Adding circuit for a mini split: Two options from electrician in an attached garage

XS29L9B

Well-known member
Joined
Nov 22, 2012
Messages
318
When first discussed, I was just going to have a 220v dedicated circuit pulled for a mini split w/. a disconnect at a box mounted outside. That's pretty much still the plan, but then the electrician asked about bringing a 100A sub panel to the garage and then, when ready for the mini split, just pull from there. The plan was also to have a 220v pull from the main panel for a compressor, etc., just to have a 220v outlet in the garage.


So those are my two choices.

On one hand, I think I only need the dedicated run to the disconnect box for the mini split.

On the other hand, the 100A sub panel allows for any further/future expansion.

What are the pros/cons? I am sure the sub panel will be at least 2x the cost. At least.............

Thanks for any input.
 
To avoid these ads, REGISTER NOW!

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
10,977
Location
Rhode Island
I would say it would probably make sense for a 30 or 40A sub in the garage if you plan a compressor in the future. Square D makes a cute lil 6 slot QO panel. A 100A sub is way overkill.
 

Jakemedic

Well-known member
Joined
Jul 26, 2013
Messages
722
Location
Cornfields of SE Iowa
Get a quote for both, then you can make an educated decision. If you are just building out your garage, it may be nice to get a 100 amp sub panel so you don’t have to use up all your opening in your main box. I did 100 amp into my shop, which was a new build. Since finishing it, I had to pull a 30 amp circuit for my surface planer. Nice not going back to the basement to pull a circuit. It’s your money, but look towards the future too.
 

Dig Doug

Well-known member
Joined
Apr 16, 2018
Messages
1,111
Your biggest expense will be the wire feeding the sub panel !

you can go
100 amp
50 amp 30/40 amp

100 amp panel is $110 from Depot !

so what ever look at wire costs how many feet of cable do you need?

I would go a minimum 50 amp! You might add more stuff down the road, welder, grinders, table saw ceiling fans, TV ….

my electrical problem is is breaker space!! I’m out of spaces….
you can use the panel below and feed it with 40/ 50 amps and you’ll have plenty of breaker space.

I wouldn’t say the labor is the same for pulling a 50 amp feeder to a sub panel than a couple of 220 circuits …. But I’d rather pay once and be done than be limited in the future…..

D44746C6-8CEE-4861-AE75-D2F2FAC11F63.jpeg
 
Last edited:

tfi racing

Well-known member
Joined
Apr 19, 2008
Messages
2,907
Location
Cedar,BC
Pay now, or even pay a lot more later. You will need to provide some more information to get any realistic answers that can actually help with your decision making.
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
The main panel in my house is in the finished basement, flush mounted with drywall all around it. Adding circuits to it is a major pain. That's why I installed a subpanel in my attached garage. I had to run only one circuit from the main panel (which indeed was a pain), but now I never have to mess with the main panel again. I installed several new circuits from the subpanel, and if I need to add more circuits, the subpanel is right there, easy to access, and easy to make changes/add stuff.
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,778
Location
Austin, TX
The plan was also to have a 220v pull from the main panel for a compressor, etc., just to have a 220v outlet in the garage.


So those are my two choices.

On one hand, I think I only need the dedicated run to the disconnect box for the mini split.

On the other hand, the 100A sub panel allows for any further/future expansion.

What are the pros/cons? I am sure the sub panel will be at least 2x the cost. At least.............

Thanks for any input.
You need more than one circuit to that garage, I'm going with sub-panel too. 60A copper or 90A aluminum would be my go-tos for feeds.
I actually use an outside rated sub panel for our main HVAC disconnects. It provides the required 120V "service outlet". That particular panel costs around $240 right now. Sits between the two units on the wall.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,903
I would say it would probably make sense for a 30 or 40A sub in the garage if you plan a compressor in the future. Square D makes a cute lil 6 slot QO panel. A 100A sub is way overkill.
Anyone who installs a 30A subpanel in a garage these days is seriously out of touch with what the future demands will be, or is planning on getting the job of replacing it when a car charger is installed. The cost difference between a 30A six-space panel and a 20 space 100A panel is very little more than the difference in wire cost. 100A 20ish space panels are cheap, because they sell lots of them. six space panels are not usual, and are surprisingly expensive.
 

starquestMM

Well-known member
Joined
Jan 7, 2013
Messages
1,076
Location
JC, Missouri
go big.

