Awhile back my pole barn electric was done to a minimum by the electrician, just enough to pass so the power could be turned on..Now I wish to get some outlets for heat etc installed before it gets to cold. Question is should I go the route as the electrician(in pics) or just run stapled romex to my receptacles..I plan on finished electrical, 2x6 studs and insulating the walls next summer?
 

Attachments

  • 20241130_172135.jpg
    20241130_172135.jpg
    624.4 KB · Views: 156
  • 20241130_171925.jpg
    20241130_171925.jpg
    443.7 KB · Views: 138
  • 20241130_171823.jpg
    20241130_171823.jpg
    441.4 KB · Views: 137
  • 20241130_171555.jpg
    20241130_171555.jpg
    550.8 KB · Views: 131
  • 20241130_171530.jpg
    20241130_171530.jpg
    527.3 KB · Views: 150
To avoid these ads, REGISTER NOW!

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,407
Location
Richmond, VA
Romex thru conduit? Not in my garage!
Its completely fine and is a good way to add protection where needed. People thinking romex can't be in conduit is an internet myth

@hiccup you need to protect wiring anywhere subject to damage. If the walls were staying open, I'd mimic what the electrician did, but if you are going to finish the interior, just staple it to the sides of the posts
 
Last edited:

luvtheheat

Well-known member
Joined
Jan 28, 2017
Messages
489
Location
Tucson AZ
Its completely fine and is a good way to add protection where needed. People thinking romex can't be in conduit is an internet myth

@hiccup you need to protect wiring anywhere subject to damage. If the walls were staying open, I'm mimic what the electrician did, but if you are going to finish the interior, just staple it to the sides of the posts
I didn't say it wasn't allowed; I just wouldn't do it personally.
 

luvtheheat

Well-known member
Joined
Jan 28, 2017
Messages
489
Location
Tucson AZ
Usually the argument is that it's against code.

What about it don't you like?
Heat dissipation during high loads. Impossible to pull another circuit through it if needs. I've also seen it used on roof tops in AZ (which would be a violation (outdoors), if I understand correctly) where ambient temps can be 120+. Easy to see it overheating in that environment under any heavy load.
 
Last edited:

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,381
Location
VT
@hiccup you need to protect wiring anywhere subject to damage. If the walls were staying open, I'm mimic what the electrician did, but if you are going to finish the interior, just staple it to the sides of the posts

Nailed it IMHO

Heat dissipation during high loads. Impossible to pull another circuit through it if needs. I've also seen it used on roof tops in AZ (which would be a violation (outdoors), if I understand correctly) where ambient temps can be 120+. Easy to see it overheating in that environment under any heavy load.

This is (mostly) personal opinion about situations that don't even apply to the op, why bother bringing it up?
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,583
Location
BC
Consider that what you add technically needs re-inspection before concealing it.

I have lots of temporary NMD wiring in the shop. I kept it outside the walls because it will be switched to surface conduit when I'm happy with it. That way it can also be inspected anytime, (unlikely as that may be).
 

Fav Onefour

Well-known member
Joined
Jul 14, 2022
Messages
695
Location
MN cold and hot
I wouldn't spend much energy on wiring if the framing isn't in place.

Just sling some rx to a few 4" sq boxes and add temporary recepts. All of this material can be re-used as you progress.
Dang good advice.
I'd go even further.
Hang a couple of retractable extension cord units from the ceiling. Play around and use the space until you are ready to finish the interior. It will help with decisions on where to run power and outlets.
I spend quite a bit of time planning wiring for work space. I've done a few shops over the years. Even with planning, I still find spots to add or reconfigure layout and wiring.
 
OP
H

hiccup

Active member
Joined
Oct 23, 2023
Messages
42
Location
W.Ky
thanks just wanting some reassurance that will be ok until my walls are finished out next year..I'm probably gonna redo the electricians work too..I like the metal conduit look for a work space but by time I run that everywhere and pull wire it would feel like a big expense for a 36x48 with loft..Also one place I screwed up was not blocking my breaker panel out to account for a finished wall so that messed up my "industrial" look 😖
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,583
Location
BC
thanks just wanting some reassurance that will be ok until my walls are finished out next year..

You're the one that will be working around it. Your care, attention, and habits go way further than any reassurance we can give you.

Retractable/reel cords have never been my thing, but always been flush with spare lengths of cable and junction boxes.

Maybe see if you can still block the panel out how you intended.
 
To avoid these ads, REGISTER NOW!
OP
H

hiccup

Active member
Joined
Oct 23, 2023
Messages
42
Location
W.Ky
You're the one that will be working around it. Your care, attention, and habits go way further than any reassurance we can give you.

Retractable/reel cords have never been my thing, but always been flush with spare lengths of cable and junction boxes.

