AFCI Trips Randomly

bad_idea

Well-known member
Joined
Jun 11, 2011
Messages
4,335
Location
Pasquotank, NC
The AFCI breaker feeding my daughter's room trips randomly. Used to be once every couple months, recently has escalated to once or twice a week. House was built in 2005, and has a Square D Homeline panel. I replaced the AFCI breaker, hoping that would solve the issue. It did not. The circuit has the following items on it: ceiling fan/light with dual switch to control each function (14/3 between switch and fixture), closet light with switch, smoke detector (replaced a few months ago because one failed), and six receptacles.

The following items are plugged into the outlets: night light, alarm clock, and desk lamp. These items stay plugged in, breaker does not trip when any one item is flipped on/off.

I used a thermal camera to look for hot spots - everything looks good there.

I plan to pull open the receptacles, switches, and fixtures to look for loose connections tomorrow. Anything else I should look for while I'm in there? Other causes I should look into?
 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,017
Location
Central Iowa
Try putting one of these in and I bet your problems go away.


I'm not going to waste any time reading this, but nuisance tripping is the topic, I only know of one way to eliminate it.

 
OP
B

bad_idea

Well-known member
Joined
Jun 11, 2011
Messages
4,335
Location
Pasquotank, NC
I've read up on AFCIs, I know they are a nightmare. My concern is this is the only circuit that has had nuisance trips, the other four AFCIs in the house have not tripped once in the six years we have owned the house.

The ceiling fan is the exact same unit in the other bedrooms (each on AFCI breakers). My wife insisted we replace every ceiling fan in the house to match a few years ago.

I'll do an 'open and inspect' on all of the boxes today. If I don't find anything, I'll look at swapping in a standard breaker.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,517
Location
VT
Well this one almost sounds like it's properly working.

Haven't smoked detectors required a dedicated circuit for a while? The combo of items on one breaker makes me think and old circuit/one that has been added to.

I'd do a little more investigation before writing off to afci as snake oil.

Note: I'm not a fan of them either
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,517
Location
VT
@bad_idea can you provide a little detail on how you used the thermal camera? I'm assuming you didn't just stand in the doorway and point it at each device...
 

SlappyWhite

Well-known member
Joined
Oct 3, 2012
Messages
1,819
Location
Upper Canada
When opening the outlets check to see if they are backstabbed, if they are move the wires to the screws. This is a common source of trips. Also make sure any pigtails/connections are tight. Like others noted, check anything with a motor that uses brushes, another possible cause.

They can also trip if current is bleeding to ground, not a full GFCI level protection but circuit will trip it just at a higher current (I think >50ma or so). I have had a damaged wire cause tripping, a neutral to ground "leak".
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,017
Location
Central Iowa
Well this one almost sounds like it's properly working.
Tripping doesn't mean anything. I've been there and done that. Tried swapping AFCI breakers around d to verify and the same breaker was tripping no matter the circuit.
Haven't smoked detectors required a dedicated circuit for a while?
Never unless it's a local ammendment.
The combo of items on one breaker makes me think and old circuit/one that has been added to.
Sounds like a typical bedroom circuit to me. I wouldn't be surprised if the smoke detector isn't on the same circuit but it could be. If it is on the bedroom circuit, all of the detectors in the house should be as well.
I'd do a little more investigation before writing off to afci as snake oil.

Note: I'm not a fan of them either
They are snake oil whether they work properly or not.
 
OP
B

bad_idea

Well-known member
Joined
Jun 11, 2011
Messages
4,335
Location
Pasquotank, NC
@bad_idea can you provide a little detail on how you used the thermal camera? I'm assuming you didn't just stand in the doorway and point it at each device...

I pointed the thermal camera at each device ~2-3' away. The heat of each device was within a few degrees of the adjacent sheet rock.
 
OP
B

bad_idea

Well-known member
Joined
Jun 11, 2011
Messages
4,335
Location
Pasquotank, NC
Well this one almost sounds like it's properly working.

Haven't smoked detectors required a dedicated circuit for a while? The combo of items on one breaker makes me think and old circuit/one that has been added to.

I'd do a little more investigation before writing off to afci as snake oil.

Note: I'm not a fan of them either

The smoke detectors were all wired into the same circuit, the circuit for my daughter's room. The wiring is all original, no signs of additions.
 
OP
B

bad_idea

Well-known member
Joined
Jun 11, 2011
Messages
4,335
Location
Pasquotank, NC
So... I found the issue. Long story short, the smoke detector in the master bedroom had the neutral for the detector wired to ground. Plain as day, white wire and ground wire under the same wire nut.

