How many amps does a 230 volt 1/2hp well pump draw
The tag on the pressure tank says 6 amps
I find that kinda hard to believe especially when it’s on a 20 amp breaker
When it cuts on I can tell by the sound of the generator it’s drawing some amps
I’m no electrician that’s why I’m asking you guys
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
How many amps does a 230 volt 1/2hp well pump draw
The tag on the pressure tank says 6 amps
I find that kinda hard to believe especially when it’s on a 20 amp breaker
When it cuts on I can tell by the sound of the generator it’s drawing some amps
I’m no electrician that’s why I’m asking you guys

you sure its 1/2 hp?

NEC table FLC lists 1/2hp as 4.9a, which is always higher than nameplate FLA.

also, motors have in-rush currents which are 4x-8x nameplate FLA.... they draw a lot more current on startup

Is there an issue?

430-248.png
 
OP
H

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
dae3b8c17423dcd417ceca133dcaf9f1.jpg


Sent from my iPhone using Tapatalk
 

Attachments

  • dae3b8c17423dcd417ceca133dcaf9f1.jpg
    dae3b8c17423dcd417ceca133dcaf9f1.jpg
    23.6 KB · Views: 0
OP
H

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
88c89268d9f787f7d3a21675ac4c0ff4.jpg


Sent from my iPhone using Tapatalk
 

Attachments

  • 88c89268d9f787f7d3a21675ac4c0ff4.jpg
    88c89268d9f787f7d3a21675ac4c0ff4.jpg
    76.9 KB · Views: 0
OP
H

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
I know starting watts is more
I guess u need an amp meter for that
I’m getting all my amperage numbers so I know what I can run off of generator
I’m having to toggle things off and on so I don’t overload the generator
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
Youve got 2 different motor stickers there.

which brand is in the well?

or those may be old and it may be something else

but for a motor, you need to consider the inrush current as well, because while you generator running watts may be able to handle the load, it may not be able to handle it when the pump is starting

also notice the SF is pretty high.... this can change the FLA
 
OP
H

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
Myers tank
Franklin pump
That’s what was here when I bought the house
I guess because of the surge is why it’s on a 20 breaker
 
OP
H

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
Here’s why I have to toggle things on and off
6 amp fridge
5 amp upright freezer
1500 watt toaster oven
1100 watt microwave
Coffee maker??
2 1500 watt delonghi oil filled radiators for 2 bedrooms gas logs do the living room
Dishwasher 12 amps Haven’t run that since power outage
Well pump
Water heater
Septic pump don’t know what that draws. It’s on a single pole 20
Wonder if the 12 amps on dishwasher is pump motor and heat element combined amperage
 

Captain Spaulding

Well-known member
Joined
Feb 13, 2017
Messages
753
Location
Southern Indiana
Just because a motor works on a 20A breaker doesn’t mean it will work on a generator, even if the generator is rated for the same power as the breaker can pass. The generator has a surge rating and a continuous rating. Generally the surge rating is the absolute maximum the generator can provide. A 20A household circuit could potentially source 100A for the very brief period it takes the motor to spin up.
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,048
What generator do you have? assuming a "typical" 4kW/8hp generator with a 20A 220V 2x 120V 20A breakers, yes, you will have to manage your loads. technically, the space heaters would come close to maxing that out on their own (12A each on high /3kW), and should be on opposite sides of the generator spit phase.

toaster/microwave only use power while in use, so that's easy. use one at a time. coffee maker: it depends.
 
OP
H

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
What generator do you have? assuming a "typical" 4kW/8hp generator with a 20A 220V 2x 120V 20A breakers, yes, you will have to manage your loads. technically, the space heaters would come close to maxing that out on their own (12A each on high /3kW), and should be on opposite sides of the generator spit phase.

toaster/microwave only use power while in use, so that's easy. use one at a time. coffee maker: it depends.

