Here's the situation - I have a hallway with two recessed lights controlled by a switch at each end of the hall. These lights worked fine for many years. Then they quit working for a while. Then they started working again and now they are out again. I removed the wires from both three-way switches, located the travelers with a continuity check, separated all wires and turned on power. Neither switch has line current! But, there is a half-bath on the same lighting circuit and the vanity light and fan work just fine. So, if the breaker is OK, why don't I have any power at either switch?? After all these years??
 
To avoid these ads, REGISTER NOW!

cmandp

Well-known member
Joined
Dec 22, 2011
Messages
1,295
Location
New Jersey
Do you know where power is coming from and feeding to this 3 way circuit? Since you have the bathroom on the same circuit and it's working I would think you're getting power from there to this circuit. I would then guess the connection is bad or something damaged the power wire feeding this circuit.
 

CoogarXR

Well-known member
Joined
Jan 11, 2016
Messages
6,882
Location
Ohio
Do you know where power is coming from and feeding to this 3 way circuit? Since you have the bathroom on the same circuit and it's working I would think you're getting power from there to this circuit. I would then guess the connection is bad or something damaged the power wire feeding this circuit.

Pretty much this.

Where do the wires come from? Attic, basement, adjacent room? Go find 'em :D
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,145
Location
Modesto, CA
One common is power into the circuit, the other common is power out to the fixtures

You need to figure out which “common” is the power into the 3-way switch circuit.

From there you trace this wire to where it gets power.
 
Last edited:

klassenl

Well-known member
Joined
Feb 20, 2016
Messages
716
Location
Southern Alberta
I checked every wire with a voltmeter. Nothing. The travelers are isolated so that leaves a line wire in one and a load wire in the other. Both are dead. After having worked for over 20 years.

Did you check against neutral or ground

I have to remind myself when I'm checking for power that I need line and a reference point - either neutral or ground. Sometimes I use an extension cord plugged in to a receptacle and use the ground and neutral from that to check.
 

MikeF2316

Well-known member
Joined
Dec 29, 2012
Messages
9,605
Location
Thornhill, ON
I'd make note of everything on the circuit, and start at the junction box closest to and physically in between the hallway and breaker box. Look for the hot splice, whether in a wire nut or using the second connection on an outlet.
 
To avoid these ads, REGISTER NOW!

ambenz

Well-known member
Joined
Dec 12, 2010
Messages
4,245
Location
NW Chicago Suburbs
Maybe it was NEVER wired correctly in the first place and the hot is coming thru a lightbulb that has a burnt out filament and they are switching neutrals? I've seen some weird stuff wired.
 

cabranch47

Well-known member
Joined
Jun 8, 2011
Messages
103
Location
Louisiana
Are the lights maybe fed from a GFIC receptacle in the bathroom? I had a similar problem and the GFCI was bad.
 

Innovate1

Well-known member
Joined
Jul 28, 2014
Messages
4,315
Location
Illinois near St. Louis, Missouri
Yep. Just need to find the bad connection. I had a similar thing happen on a feed to a microwave in a rental. It had worked for at least 10 years. Don't remember exactly how I found the bad splice because it was hidden in a soffit above a cabinet on the other side of the kitchen. Had to cut a hole in the top of the cabinet to get to it. Was just a wire not gripped well in a wire nut.

Turn off the breaker and note everything effected. Then trace the wiring to figure out where the feed is from. Pull the outlets and switches nearby. Perhaps a wire tracer. It can be difficult to track these things down - think of it as a puzzle and you are looking for clues... :)
 

MatBirch

Well-known member
Joined
Oct 10, 2013
Messages
419
Location
Filer, Idaho
Does the power feed the fixture first? Not uncommon, and easy to check. Could simply be a loose connection in the fixture, or a problem with the fixture itself.
 
OP
B

bassbone52

Well-known member
Joined
Jan 7, 2011
Messages
516
Location
Central Indiana
All the suggestions regarding a bad splice make the most sense. Part of this circuit - bathroom lighting and fan - is fine. It's the adjacent hallway lighting which is not working. As a test, I connected the hot wire from a 4-way switch to the common terminal on the adjacent 3-way switch of the circuit in question. The hall lighting works fine with this setup. I just have to get in the attic, make the long cold walk and find out why I have lost power to one of the 3-way switches.
 