. Man, I wish I had known. You have to remember, this is my first electrical project, I had a lot to learn. ;)
Next time, I'd just stub up a couple pieces of conduit in the most likely spots with a sweep 90 at the bottom. Worst case, you cut it flush if you don't need it.

But that doesn't help you now.

I would have flipped the panel over. No need to have the feeder wrap all the way through to the top
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,259
Location
Coastal NJ
I'd cut back all that jacket on the NM-B at the top of the panel shown in post #28.

Lots of folks use this labeling technique.


1700578442679.png
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,479
Location
Richmond, VA
Yeah, that kinda thing doesn't bother me. As long as it works!
Makes it harder to work on the panel and it wastes wire.

Also causes a high current feeder to run through an area that you are workinging whenever you are in the panel.

I'd flip it and get block offs for the knock outs you used
 