Could you explain how the split phase works
I have an idea
Is it evening out the load
I’m trying to learn all I can about this stuff
 
Last edited:
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
Could you explain how the split phase works
I have an idea
Is it evening out the load
I’m trying to learn all I can about this stuff

Split phase is 120/240. 2 hots and a neutral that is tapped in the middle of the secondary winding. Thus its called split phase

You want to balance the load as evenly as possible on the 2 phase legs of your generator
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,269
Location
Coastal NJ
And how do I do that

I could give you the full engineering explanation - but instead I will give you a practical example.

Lets say you have 2 separate duplex receptacles on your generator - remember a duplex receptacle can receive 2 plugs. So lets call those duplex receptacles A and B.

You want to split up your appliance loads evenly on A and B.

So if you have (2) space heaters and they each consume 1500W, you want to put 1 heater on A and 1 on B.

Following that example - add up the consumption of your appliances and distribute them to A and B evenly.
 
OP
H

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
Gotcha
Yea I’m not using any of those
I’m using the 30 amp plug on the generator
Back feeding to the main panel in the house
Thanks for clarifying that up
 

Lightning rod

Well-known member
Joined
Dec 1, 2012
Messages
283
Location
Toronto , Ontario
actually , the 30a (assume 240v) plug on the generator still connects back to the same place (windings)that the outlets connect to.

what model /make of generator do you have?
the owners manual has the wiring connections and you can confirm some things

if the 30 plug connects back to the main panel as a 120/240v connection, load balancing is still required. as previously explained
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
Gotcha
Yea I’m not using any of those
I’m using the 30 amp plug on the generator
Back feeding to the main panel in the house
Thanks for clarifying that up

doesnt matter what method you use to connect to the generator. the principle is the same. that 30a 120/240 outlet, has 2 legs that need to have equal load on them

since this will be connected to a panel, you need to balance the circuit breakers across the 2 phases in the panel

And hopefully you are using an interlock or transfer switch to lock out the utility power from the generator power.
 
OP
H

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
a3b57c392ff2fd52de3b966b0a060af8.jpg
2166f9569fb79019216b8da6b7ff9cf3.jpg
5b9ab0394344e993099c450763a3e10d.jpg


Sent from my iPhone using Tapatalk
 

Attachments

  • a3b57c392ff2fd52de3b966b0a060af8.jpg
    a3b57c392ff2fd52de3b966b0a060af8.jpg
    155.8 KB · Views: 0
  • 2166f9569fb79019216b8da6b7ff9cf3.jpg
    2166f9569fb79019216b8da6b7ff9cf3.jpg
    128.6 KB · Views: 0
  • 5b9ab0394344e993099c450763a3e10d.jpg
    5b9ab0394344e993099c450763a3e10d.jpg
    108.9 KB · Views: 0

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,269
Location
Coastal NJ
30 amp plug
Why does it say 43-21 amps

Generator can supply 21 amps at 240 volts or 43 amps at 120 volts
And watts = volts X amps.
Generators are rated in watts.
Your loads may be 120, 240 volts
You get to do the math based on your loads.

You use a 30A cord set and connectors because your generator can supply 21A at 240V so the cord set is sufficient.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,269
Location
Coastal NJ
Gotcha
Yea I’m not using any of those
I’m using the 30 amp plug on the generator
Back feeding to the main panel in the house
Thanks for clarifying that up

Since you are feeding the main panel it’s a little harder to determine how your loads hit the main panel compared to plugging in to receptacles. Ultimately your main panel has 2 legs that are connected like the examples I gave as receptacle A and B.
Half of your breakers are on A and half on B
The 240 loads are across A and B.
 
OP
H

Hot shot

Well-known member
Joined
Jul 10, 2019
Messages
420
Location
Virginia
The other thing is I have POWER!! After 6 1/2 days
Power company cut it on and it blew a 100 amp fuse on the pole near the transformer
They drove up and down the road looking at the wires, didn’t see anything. Put another fuse in and blew it too. Guy said it was something small doing it
They went back up the road looking at stuff. They either found the problem or got lucky on the 3rd try because it never blew again
 