To avoid these ads, REGISTER NOW!

Am I going overboard? 30a Generator Input

HamAndEggs

Well-known member
Joined
Nov 16, 2020
Messages
932
Location
Houston, TX
I just had my entire electrical system overhauled, and before I fix up the walls I'm thinking of installing a 30a power inlet and interlock kit for a generator

The reason this might be crazy, is that I don't own a gasoline generator, and I've already paid for (Pending install, long wait!) a 27kw Natural Gas generator

My thinking is that at some point I'm sure I'll have a gas generator, and then at least I can still have lights if the natural gas goes out (Never has, not sure if it ever will. I'm Houston)

Good idea, or am I just taking things too far?
 
To avoid these ads, REGISTER NOW!

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
12,085
Location
Austin, TX
I don't think this is overkill.. I might do the same (drop in an interlock kit) where I have a whole house unit - it'd allow "partial power" scenarios. Just remember that loading is manual.
 

Noltz

Well-known member
Joined
Mar 10, 2020
Messages
377
Location
Ontario, Canada
I did exactly this when I was dropping power into my garage. I made a mistake though; I used 8/3 Romex instead of individual conductors. If I had used 8 gauge conductors I could have put a 50A inlet on in the future. Code prohibits 50A in Romex, but it's okay if they're loose. I didn't plan on such a big generator but a good deal showed up.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,253
Location
Modesto, CA
I did exactly this when I was dropping power into my garage. I made a mistake though; I used 8/3 Romex instead of individual conductors. If I had used 8 gauge conductors I could have put a 50A inlet on in the future. Code limits #8 NM-b to 40a, but it's okay if they're loose. I didn't plan on such a big generator but a good deal showed up.

fixed it for you :thumbup:
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,323
Location
Coronado, CA
Thanks for letting me know about the limits on NM-B Cable. I ran THHN 8 Gauge to feed my welder. I might use that same circuit, if and when, I feed the house from my generator.
 

b-boy

Well-known member
Joined
Oct 2, 2013
Messages
2,157
Location
Buffalo NY
My thinking is that at some point I'm sure I'll have a gas generator, and then at least I can still have lights if the natural gas goes out (Never has, not sure if it ever will. I'm Houston)

Good idea, or am I just taking things too far?

Honestly, I know several people with NG generators.

It might be a coincidence, but every one of them has told me that it failed during at least 1 power outage. Usually it's a dead battery or some error code that was flashing on the unit that no one noticed.

I think you need to be prepared, and having a backup is never a bad thing. I converted my generator to run on NG and gasoline in case one is not available.
 

Backfeed

New member
Joined
Feb 24, 2021
Messages
1
Location
Oregon
Don’t quote me but I believe 30a inlet will only feed up to a 7000kw generator anything larger will need 50a just food for thought depending on what size portable generator you plan on buying.
 
OP
H

HamAndEggs

Well-known member
Joined
Nov 16, 2020
Messages
932
Location
Houston, TX
I got my garage panel upgraded today as well as getting the interlock installed. 30a breaker in there now, but the inlet was out of stock so it goes nowhere

I might grab the 50a, seems to make sense

O5aUirw.jpg


w6SaX4w.jpg


This panel has feed through lugs and feeds my house, and the 60a breaker goes to the garage sub panel. It will be upgraded to 125a when the breaker arrives, all out of stock

New garage sub

WsM4w8p.jpg


z1vInV4.jpg


I'll be "upgrading" to AFCI/GFCI breakers soon

Its nice to have all this capacity and space to add more circuits!
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
12,002
Location
Fargo, ND
27KW is over 100 amps. Why put in a 30 amp generator connection? Although 30 amps will go a fair distance to power a home unless you have electric heat.
 
OP
H

HamAndEggs

Well-known member
Joined
Nov 16, 2020
Messages
932
Location
Houston, TX
The 27kw Generator comes off the transfer switch on the line side, before the main breaker on the panel

But, if I want to connect a gasoline generator, I can now use it with the inlet
 

NickH

Well-known member
Joined
Nov 18, 2015
Messages
283
Location
Southern Maine
It may be redundant, but I wouldn't call it over kill. It's a very low-cost, easy to install way to ensure you can power your place in the event of grid power AND utilities going out. I'd do it too if I was in your shoes.
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
12,085
Location
Austin, TX
27KW is over 100 amps. Why put in a 30 amp generator connection? Although 30 amps will go a fair distance to power a home unless you have electric heat.

I dunno, maybe your primary generator fails.. Or you decide you're looking at an extended outage and you don't want to burn 27KW worth of propane/natural gas all day...
 
To avoid these ads, REGISTER NOW!
OP
H

HamAndEggs

Well-known member
Joined
Nov 16, 2020
Messages
932
Location
Houston, TX
I dunno, maybe your primary generator fails.. Or you decide you're looking at an extended outage and you don't want to burn 27KW worth of propane/natural gas all day...

Its not all or nothing, so under normal load the natural gas usage isn't too bad. And natural gas is cheaper here

The 27kw liquid cooled unit supporting 12kw uses less natural gas than the 22kw air cooled unit supporting 10kw

Its actually pretty good
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,323
Location
Coronado, CA
That is a very good looking installation.

Because my "Homebrewed" generator has a 10KW Peak rating I intend to feed my house through my welder power connection after opening the service disconnect.

Standing by for the Flame Cannons.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,253
Location
Modesto, CA
That is a very good looking installation.

Because my "Homebrewed" generator has a 10KW Peak rating I intend to feed my house through my welder power connection after opening the service disconnect.

Standing by for the Flame Cannons.

so you will be using a suicide cord? :shocking: :shocking:
 

slow

Well-known member
Joined
Feb 26, 2006
Messages
2,596
Location
near Orlando
This is how we do it in California

16d66d320bf864b9cf52331f3c852ead.jpg

While a suicide cord is really bad, a 4 wire to 3 wire suicide cord is even worse as your not connecting the neutral, OR connecting the neutral to the ground, both are bad ignoring the suicide cord having a hot end when connected to the generator.
 

Attachments

  • 16d66d320bf864b9cf52331f3c852ead.jpg
    16d66d320bf864b9cf52331f3c852ead.jpg
    26 KB · Views: 0

quickfarms

Well-known member
Joined
Feb 14, 2021
Messages
1,027
Location
Southern California
While a suicide cord is really bad, a 4 wire to 3 wire suicide cord is even worse as your not connecting the neutral, OR connecting the neutral to the ground, both are bad ignoring the suicide cord having a hot end when connected to the generator.



Since the connection is at the service entrance the inspector and power company do not have an issue with the neutral and ground being connected since they are connected a foot away
 

slow

Well-known member
Joined
Feb 26, 2006
Messages
2,596
Location
near Orlando
well that is better than using a regular 3 wire dryer plug, Amazed that an inspector for a CA company would allow that setup.
 
To avoid these ads, REGISTER NOW!