My electrical meter and service disconnect are about 300’ north of my house, mounted on a pole. From there it comes underground into my house. On the main disconnect I have three lugs, two of which are being used. These lugs are very big, sized for 2/0 wire. The third lug I plan to use when I build my barn.
I would like to have an electrical outlet in this area. A single 20 amp circuit would be fine. Running it from the house is an option but I really don’t want to for logistical reasons. Electrically I understand well enough how the connections need to work but there are few things that I don’t understand.
1) assuming I install a 20 amp breaker how do I protect the wire between my main disconnect and the breaker? The largest wire size I can fit in the panel is 2awg, which is too small for the 200a disconnect. Larger won’t fit in the terminal of my breaker. Obviously cost is no issue here because I only need a foot or two.
2) what is the best way to add a fourth lug to my disconnect?
This is what I was planning to use:
https://www.homedepot.com/p/Eaton-B...Lug-Loadcenter-with-Cover-BR24L70RP/100128514
Plan B is to install a larger load center and then just feed the barn from there but I don’t really want to do that just to get a single 20a circuit.
I would like to have an electrical outlet in this area. A single 20 amp circuit would be fine. Running it from the house is an option but I really don’t want to for logistical reasons. Electrically I understand well enough how the connections need to work but there are few things that I don’t understand.
1) assuming I install a 20 amp breaker how do I protect the wire between my main disconnect and the breaker? The largest wire size I can fit in the panel is 2awg, which is too small for the 200a disconnect. Larger won’t fit in the terminal of my breaker. Obviously cost is no issue here because I only need a foot or two.
2) what is the best way to add a fourth lug to my disconnect?
This is what I was planning to use:
https://www.homedepot.com/p/Eaton-B...Lug-Loadcenter-with-Cover-BR24L70RP/100128514
Plan B is to install a larger load center and then just feed the barn from there but I don’t really want to do that just to get a single 20a circuit.