air return: cylindrical duct vs joist space?

2cool2hear

Well-known member
Joined
Aug 19, 2012
Messages
91
Is it safe to replace building cavities with metal cylindrical duct for cleaner, tighter air control? Most of the ductwork runs through the garage (unconditioned area).

Somebody mentioned that modifying the ductwork may throw HVAC balance out of control and possibly fry the system.

Suggestions/thoughts?
 
Last edited:
To avoid these ads, REGISTER NOW!

bgarrett

Well-known member
Joined
Feb 11, 2006
Messages
4,393
I've used the joist space for return air on two houses for 40 years. no problem
 

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
You can use any joist space but not if there's wire or gas line running through it.
But if it's in the garage , you'll have to use fire rated panning .
 
Last edited:

rkevins

Well-known member
Joined
Aug 6, 2011
Messages
951
Location
Central Arkansas
you must make sure that the duct work will carry the same amount of air, if the duct is not large enough you will starve the system of return air
 

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
Rule of thumb for return air 2 sq inches per btu of heat, so for a 80 ,000 btu . You would need 160 sq inches total of all return air runs combined.
 
To avoid these ads, REGISTER NOW!

pseudorealityx

Well-known member
Joined
Nov 10, 2009
Messages
999
Location
USA
That is a ridiculous rule of thumb. Any duct size should be based on the airflow, not a heating value. I can buy a 2 ton or a 5 ton with a 80k btu furnace. They certainly need different return ducts.
 

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
That is a ridiculous rule of thumb. Any duct size should be based on the airflow, not a heating value. I can buy a 2 ton or a 5 ton with a 80k btu furnace. They certainly need different return ducts.


It was never meant to be an exact measurement only a guideline , have you never heard the term .
 

pseudorealityx

Well-known member
Joined
Nov 10, 2009
Messages
999
Location
USA
It was never meant to be an exact measurement only a guideline , have you never heard the term .


Sure, but the guideline should 'sound' more like....

~80 sq inches per ton of cooling (nominally 400 cfm/ton)

THAT makes sense and is consistent.
 

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
I'm not in disagreement at all , but some of these new homers , it's becoming harder al the time , especially a log home. We have had to become very creative .
 