Hi folks,
First, thanks to the members on this site. Your knowledge and advice has been an invaluable resource.
I have a question regarding the electrical system of a property I recently purchased. It was primarily used for bluegrass gatherings, people would bring their campers and travel trailers to stay on the land, so the infrastructure may be unconventional for a typical residence.
There is an aerial service entrance at the road which brings 240v single phase power through the meter into a 200 amp breaker. This panel (panel #1) is the main service disconnect, with neutral and grounding bus bars connected via a main bonding jumper and a grounding electrode conductor connected to the bus bar and to a grounding electrode. There is a green grounding screw with an equipment bonding jumper for the enclosure, but this has been disconnected from the bus bar (would this be a violation of 250.24(C)?). Panel #1 has feed-through lugs with two wires under each lug. One set of wires are 6/2 NM-B with ground run in a 1” PVC conduit about 100’ underground to a small concrete pad where the conduit comes out of the ground and terminates. The cable has no connections, just wire nuts on the conductors. These wires have no OCPD and are not being used so I have them disconnected at panel #1.
The other set of wires under the feed through lugs in panel #1 are 4/0-4/0-2/0 AL URD which run in 2” PVC conduit about 350’ underground to a pole mounted enclosure (panel #2) where they terminate at a 150 amp breaker. Panel #2 directly feeds three branch circuits, a 15 amp circuit that powers a pole mounted light, and two 20 amp circuits that each power a single duplex receptacle mounted underneath the panel. Panel #2 also has feed-through lugs with two wires under each lug, both sets are 2-2-2 AL SEU. One set runs underground in 1” PVC conduit approximately 30’ to an indoor enclosure (panel #3) inside a cabin, the other set runs underground in 1 1/2” PVC conduit about 120’ to a small enclosure (panel #4) that has four 30 amp branch circuits and four TT-30R receptacles, and also feeds a duplex receptacle about 50’ away. Panel #4 has no main breaker.
Panel #2 does have a grounding electrode system, and the grounding electrode conductor and all the equipment grounds are bonded together with the neutral bus bars. It does not have bonding screws from the bus bars to the panel enclosure installed.
Panel #3, inside the cabin, has a 100 amp main breaker and seven 20 amp 120V branch circuits for receptacles and lighting, plus two 240V branch circuits, a 30 amp circuit for the water heater and 50 amp circuit for the stove. There is also a 40 amp double pole breaker of which one leg was used to feed 120V to a stage located about 100’ from the cabin, but I have disconnected and removed the stage’s sub panel and the wires running to it. Panel #3, like panel #2, has grounds and neutrals bonded together. Panel #3 does have screws bonding the panel enclosure to the neutral/ground bus bars. It has no grounding electrode system, nor does it have an equipment grounding conductor that feeds it, only the grounded conductor and two ungrounded conductors.
Apologies for the lengthy preamble, I wanted to give an explanation of the situation in case there are implications to my questions, which do pertain to a garage.
I had a 26’x40’ metal building built about 75’ from panel #2, which houses the 150 amp breaker. The plan is to use panel #2 to feed a 100 amp sub panel (panel #5) that will power the garage. Panel #5 has isolated grounds and its own grounding electrode system. I trenched from the pole where panel #2 is mounted to the garage and laid a 1 1/2” PVC conduit through which I ran 1-1-2-6 AL XHHW-2 wires. Those wires terminate at the garage in the 100 amp panel #5 enclosure and have a 100 amp breaker installed at panel #2, but I am waiting to connect until I have some clarity on the panel configurations, particularly panel #2 which feeds the garage.
I have read Article 250 and looking specifically at Section 250.32(B)(1), it appears that there is an exception for panels supplied by 3 wire feeders that allows for re-grounding the feeder’s grounded conductor if certain conditions are met. In this case it IS true that:
1) An equipment grounding conductor is not run with the supply to the structure.
2) There are no continuous metallic paths bonded to the grounding system in each structure (bonded water, or gas piping, other conduit, etc.).
3) Ground-fault protection of equipment has not been installed on the supply side of the feeders.
Does this indicate that panel #2 is acceptable the way it is and there is no need to separate ground and neutral busses and run a grounding conductor from panel #1 along with the supply conductors? I do plan on reworking panel #3 inside the cabin since the allowable ampacity for 2AWG AL conductors is less than the 100 amp OCPD they serve. I assume it is better to have a separate grounding conductor and not use the grounded conductor as the ground-fault return path. That said, I would appreciate any input from those wiser and more experienced than myself. What would you do if you were in my position?
My property is unrestricted so I don’t have to worry about inspections, my main concern is safety for myself and those who come after me.