Long story long - some times I fear I am a dumb ***. I went to the breaker to secure power to the circuit and realized I replaced the wrong breaker. I swapped the two breakers and now the new breaker on the trouble circuit was tripping immediately, every time.

I opened all of the receptacles up to find they were back stabbed. I removed all of the receptacles, identified the receptacle box the power cable from the breaker was coming from (turned breaker on and probed wires until I found 120v. The first box from the breaker had three cables in it - one from the breaker, second to the next outlet, and the third went to the smoke detectors. I installed the receptacle, turned the breaker on, it tripped. I removed the smoke detector wire from the junction, turned the breaker on and it stayed on.

I then went around the room installing receptacles and turning the breaker on between each one, breaker did not trip again. Once I had the entire circuit hooked up (with new receptacles with the wires under the side screws, not back stabbed), I then opened up the smoke detector boxes. I found the neutral from the pigtail wired to the ground in the box for the detector in the master bedroom. Swapped the neutral to the neutral and now the entire circuit functions correctly.
 

SlappyWhite

Well-known member
Joined
Oct 3, 2012
Messages
1,819
Location
Upper Canada
As the fault is staying with the circuit and not the breaker (breaker was swapped and the new one keeps tripping). This means to me that something is wrong in the circuit or with something plugged into it.

Also to add to my previous post in this tread. A device that is producing a large amount of EMI can also cause the trip. Look for cheap dollarstore phone chargers etc.

Edit, you found the problem!
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,017
Location
Central Iowa
I'm confused. It was tripping randomly in post #1, then switching the breakers caused it to trip immediately in #13. If the smoke was wrong from the beginning the AFCI should have immediately tripped on day one. If what I am thinking is true, the original breaker was junk out of the box.
 

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,757
Location
AK
Well this one almost sounds like it's properly working.

Haven't smoked detectors required a dedicated circuit for a while? The combo of items on one breaker makes me think and old circuit/one that has been added to.

I'd do a little more investigation before writing off to afci as snake oil.

Note: I'm not a fan of them either
That seems like a horrible idea. If on a lighting circuit it'd be noticed fairly quickly. On it's own, maybe never.
 
OP
B

bad_idea

Well-known member
Joined
Jun 11, 2011
Messages
4,335
Location
Pasquotank, NC
I'm confused. It was tripping randomly in post #1, then switching the breakers caused it to trip immediately in #13. If the smoke was wrong from the beginning the AFCI should have immediately tripped on day one. If what I am thinking is true, the original breaker was junk out of the box.
My thoughts exactly - the original was junk from day one.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,074
Location
Modesto, CA
Well this one almost sounds like it's properly working.

Haven't smoked detectors required a dedicated circuit for a while? The combo of items on one breaker makes me think and old circuit/one that has been added to.

I'd do a little more investigation before writing off to afci as snake oil.

Note: I'm not a fan of them either
as said above you definitely dont want them on a dedicated circuit because if it trips or stops working, you may never know. and then your smokes stop working. cant always rely on battery backup either.
 

SlappyWhite

Well-known member
Joined
Oct 3, 2012
Messages
1,819
Location
Upper Canada
as said above you definitely dont want them on a dedicated circuit because if it trips or stops working, you may never know. and then your smokes stop working. cant always rely on battery backup either.
Code here requires smoke detectors to have a regularly used light on the same circuit. When the light stops working you know the breaker is tripped (or the bulb is out...).

My boiler, fridge and smoke detectors are the only three 120v circuits without CAFI (AFCI) in my house. Smoke detectors are also prohibited to be on arc fault here by code.
 
To avoid these ads, REGISTER NOW!

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,517
Location
VT
I'll have to look later and see how I wired my smokes pretty sure I looked up what the code was followed that to the t. For some reason was thinking they were dedicated...
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,017
Location
Central Iowa
I'll have to look later and see how I wired my smokes pretty sure I looked up what the code was followed that to the t. For some reason was thinking they were dedicated...
They can be but nothing says they have to be as far as the NEC goes. I put them on a dedicated circuit but that's only because that's the way I was taught way back when...
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,582
Location
Northern Virginia
The sparkles at the day job put the smokes on a dedicated circuit.

They do include the attic radon pump prewire on that circuit for convenience as the smokes are a small load.
 
