Air Compressor Wiring Proposal Plz Check

bugnut

ALLIANCE MEMBER
Joined
Jul 14, 2012
Messages
3,875
Location
Central Ohio
I have a CH compressor. It is CH#hs5180000 sold by HD.
I have a 50amp circuit terminating in an outlet (nema 6-50r 50a-250v) in 2 distant locations in my shop.
I want to be able to use the compressor in either location.
I propose to wire in the following manner:
Male plug to match 50amp outlet with #8 wire to a Sq D box (qo2l30scp) with a Sq D (hom130cp) 30 amp breaker
from there with #10 wire to feed the compressor
images below show #12 wire from compressor switch to motor, this is the factory wiring.
The white outlet is a 20amp for the previous compressor. I will be unused but remain.

Am I missing anything?

TIA
 

Attachments

  • 20200406_100242.jpg
    20200406_100242.jpg
    69.5 KB · Views: 39
  • 20200406_100325.jpg
    20200406_100325.jpg
    129.8 KB · Views: 32
  • 20200406_100331.jpg
    20200406_100331.jpg
    54.8 KB · Views: 28
  • 20200406_100347.jpg
    20200406_100347.jpg
    119.4 KB · Views: 66
  • 20200406_100401.jpg
    20200406_100401.jpg
    153.1 KB · Views: 43
  • 20200406_111707.jpg
    20200406_111707.jpg
    150.7 KB · Views: 35
  • 20200406_111720.jpg
    20200406_111720.jpg
    92.7 KB · Views: 34
To avoid these ads, REGISTER NOW!

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
You won't find a 50 amp plug or receptacle thats horsepower rated unless you go to a pin/ sleeve style. Motors over 3 hp typically need to be hardwired..

Wire size for motors is based off of a table, #10 would be to small in nm-b but thhn in conduit would be ok.

Sent from my SM-G965U using Tapatalk
 

bamawildcat

Well-known member
Joined
Jul 12, 2014
Messages
148
You won't find a 50 amp plug or receptacle thats horsepower rated unless you go to a pin/ sleeve style. Motors over 3 hp typically need to be hardwired..

Wire size for motors is based off of a table, #10 would be to small in nm-b but thhn in conduit would be ok.

This. Also, you mention distant locations of your shop. If you are over 50 feet from your panel, or access is obstructed between the motor and panel (door, partition, cage), you will need a motor rated means of disconnect at the compressor, such as a disconnect switch or pin and sleeve like mentioned above.
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
I would keep the compressor in one location and hardwire it. If you need air in multiple locations, install air piping to those locations.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
I have a CH compressor. It is CH#hs5180000 sold by HD.
I have a 50amp circuit terminating in an outlet (nema 6-50r 50a-250v) in 2 distant locations in my shop.
I want to be able to use the compressor in either location.
I propose to wire in the following manner:
Male plug to match 50amp outlet with #8 wire to a Sq D box (qo2l30scp) with a Sq D (hom130cp) 30 amp breaker
from there with #10 wire to feed the compressor
images below show #12 wire from compressor switch to motor, this is the factory wiring.
The white outlet is a 20amp for the previous compressor. I will be unused but remain.

Am I missing anything?

TIA

This is not gonna work

Since the motor is 5HP, it will need to be hardwired. A nema 6-50p and r is not rated for 5HP

circuit wire for 5HP will need to be 35a rated, so #10 THWN or #8 NM-b.

The wire on the compressor is listed and not the same wire as building wire so you cant compare the 2.

If the compressor is more than 50' from and not within sight of the panel, then you will need a local disconnect. An A/C (air conditioning) pullout disconnect will work for this.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,585
Location
BC
I have a CH compressor. It is CH#hs5180000 sold by HD.
I have a 50amp circuit terminating in an outlet (nema 6-50r 50a-250v) in 2 distant locations in my shop.
I want to be able to use the compressor in either location.
I propose to wire in the following manner:
Male plug to match 50amp outlet with #8 wire to a Sq D box (qo2l30scp) with a Sq D (hom130cp) 30 amp breaker
from there with #10 wire to feed the compressor

That will work just fine, and be reasonably safe.

The limitation being its not safe to unplug the compressor while running. And no, it won't meet Code.
 

Bigblockyeti

Banned
Joined
Feb 1, 2018
Messages
2,550
Location
Upstate, SC
I have a CH compressor. It is CH#hs5180000 sold by HD.
I have a 50amp circuit terminating in an outlet (nema 6-50r 50a-250v) in 2 distant locations in my shop.
I want to be able to use the compressor in either location.
I propose to wire in the following manner:
Male plug to match 50amp outlet with #8 wire to a Sq D box (qo2l30scp) with a Sq D (hom130cp) 30 amp breaker
from there with #10 wire to feed the compressor
images below show #12 wire from compressor switch to motor, this is the factory wiring.
The white outlet is a 20amp for the previous compressor. I will be unused but remain.

Am I missing anything?

TIA
Sounds perfect, I ran my 7.5hp Quincy off a 50A 250 plug and it worked perfect. No need to over think it or add a bunch of expensive **** that would be needed in an industrial environment just for a home shop, especially when powering an SPL horsepower motor.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
Sounds perfect, I ran my 7.5hp Quincy off a 50A 250 plug and it worked perfect. No need to over think it or add a bunch of expensive **** that would be needed in an industrial environment just for a home shop, especially when powering an SPL horsepower motor.

Umm the OPs motor is NOT listed as SPL. It is listed as 5HP. The plug is not rated for 5 HP or 7.5HP.

Theres a reason code requires this to be hardwired. Nothing is being over think [sp] nor is the stuff needed to comply with the code, expensive. It also has nothing to do with being an industrial environment.

your comment is illogical, not to code, nor makes any sense.
 
To avoid these ads, REGISTER NOW!

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
I would keep the compressor in one location and hardwire it. If you need air in multiple locations, install air piping to those locations.

My thought as well. Unless the shop is like 45,000 square feet.

Hardwire w a piece of flex. Run some copper air pipe, couple of drops.

Would be a solid install, with no dragging the compressor around!
 
OP
B

bugnut

ALLIANCE MEMBER
Joined
Jul 14, 2012
Messages
3,875
Location
Central Ohio
Thanks to all for the replies. I'll see if I can get it hardwired and leave in one location. Shop is 30x40 so getting air everywhere is not an issue. Again Thanks All!
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
If its a cable its a size up, not a fatal flaw and cost depends on length. But I agree some of those calculators just don't seem right for lack of better words.
 
OP
B

bugnut

ALLIANCE MEMBER
Joined
Jul 14, 2012
Messages
3,875
Location
Central Ohio
All, sparky was out and hardwired with a suitable switch we're off and running. Filled with synthetic oil and did the one hour run in, all seems to be in good shape. Plumbed everything to the hose reel so we are ready to go.
Thanks to all!
 

1Garageman

Well-known member
Joined
May 12, 2009
Messages
4,417
Location
Columbus, Ohio
Bugnut, hello fellow Ohio'an. Do you have any updates on the wiring for your compressor? And are you happy with the CH compressor?
 