There is a tax credit for this right now i think. IRS form 8911 and its instructions don't mention actually buying an electric vehicle... :)
 
To avoid these ads, REGISTER NOW!
OP
X

XS29L9B

Well-known member
Joined
Nov 22, 2012
Messages
318
go big.

There is a tax credit for this right now i think. IRS form 8911 and its instructions don't mention actually buying an electric vehicle... :)
Oh boy, this is awesome!!!!!!!

 
OP
X

XS29L9B

Well-known member
Joined
Nov 22, 2012
Messages
318
Pay now, or even pay a lot more later. You will need to provide some more information to get any realistic answers that can actually help with your decision making.


What other info might be useful?

Garage is 56x36

I am putting 24 can lamps in the vaulted ceiling to illuminate, then a bunch of outlets. Maybe 18 of them.

In the future, I want to add a Mr. Cool Mini Split 36,000 unit.

Also, adding 220 outlet for EV ;)
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,763
What other info might be useful?

Garage is 56x36

I am putting 24 can lamps in the vaulted ceiling to illuminate, then a bunch of outlets. Maybe 18 of them.

In the future, I want to add a Mr. Cool Mini Split 36,000 unit.

Also, adding 220 outlet for EV ;)
Recessed cans are a poor way of illuminating a space.
 
OP
X

XS29L9B

Well-known member
Joined
Nov 22, 2012
Messages
318
The can lamps are a clean look compared to shop lighting I've seen.
But if ya got some other ideas, post up pics. Sway my mind. Thanks
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,903
The can lamps are a clean look compared to shop lighting I've seen.
But if ya got some other ideas, post up pics. Sway my mind. Thanks
the problem with cans is they're a spot light. They cast light in a cone, with an angle depending on what the emitter in the can is, and illuminate a spot on ground. if the spots from the cans don't overlap, you have areas that are not directly illiuminated, and will be in shadows. Increasing the brightness of the emitter won't fix that, it creates glare. Note that the overlap needs to be at the plane you care about. For general illumination, that's the floor, more or less. For working on a car or a workbench, that's rather higher up, which means smaller spots. If you don't have high ceilings, you end up needing huge numbers of cans, which is expensive and ugly, and you'll want to dim them, which adds to cost. They work great for accent lighting or lighting a bench or something like that.
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
If you walk into a new Target it is well lit but you don't look into the lights unless you look more or less straight up. Baffles are used to keep light out of your eyes. It takes a lot of can lights to illuminate a space, but done right with task lighting it's really nice.

I have 2 lighting systems in my small garage. One for show and one for go.
 
OP
X

XS29L9B

Well-known member
Joined
Nov 22, 2012
Messages
318
the problem with cans is they're a spot light. They cast light in a cone, with an angle depending on what the emitter in the can is, and illuminate a spot on ground. if the spots from the cans don't overlap, you have areas that are not directly illiuminated, and will be in shadows. Increasing the brightness of the emitter won't fix that, it creates glare. Note that the overlap needs to be at the plane you care about. For general illumination, that's the floor, more or less. For working on a car or a workbench, that's rather higher up, which means smaller spots. If you don't have high ceilings, you end up needing huge numbers of cans, which is expensive and ugly, and you'll want to dim them, which adds to cost. They work great for accent lighting or lighting a bench or something like that.


In the 56 x 36 space, I will have 24 cans.

The ceiling, in the lowest point, is 11' and vaulted, to a peak of 18'

I planned to "drop" the bulbs as low in the fixtures as possible, that way the bulbs are nearly flush, or just proud to the surface to allow more light to cast outward a bit.

Being flush on an angled ceiling, the lights will spread a bit, too. I think
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,269
Location
Coastal NJ
I’m using Lithonia CPANL 2x4 LED panels. 6000lm 0-10v dimming. I wanted good light and reasonable aesthetics.