Adding Garage Heater 30AMP 240V

CJW

New member
Joined
Oct 15, 2013
Messages
3
My panel is full, but I have a 50 AMP 240V Breaker feeding a metal outlet box that I use for my welder. My welder only needs 20 AMP 240V, so could I split the circuit by simply using wire nuts and connecting a 10/3 wire for 30AMP 240V that would feed the heater to the 6/3 wire coming from the 50 AMP breaker and dog tailing a 12/3 wire for 20AMP 240V to feed the welder??
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
No you can't. You can replace the 50A outlet with a small sub panel and have a 30A breaker and a 20A breaker for the two outlets.
 
To avoid these ads, REGISTER NOW!

G_P

Well-known member
Joined
Jul 11, 2010
Messages
7,135
Location
Central CT
The breaker protects the wiring. Putting 10ga wire on a 50a breaker could easily cause a fire as 10ga not capable of carrying 50a.

Is there any way you can use some tandem breakers on some of the existing 120v circuits to free up some space in the panel?
 