ecnsupplies
New member
- Joined
- Feb 18, 2025
- Messages
- 3
I have a brand new 28btu pioneer mini split cassette system. I have vacuumed the system and it holds a vacuum for 24hours.
My question is my line set is longer then the 16 foot so I need to add .68 lb more r410. I connected the hoses to the valve but no freon will go in. I tested and if I remove the yellow hose from mini split freon does go out the hose.
Do I need to release the Freon in the new mini split system first before I can add more Freon to it?
Will the hex nut using the wrinch valves not being open stoping the Freon from going in?
The book says you have to open this to release the stored freon into the line set.
It does not restrict a vacuum from being pulled.
I just want to make sure before I release the new freon in the unit to the line set. Before Tring it that way. Hope this makes sense.
My question is my line set is longer then the 16 foot so I need to add .68 lb more r410. I connected the hoses to the valve but no freon will go in. I tested and if I remove the yellow hose from mini split freon does go out the hose.
Do I need to release the Freon in the new mini split system first before I can add more Freon to it?
Will the hex nut using the wrinch valves not being open stoping the Freon from going in?
The book says you have to open this to release the stored freon into the line set.
It does not restrict a vacuum from being pulled.
I just want to make sure before I release the new freon in the unit to the line set. Before Tring it that way. Hope this makes sense.