Aerial service

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,996
Location
Thousand Islands NYS
Just thinking about electrical service way off road, and realized how little I know about aerial. I believe Poco will set a transformer on a pad at corner of property. Trenching through bedrock doesnt seem easy for 1200 feet so thinking aerial. I think 200 amp requires 4/0 aluminum triplex? Along property line, no driveways or any passages, how high and how close do I need to set poles?

Still considering pure solar and battery. Project is probably 2 years out, so solar and batteries can only improve.
 
To avoid these ads, REGISTER NOW!

JohnKal

Well-known member
Joined
Mar 24, 2014
Messages
1,800
Location
New York State
If your going aerial I believe the poco will most likely set a transformer on a pole rather than a pad. As far as height and spacing, they can probably give you the specifics. National Grid?
 
OP
B

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,996
Location
Thousand Islands NYS
Thank you.

Yes National Grid.

I have not seen another pole mount transformer in the area, and there are some aerial feeds. Just to complicate it - I'm at a town line and service ends 400-500 feet down the road one way, more the opposite way.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
If the meter is at the house/cabin/site they own the wire down to the meter, usually, and will specify the wire needed.

Curious, how did this campsite escalate to 200a service? ;)
 
OP
B

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,996
Location
Thousand Islands NYS
I started at 200. May look at 100 or 150. I keep bouncing around with different ideas.

I'm told by a GC a pad and transformer with meter at road - everything else is mine.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
I started at 200. May look at 100 or 150. I keep bouncing around with different ideas.

I'm told by a GC a pad and transformer with meter at road - everything else is mine.
4/0 is way too small at 200a for 1200ft. Is that how far the aerial would run? That wire would be over 6% voltage drop for even 60a

200a would require parallel conductors as 1000MCM isnt even adequate.

That's a draw that really requires voltage higher than 240, I think
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,243
Location
Modesto, CA
Just thinking about electrical service way off road, and realized how little I know about aerial. I believe Poco will set a transformer on a pad at corner of property. Trenching through bedrock doesnt seem easy for 1200 feet so thinking aerial. I think 200 amp requires 4/0 aluminum triplex? Along property line, no driveways or any passages, how high and how close do I need to set poles?

Still considering pure solar and battery. Project is probably 2 years out, so solar and batteries can only improve.
way to long of a run.... voltage drop would be extreme with 4/0 AL

Can you get the PoCo to install a padmount transformer closer to the house?
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,324
Location
Illinois near St. Louis, Missouri
I would be talking to the POCO. I am about 500 ft from the road and before I converted to underground had a couple poles on my property with the last one about 100' from the house with the transformer on it. The POCO did everything up to the meter. Your area may be totally different though. My PoCo was very easy to deal with but then it's a coop and others may not be as easy.
 

cvairwerks

Well-known member
Joined
Aug 12, 2016
Messages
7,311
Location
Within hearing distance of Texas Motor Speedway
Depends on a lot of factors. Buddy needed about 250 amps of 440 3 phase for his back shop. POCO was way high on costs til he talked engineering into simply extending the 12.5kV 3p running across the front of the place, back to his shop, and he would supply the transformer. Think it ended up costing him a couple grand and he already had the transformer from a building cleanout he was doing.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,243
Location
Modesto, CA
Depends on a lot of factors. Buddy needed about 250 amps of 440 3 phase for his back shop. POCO was way high on costs til he talked engineering into simply extending the 12.5kV 3p running across the front of the place, back to his shop, and he would supply the transformer. Think it ended up costing him a couple grand and he already had the transformer from a building cleanout he was doing.
He had a 12.5Kv/480v 3ph wye pole transformer just sitting around?
 
To avoid these ads, REGISTER NOW!

cvairwerks

Well-known member
Joined
Aug 12, 2016
Messages
7,311
Location
Within hearing distance of Texas Motor Speedway
He had a 12.5Kv/480v 3ph wye pole transformer just sitting around?
Wasn't a pole pig, but a pad mount unit....He had bought out a facility that was going to be torn down. Most of the machinery was sold off as it was removed. The transformer and some small machines were all that he kept. He made a bunch of money off of that place. One of those things where he was in the right place at the right time and made a good offer.
 

beemerphile

Well-known member
Joined
Jul 9, 2021
Messages
727
Location
Danielsville, GA USA
Wasn't a pole pig, but a pad mount unit....He had bought out a facility that was going to be torn down. Most of the machinery was sold off as it was removed. The transformer and some small machines were all that he kept. He made a bunch of money off of that place. One of those things where he was in the right place at the right time and made a good offer.
Did the POCO take ownership of your bud's transformer or did they do primary metering? This sounds unorthodox to me.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
38,398
Location
Richmond, VA
Did the POCO take ownership of your bud's transformer or did they do primary metering? This sounds unorthodox to me.
Maybe it's classified as commercial. One of the plants I work in has a primary feeder and we own the transformers. There's actually two discounts on our bill for "high voltage metering" and a "high voltage discount". About $1900 on last month's $40k transmission bill
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,243
Location
Modesto, CA
Did the POCO take ownership of your bud's transformer or did they do primary metering? This sounds unorthodox to me.
They mustve given him primary metering as i highly doubt they would take ownership of a transformer with unknown conditions.

This of course is a rare situation as most PoCos will only do primary metering for industrial customers that own their own substation
 
OP
B

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,996
Location
Thousand Islands NYS
Just to fill in (because the ec's note on costs resurfaced on my desk) they offered 240/130 amp - two 350 kcmil urd - for $25k; or 240/80 amp - one 500 kcmil urd - for $16k. Thats wire only - trenching, panels, termination extra - and is near 5% bv oltage drop. He said National Grid would do overhead for $25,200 - I assume all except panels.

I liked the transformer and meter at the road so easy to have power there. Maybe a garage/shop.

So, just a lot of pieces to juggle.
 