Maybe see if you can still block the panel out how you intended.
If had planned it right or at least got a suggestion from the electrician I'd had the panel set out flush with the post at least..I dont know what trouble it'd be to do that now
 

Attachments

  • 20241201_162425.jpg
    20241201_162425.jpg
    655 KB · Views: 96
  • 17330922276976340471315737986205.jpg
    17330922276976340471315737986205.jpg
    584.3 KB · Views: 96

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,583
Location
BC
It's a bunch easier/safer because your meter has a disconnect. See if there is enough wire slack to renew the thru-wall conduit with a longer piece. If not, you need longer wire from the disconnect to the panel.
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,281
Location
Illinois near St. Louis, Missouri
When I read the title I thought the the main issue was about adding more circuits without another permit/inspection. An electrician who built a detached garage near me did the minimum electrical for permit and said he would be adding more circuits after inspection. I think some areas charge by the circuit so maybe he was worried about that but I just built under the same city code and there wasn't anything about how much electric was planned. Maybe he figured it would be lower valuation for taxes - our taxes here are high. I did all of it up front but not to say if I needed to add a circuit I would probably just do it.
 
OP
H

hiccup

Active member
Joined
Oct 23, 2023
Messages
42
Location
W.Ky
Where is the conduit out the bottom of the panel going? Is the feed from the meter into the back?
The outside panel conduit going underground to utility pole..the inside conduit to a sub on opposite wall.
 

Attachments

  • 20241201_162458.jpg
    20241201_162458.jpg
    554.1 KB · Views: 91
OP
H

hiccup

Active member
Joined
Oct 23, 2023
Messages
42
Location
W.Ky
When I read the title I thought the the main issue was about adding more circuits without another permit/inspection. An electrician who built a detached garage near me did the minimum electrical for permit and said he would be adding more circuits after inspection. I think some areas charge by the circuit so maybe he was worried about that but I just built under the same city code and there wasn't anything about how much electric was planned. Maybe he figured it would be lower valuation for taxes - our taxes here are high. I did all of it up front but not to say if I needed to add a circuit I would probably just do it.
Yes you are correct I was just wanting the ok to add a few receptacles fed romex only temporarily..the discussion of the panels was added because of talk of my final plan to stay with "visible" conduit/ metal boxes out of a fully exposed panel..or everything just put behind finished walls like in a house..As far as inspections or codes it will never see another inspect cause its on a farm in a Kentucky county.
 
OP
H

hiccup

Active member
Joined
Oct 23, 2023
Messages
42
Location
W.Ky
That's Going to make it tough to move the panel out. Is there already wire in it?
Yes it's in use and probably no loops left in there for future work..It will probably remain where it is and will have the panel offset within the wall.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,967
Location
Central Iowa
If had planned it right or at least got a suggestion from the electrician I'd had the panel set out flush with the post at least..I dont know what trouble it'd be to do that now
It won't be too bad. Obviously the ****** between the meter and panel is going to be too short, the wires probably will be as well but they are short enough that replacing them won't cost much. Hopefully, the wires to the subpanel haven't been pulled, if they have, pull 'em out. You can cut the PVC off a few inches above the floor, heat up a new piece and bend an offset in it. You could also bend an offset in the existing, but it's gonna be too short so a piece will have to be cut off the top and replaced by a piece a little longer.

As far as slinging in some temp outlets, use 4X4 metal boxes screwed to scrap wood. You can screw the wood to the framing and take it off without taking the box apart to move it out of the way while finishing the inside.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,871
Location
NJ
Get a new length of conduit and bend the necessary offset in it for the panel to be flush with the framed wall surface.
Use the offset piece to determine where to cut the stub up at. Also check the offset amount against the feeder slack in the panel.......worst case you may need to lower panel 4".

If lowering the panel is necessary, KO seal the existing feeder hole and punch a new one.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,967
Location
Central Iowa
Or get a 12X12X8 junction box. Set it up so there the sub panel feeder is going into it as well as 4" sticking out of the finished wall. Come out the top of it and into the bottom of the panel. It will probably still need an offset to make everything happen but the offset will stay inside the wall and won't be an eyesore.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,992
Location
Modesto, CA
Heat dissipation during high loads. Impossible to pull another circuit through it if needs. I've also seen it used on roof tops in AZ (which would be a violation (outdoors), if I understand correctly) where ambient temps can be 120+. Easy to see it overheating in that environment under any heavy load.
Is this a joke? Heat dissipation is not an issue in conduit. Smh

So many people continue to spread this myth throughout the internet. Wish it would die

Also if the conduit is large enough you most certainly can pull another thru.
 
Last edited:
OP
H

hiccup

Active member
Joined
Oct 23, 2023
Messages
42
Location
W.Ky
When I read the title I thought the the main issue was about adding more circuits without another permit/inspection. An electrician who built a detached garage near me did the minimum electrical for permit and said he would be adding more circuits after inspection. I think some areas charge by the circuit so maybe he was worried about that but I just built under the same city code and there wasn't anything about how much electric was planned. Maybe he figured it would be lower valuation for taxes - our taxes here are high. I did all of it up front but not to say if I needed to add a circuit I would probably just do it.
👍
 