Another compressor wiring question

Rickster55

Well-known member
Joined
Jun 22, 2009
Messages
1,132
Location
Syracuse, NY
I will be buying this compressor soon. What size wire do I need to run for this compressor? It will be installed approx. 30 ft. from the main breaker panel. TIA

Manufacturers Number: TS4N5
Brand: Ingersoll Rand®
Grade: Consumer
Style: Stationary
Tank Size: 80 gal.
Running HP: 5 HP
Voltage Rating: 230 V
Phase: Single
CFM @ 90 PSI: 15.8
Maximum Pressure: 175 PSI
Width: 40 in.
Total Length: 48 in.
Height: 76 in.
Weight: 600 lb.
Warranty: 1 yr. or 2 yr. w/Use of Ingersoll Rand Synthetic Lubricant
PSI Rating: 175 PSI
Pump Style: Two-Stage
Material: Cast Iron
 
To avoid these ads, REGISTER NOW!

Tom in Seattle

Well-known member
Joined
Feb 8, 2012
Messages
45
Location
Sammamish, WA
5 HP = 3730 W. At 230V that's a bit over 16A running load. Startup will be more, so you should probably be OK with a 30A circuit running 10/2 wire. I'm surprised the manufacturer doesn't provide the electrical requirements.
 
OP
R

Rickster55

Well-known member
Joined
Jun 22, 2009
Messages
1,132
Location
Syracuse, NY
Thanks Tom. They might. I havent bought it yet. I figured it was 30 Amp with 10 gauge - just making sure. Is it because its a single phase that I only need 10/2 wire?
 
Last edited:

PT Doc

Well-known member
Joined
Nov 12, 2010
Messages
3,197
Quincy recommended a 50 amp breaker for my 80g, 2stage, 5hp, 17 cfm, 175 psi. Baldor motor states 23 fla. wire gauge for was based on future welder addition so I went with 6g over 75' and went with 60a breaker.
 
To avoid these ads, REGISTER NOW!

Tom in Seattle

Well-known member
Joined
Feb 8, 2012
Messages
45
Location
Sammamish, WA
Thanks Tom. They might. I havent bought it yet. I figured it was 30 Amp with 10 gauge - just making sure. Is it because its a single phase that I only need 10/2 wire?
You only need a 3-wire connection if the appliance is running both 120 and 240 volt circuits, such as a dryer, ovens or range. For 240 V only you only need two hots and ground... no neutral is required.


The 30A breaker is only a guess based on the 5 HP running load. The manufacturer must provide a spec on the unit that will state the requirements. Try to find a PDF file with the installation instructions. Good luck.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
That comp will be well served by a 10 wire and 30A breaker. I think if falls in to the legal limit where it would run from a 12 if its all a guy had but since you got to get wire a 10 isn't going to hurt, you are doing your own work, the cost difference is minimal, why not give it a little extra.
 
Last edited:

tomshep

Well-known member
Joined
Sep 24, 2011
Messages
441
I will be buying this compressor soon. What size wire do I need to run for this compressor? It will be installed approx. 30 ft. from the main breaker panel. TIA

Manufacturers Number: TS4N5
Brand: Ingersoll Rand®
Grade: Consumer
Style: Stationary
Tank Size: 80 gal.
Running HP: 5 HP
Voltage Rating: 230 V
Phase: Single
CFM @ 90 PSI: 15.8
Maximum Pressure: 175 PSI
Width: 40 in.
Total Length: 48 in.
Height: 76 in.
Weight: 600 lb.
Warranty: 1 yr. or 2 yr. w/Use of Ingersoll Rand Synthetic Lubricant
PSI Rating: 175 PSI
Pump Style: Two-Stage
Material: Cast Iron


Nice compressor. I was looking at the same unit but dropped down to the 60 gal unit/single stage. I think ss5l5. Much higher cfm and $150 less. Maybe something to consider.

Tom
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
That comp will be well served by a 10 wire and 30A breaker. I think if falls in to the legal limit where it would run from a 12 if its all a guy had but since you got to get wire a 10 isn't going to hurt, you are doing your own work, the cost difference is minimal, why not give it a little extra.

A true 5HP draws 28 amps.

28 amps x 125%= 35 amps= #8 Romex or #10 THHN minimum.

Minimum 35 amp breaker.
 