First, thanks to the members on this site. Your knowledge and advice has been an invaluable resource.
I have a question regarding the electrical system of a property I recently purchased. It was primarily used for bluegrass gatherings, people would bring their campers and travel trailers to stay on the land, so the infrastructure may be unconventional for a typical residence.
There is an aerial service entrance at the road which brings 240v single phase power through the meter into a 200 amp breaker. This panel (panel #1) is the main service disconnect, with neutral and grounding bus bars connected via a main bonding jumper and a grounding electrode conductor connected to the bus bar and to a grounding electrode. There is a green grounding screw with an equipment bonding jumper for the enclosure, but this has been disconnected from the bus bar (would this be a violation of 250.24(C)?). Panel #1 has feed-through lugs with two wires under each lug. One set of wires are 6/2 NM-B with ground run in a 1” PVC conduit about 100’ underground to a small concrete pad where the conduit comes out of the ground and terminates. The cable has no connections, just wire nuts on the conductors. These wires have no OCPD and are not being used so I have them disconnected at panel #1.
The other set of wires under the feed through lugs in panel #1 are 4/0-4/0-2/0 AL URD which run in 2” PVC conduit about 350’ underground to a pole mounted enclosure (panel #2) where they terminate at a 150 amp breaker. Panel #2 directly feeds three branch circuits, a 15 amp circuit that powers a pole mounted light, and two 20 amp circuits that each power a single duplex receptacle mounted underneath the panel. Panel #2 also has feed-through lugs with two wires under each lug, both sets are 2-2-2 AL SEU. One set runs underground in 1” PVC conduit approximately 30’ to an indoor enclosure (panel #3) inside a cabin, the other set runs underground in 1 1/2” PVC conduit about 120’ to a small enclosure (panel #4) that has four 30 amp branch circuits and four TT-30R receptacles, and also feeds a duplex receptacle about 50’ away. Panel #4 has no main breaker.
Panel #2 does have a grounding electrode system, and the grounding electrode conductor and all the equipment grounds are bonded together with the neutral bus bars. It does not have bonding screws from the bus bars to the panel enclosure installed.
Panel #3, inside the cabin, has a 100 amp main breaker and seven 20 amp 120V branch circuits for receptacles and lighting, plus two 240V branch circuits, a 30 amp circuit for the water heater and 50 amp circuit for the stove. There is also a 40 amp double pole breaker of which one leg was used to feed 120V to a stage located about 100’ from the cabin, but I have disconnected and removed the stage’s sub panel and the wires running to it. Panel #3, like panel #2, has grounds and neutrals bonded together. Panel #3 does have screws bonding the panel enclosure to the neutral/ground bus bars. It has no grounding electrode system, nor does it have an equipment grounding conductor that feeds it, only the grounded conductor and two ungrounded conductors.
Apologies for the lengthy preamble, I wanted to give an explanation of the situation in case there are implications to my questions, which do pertain to a garage.
I had a 26’x40’ metal building built about 75’ from panel #2, which houses the 150 amp breaker. The plan is to use panel #2 to feed a 100 amp sub panel (panel #5) that will power the garage. Panel #5 has isolated grounds and its own grounding electrode system. I trenched from the pole where panel #2 is mounted to the garage and laid a 1 1/2” PVC conduit through which I ran 1-1-2-6 AL XHHW-2 wires. Those wires terminate at the garage in the 100 amp panel #5 enclosure and have a 100 amp breaker installed at panel #2, but I am waiting to connect until I have some clarity on the panel configurations, particularly panel #2 which feeds the garage.
I have read Article 250 and looking specifically at Section 250.32(B)(1), it appears that there is an exception for panels supplied by 3 wire feeders that allows for re-grounding the feeder’s grounded conductor if certain conditions are met. In this case it IS true that:
1) An equipment grounding conductor is not run with the supply to the structure.
2) There are no continuous metallic paths bonded to the grounding system in each structure (bonded water, or gas piping, other conduit, etc.).
3) Ground-fault protection of equipment has not been installed on the supply side of the feeders.
Does this indicate that panel #2 is acceptable the way it is and there is no need to separate ground and neutral busses and run a grounding conductor from panel #1 along with the supply conductors? I do plan on reworking panel #3 inside the cabin since the allowable ampacity for 2AWG AL conductors is less than the 100 amp OCPD they serve. I assume it is better to have a separate grounding conductor and not use the grounded conductor as the ground-fault return path. That said, I would appreciate any input from those wiser and more experienced than myself. What would you do if you were in my position?
My property is unrestricted so I don’t have to worry about inspections, my main concern is safety for myself and those who come after me.