My electrician is recommending #6 Aluminum wire to feed a new 100 sub panel from my house 200 amp main.
The total run is 100 ft. Is #6 ok?
I guess mine nor the power company don't know what they are doing either because I have #4 aluminum wire for my 125 amp service.
I guess mine nor the power company don't know what they are doing either because I have #4 aluminum wire for my 125 amp service.
The total run is 100 ft. Is #6 ok?
For certain you are going to want to meet the ampacity rating for the new panel.
#2 is the minimum,larger for that distance definitely wouldn't hurt.
Unless you really need to save big $$$.....why go aluminum at all?
Steve
Unless thats the wire coming from the pole to your service mast, your electrician is clueless
the main panel to the breaker panel in the garage is all 4 gauge aluminum.
I asked if I could see his code book to look up if #4 could be used even and he didn't have a book.... yeah....Its a code violation, plain and simple
MRB,
My installation will include pulling the wires through the house attic from the main panel, down a wall, then underground to the new garage.
Thanks for the infor on the number of wires.
Hey fellows, ive been fololwing this thread with great intrest as i am doing exactly the same thing ,running 100' with aluminum wire. I also have a friend who is an electrician and he said i would be better off setting up for 200amp service while im putting it in even if i just used it as 100. he suggested 4/0 4/0 4/0 with 2/0 ground wire. i assume this is different from the #6 and #4 you all are discussing and i have plenty as far as wire size goes....thanks in advance for any reply
here's the NEC tables http://www.okonite.com/engineering/nec-ampacity-tables.html
it's a no brainer: at least #1 (Al)....#2 is smaller, the next size up is 1/0
in air #4 is good for 100A...
Vd for L=100' at 100A #1 Al is ~2%, not a problem...
did he run MULTIPLE #4's, ie, 2 per leg?
isnt 4 too small to be allowed to parallel?
he suggested 4/0 4/0 4/0 with 2/0 ground wire.
4/0 (Al) is too small for 200A, it's only good for 180A
you need at least 250 MCM, which is preety unwieldy
isnt 4 too small to be allowed to parallel?
The run through the attic will not be in conduit, only the portion going underground from the house to the new garage.
Roughly, what is the difference in price between #6 and #2 aluminum?
240.4(B) says I can go up to the next overcurrent size(200 amp) provided the calculated load isn't over 180 amps. He said he really only needed a 100 amp panel, so we're definitely in the clear.
but for the $$ differential, and the fact you're using 200A lugs, why not full rate the system?
and doesn't a 'calculated' load have to be performed by an engineer (or under engineering supervision) ?
I'm a firm believer of matching ratings, especially if the $$$ is minimal
If a fire is caused due to faulty wiring, then the insurance company will not cover the damage. To save a few bucks now, could cost you thousands later........and besides aluminum wire requires annual maintenance....i.e. inspecting ALL connections and lubricating them with a special lubricant on order to prevent corrosion. Also, if aluminum wire is going to be used, it needs to be 2 sizes larger than the recommended copper wire size.
There is absolutely no reason too.
Do you think an engineer is involved every time an electrician puts a service on a house? No. We have a codebook, we have demand/calculation tables, we are qualified to do a load calc.
Minimal is interpreted differently for everyone. I wouldn't do it myself, the only reason I'd bump to 250mcm is if the distance was great and I knew they'd be pulling a lot of load, in this instance, this is not the case.
To make a potentially long response much shorter, suffice to say, you don't have a clue.