I'm almost at the point where I will run the main feed into my shop 100 amp panel from the meter. The distance is about 80 ft. Does anyone have an opinion on using aluminum wire versus copper? What are the pros and cons of aluminum? I hear it costs less.
 
To avoid these ads, REGISTER NOW!
To avoid these ads, REGISTER NOW!

FluxCore

Well-known member
Joined
May 28, 2012
Messages
229
Location
Born and raised in Germany, settled in Lousyana
If you are powering a shop subpanel from house main panel thru proper 2 pole breaker located in house main, and if you use properly sized(for alum) conductors, and if you terminate those conductors properly, and if the main house panel breakers and subpanel are designed for use with alum feeds, then go for it.....

Read up on how to properly feed a subpanel. Pay close attention to how bares and neutrals must be configured/bonded in the subpanel and house main. You will need to pull 4 whatever size alum or copper conductors from house panel to subpanel...2 will be insulated 120V hots, one will be insulated neutral, the 4th will be bare.

All must be sized accordingly considering alum or copper and length of run and amp capacity, and all connections must be made properly considering the type connection, the materials used for conductors and lugs, and the expected amp load.
 