My guess in this specific case.... The AFCI breaker will trip on a ground fault of ~50ma (compared to GFCI at ~5ma). Assuming the smoke alarm consumes less than 6w there is not enough current from the fault at this specific location to trip it based on the ground fault. When other devices are turned on some current will find its way through that fault and trip it. Could have been a borderline fault current wise at the detector and the new breaker is a little more sensitive. As I noted before in the thread (post #8) I have had this happen (neutral to ground fault, in my case a bad cable/wire). In that example turning on one or two lights didn't trip it...
If the new breaker happens to be dual function it will now trip based on GFCI levels... so right away.
***
I always wonder how many cases of "AFCI are black magic and the devils spawn" there is actually a small fault or loose connection (like loose backstabbing) that is beyond the skill or patience of the troubleshooter to find and how many are actually bad breakers, devil's spawn, etc. In this case the OP found a fault, the AFCI in the end did its job.
If the new breaker happens to be dual function it will now trip based on GFCI levels... so right away.
***
I always wonder how many cases of "AFCI are black magic and the devils spawn" there is actually a small fault or loose connection (like loose backstabbing) that is beyond the skill or patience of the troubleshooter to find and how many are actually bad breakers, devil's spawn, etc. In this case the OP found a fault, the AFCI in the end did its job.