OP
B

bad_idea

Well-known member
Joined
Jun 11, 2011
Messages
4,335
Location
Pasquotank, NC
as said above you definitely dont want them on a dedicated circuit because if it trips or stops working, you may never know. and then your smokes stop working. cant always rely on battery backup either.
Ohh, but you can rely on the battery backup. When one of the batteries run low, they all start going off. At 3 am. That was what finally spurred me to fix the issue. The fire alarm went off at 3 am the other day. My daughter is 5 years old and seldom turns on her light. Her light was out long enough to run the batteries down on one of the detectors.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,074
Location
Modesto, CA
Ohh, but you can rely on the battery backup. When one of the batteries run low, they all start going off. At 3 am. That was what finally spurred me to fix the issue. The fire alarm went off at 3 am the other day. My daughter is 5 years old and seldom turns on her light. Her light was out long enough to run the batteries down on one of the detectors.
You are the exception to the rule. You know how many people let those batteries die after hearing it beep for days on end?
 

Meursault74

Well-known member
Joined
Apr 1, 2019
Messages
22,088
Location
Southern California
You are the exception to the rule. You know how many people let those batteries die after hearing it beep for days on end?
Nah, they just pull out the battery to stop the beeping. If they can stand the beeping for days, they have some fortitude. If mine starts to beep, I'll pull the battery quickly. If I don't have another 9v battery for it, I'll get another battery ASAP.
 
OP
B

bad_idea

Well-known member
Joined
Jun 11, 2011
Messages
4,335
Location
Pasquotank, NC
These do not do the chirping ****. They sound the fire alarm at 150db. At 3AM. We have been in the house for 6 years. The fire alarm has gone off 5 times now for various dumb problems. Each time has been between 2-3AM. NEVER during the middle of the day.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,017
Location
Central Iowa
I've found that the damned things use the batteries to chirp when the power is out and they use 120 volt to chirp when the batteries are dead. Which reminds me, I need to put the new SD up in my living room, I'm almost so used to seeing the wires hanging down that I don't notice it anymore.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,938
Location
Richmond, VA
I've found that the damned things use the batteries to chirp when the power is out and they use 120 volt to chirp when the batteries are dead. Which reminds me, I need to put the new SD up in my living room, I'm almost so used to seeing the wires hanging down that I don't notice it anymore.
Tomorrow's a better day for that
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,017
Location
Central Iowa
Tomorrow's a better day for that
I've been saying that for about three years now. I have one for the second time. The first one I bought sat on the kitchen table long enough that Mrs. Sparky put it in a drawer where it was almost forgotten about. Then I had to trim out a room addition and realized I had forgotten about a smoke detector. I needed three but had only purchased one on the way home the day before. I about tore the house apart until I found that smoke. That gave me a reset on the clock and I picked up another about a month ago. I have no idea where it's at though...
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,938
Location
Richmond, VA
I've been saying that for about three years now. I have one for the second time. The first one I bought sat on the kitchen table long enough that Mrs. Sparky put it in a drawer where it was almost forgotten about. Then I had to trim out a room addition and realized I had forgotten about a smoke detector. I needed three but had only purchased one on the way home the day before. I about tore the house apart until I found that smoke. That gave me a reset on the clock and I picked up another about a month ago. I have no idea where it's at though...
Tomorrow... The day that never comes
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,517
Location
VT
Any chance you have a pic of the old breaker?

Still trying to figure out how a neutral/ground bond at the smoke would trip an AFCI...
 

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,313
Location
Dutzow Missouri
hmm weird. ive seen several interconnected smokes that are hardwired with battery backup and they do indeed do the low battery chirp
If by beep you mean all 18 interconnected Kidde alarms screaming at full volume while you squint staring at the tiny LED in a feeble attempt to figure out if one is winking a different pattern, then you and I have different pain thresholds.

The only thing I know for sure is blowing out the alarms and replacing the batteries ever 12 months has keep the silent.

Walta
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,268
Location
Penngrove, California
If by beep you mean all 18 interconnected Kidde alarms screaming at full volume while you squint staring at the tiny LED in a feeble attempt to figure out if one is winking a different pattern, then you and I have different pain thresholds.

The only thing I know for sure is blowing out the alarms and replacing the batteries ever 12 months has keep the silent.

Walta
Nest Protect - Each unit will verbally announce trouble and location of troubled unit. Alerts such as loss of power, low battery, carbon monoxide, fire, etc. Also will alert and show on app. Each unit also has a sounder if all else fails. The sounder is tested each month via a built in microphone, and will give a brief unique tone sequence.
 
OP
B

bad_idea

Well-known member
Joined
Jun 11, 2011
Messages
4,335
Location
Pasquotank, NC
AFCI Troubleshooting Bulletin

I do not have a picture of the old breaker available, but I found the above document for the AFCI I had installed. I found it cruising the net looking for troubleshooting information. On sheet 7 it describes a 'inadvertent neutral to ground fault'.
 